Yes, yet another grounding question.
I am designing a DC coupled system that will have a Victron inverter and SCC, and the inverter and batteries power a critical loads panel for the house. Said critical loads panel can be switched by a transfer switch to be powered by the grid/main panel or the inverter. There will be no grid feedback.
PV will be ground mounted.
I am in the USA and NEC compliance is required.
1. PV EGC will come into a grounding busbar, where all DC cases and enclosures, are connected. Said busbar will connect to the main panel ground where the neutral/ground bond is formed, then out to the rods at the side of the house via existing wiring.
2. Battery floats with no +/- ground, only the case is grounded to the ground busbar.
3. The AC-in of the Victron will come from the main panel and *only* be used to charge the batteries and power loads when batteries are low, otherwise ignored or disconnected.
My question concerns what to do with the chassis ground and the ground relay.
Victron recommends (in the Multiplus II manual), to not use the chassis ground in a fixed (as opposed to a mobile (RV)) installation where AC-in is always present. But in my case that is not true (AC-in won't always present). I am aware that the ground relay in the inverter allows the AC-in to provide grounding when it is used.
In a mobile installation, Victron says to connect the chassis ground to DC-negative busbar, and then the DC negative to ground or the vehicle chassis.
But In my situation, what should I do?
A. Connect Victron chassis ground lug to aforementioned ground busbar?
B. Connect to DC negative bar and DC negative bar to ground busbar?
C. Something else?
Implicit in these choices is what to do with the ground relay, but if I connect the chassis ground, I suspect I need the relay.
Thanks.
I am designing a DC coupled system that will have a Victron inverter and SCC, and the inverter and batteries power a critical loads panel for the house. Said critical loads panel can be switched by a transfer switch to be powered by the grid/main panel or the inverter. There will be no grid feedback.
PV will be ground mounted.
I am in the USA and NEC compliance is required.
1. PV EGC will come into a grounding busbar, where all DC cases and enclosures, are connected. Said busbar will connect to the main panel ground where the neutral/ground bond is formed, then out to the rods at the side of the house via existing wiring.
2. Battery floats with no +/- ground, only the case is grounded to the ground busbar.
3. The AC-in of the Victron will come from the main panel and *only* be used to charge the batteries and power loads when batteries are low, otherwise ignored or disconnected.
My question concerns what to do with the chassis ground and the ground relay.
Victron recommends (in the Multiplus II manual), to not use the chassis ground in a fixed (as opposed to a mobile (RV)) installation where AC-in is always present. But in my case that is not true (AC-in won't always present). I am aware that the ground relay in the inverter allows the AC-in to provide grounding when it is used.
In a mobile installation, Victron says to connect the chassis ground to DC-negative busbar, and then the DC negative to ground or the vehicle chassis.
But In my situation, what should I do?
A. Connect Victron chassis ground lug to aforementioned ground busbar?
B. Connect to DC negative bar and DC negative bar to ground busbar?
C. Something else?
Implicit in these choices is what to do with the ground relay, but if I connect the chassis ground, I suspect I need the relay.
Thanks.