I purchased a open box Victron MultiPlus 12/3000/120-50 120V from Inverter'R'US and have downloaded (and read some of) the Service Manual, Owner's Manual, and Wiring Unlimited. I have 4 x 200 AH LiFePO4 batteries; Feence brand with JBD bluetooth BMS. 12 x 100 watt panels (2 arrays 2S3P) run through two Smart Solar 150/60 - TR controllers. My installation is going slowly due to work constraints. I have a SmartShunt, MK3 to USB-C adapter and a Smart Dongle. I'm hoping my Cables To Go brand UTP Cat5E cables will work in lieu of the expensive Victron cable? If not I need to buy a Victron cable. My 2021 Outdoors RV 280RKS trailer has 30 amp service. The 30 amp shore power inlet is a Furrion IM-F30ITX-V1 and the power converter is a Progressive Dynamics PD4060K. I will continue to use the PD4060K as my 120 volt AC and 12 volt DC panels and take the converter off line. The 30 amp line in is 10 AWG Romex. I'm assuming the PD4060K will accept up to 8 AWG Romex since the manual provides torque specs for 8 AWG as well as 10-14 AWG; it doesn't provide specs for 6 AWG . The shore power inlet will accept 6 AWG, I think; I called Furrion and they said they "think" it will. Some people have posted regarding having issues connecting smaller Romex to the MultiPlus 3000. Some folded it over and some spliced to thicker wire. Power Assist sounds nice but I only want 30 amps. Can I configure the MultiPlus to put out no more than 30 amps? If not I could turn Power Assist off. Correct? Bottom line I would rather limit my 120 volt power to 30 amps to simplify my 120 volt wiring. 8 AWG Romex is stranded and rated to 40 amps. It would fit my converter and shore power inlet. Victron recommends 6 AWG stranded for the AC in and out 1. I'm thinking of using 8 AWG Romex for both which would be oversized for 30 amp max configuration but is stranded unlike the 10 AWG Romex which is solid. I also plan on hooking up only AC Out 1 since my loads won't exceed the inverter output. No sub panel. I know not to run the microwave, water heater, and air conditioner all at the same time and can turn those breakers off when they're not needed.
I have 3 possible 120 volt power sources. Shore power from a 30 amp pedestal that has a breaker. A 2000 watt Champion inverter generator rated 2000 surge and 1700 running. A 4000 watt Wen inverter generator rated 4000 surge and 3500 running. I am in Colorado year round now but eventually summer only and winter in AZ. I will be at high altitude most of the time so my generator outputs will be lower. I don't plan on running generators unless absolutely necessary or using shore power.
A 30 amp breaker in between my shore power inlet and the MultiPlus would be good but I am having trouble finding a small set up. It seems that since my generators won't be exceeding 30 amps and shore power hook ups usually have a 30 amp breaker that I could forego a 30 amp breaker in between the shore power inlet and MultiPlus. Would that be OK? Has anyone else gone that route? Otherwise I have a Midwest Electric 30 Amp AC disconnect I could use or Square D makes a couple 30 amp load centers that would work. Carling Technologies also makes panel mount 30 amp breakers. Those are the best options I've found. I'm open to suggestions that are hopefully small and affordable.
I'm wiring the DC to the MultiPlus with 2 x 1/0 as recommended in the service manual with a 400 Amp Class T fuse in between the positive connection bus bar and the MultiPlus. I will run a ground from the negative load bus bar to the chassis. From what I've read it sounds like the chassis grounds for the controllers and the MultiPlus should run to the negative load busbar which is grounded to the chassis. Correct? I'm not certain what size wire is needed for the controller and MultiPlus chassis grounds. For the negative busbar ground I understand it would need to be wire that can handle 400 amps which is 4/0. I think ABYC frowns on using 2 x 1/0 since each conductor should be able to handle the 400 amps. I believe Victron is OK with the wire being 1 size down which would be 3/0. Is that correct? I have posted about this connection before. My trailer has 3 ground connections. One at the front triangle battery location for the negative battery terminal. One at the factory negative 12 volt load busbar located in a underbelly compartment right behind the front triangle. Another at the PD4060 power center near the middle of the trailer. I plan on disconnecting the existing battery negative ground connection, running my new ground wire from the new negative busbar (at the new battery bank location in the under bed storage in the front of the trailer) to that existing ground connection on the trailer frame. I'm just confused about what wire gauge to use. It seems like 4/0 or 3/0 are the best options. It's about a 6 foot run through my front wall, out of the bottom of my pass through storage, and then to the frame connection.
I have 3 possible 120 volt power sources. Shore power from a 30 amp pedestal that has a breaker. A 2000 watt Champion inverter generator rated 2000 surge and 1700 running. A 4000 watt Wen inverter generator rated 4000 surge and 3500 running. I am in Colorado year round now but eventually summer only and winter in AZ. I will be at high altitude most of the time so my generator outputs will be lower. I don't plan on running generators unless absolutely necessary or using shore power.
A 30 amp breaker in between my shore power inlet and the MultiPlus would be good but I am having trouble finding a small set up. It seems that since my generators won't be exceeding 30 amps and shore power hook ups usually have a 30 amp breaker that I could forego a 30 amp breaker in between the shore power inlet and MultiPlus. Would that be OK? Has anyone else gone that route? Otherwise I have a Midwest Electric 30 Amp AC disconnect I could use or Square D makes a couple 30 amp load centers that would work. Carling Technologies also makes panel mount 30 amp breakers. Those are the best options I've found. I'm open to suggestions that are hopefully small and affordable.
I'm wiring the DC to the MultiPlus with 2 x 1/0 as recommended in the service manual with a 400 Amp Class T fuse in between the positive connection bus bar and the MultiPlus. I will run a ground from the negative load bus bar to the chassis. From what I've read it sounds like the chassis grounds for the controllers and the MultiPlus should run to the negative load busbar which is grounded to the chassis. Correct? I'm not certain what size wire is needed for the controller and MultiPlus chassis grounds. For the negative busbar ground I understand it would need to be wire that can handle 400 amps which is 4/0. I think ABYC frowns on using 2 x 1/0 since each conductor should be able to handle the 400 amps. I believe Victron is OK with the wire being 1 size down which would be 3/0. Is that correct? I have posted about this connection before. My trailer has 3 ground connections. One at the front triangle battery location for the negative battery terminal. One at the factory negative 12 volt load busbar located in a underbelly compartment right behind the front triangle. Another at the PD4060 power center near the middle of the trailer. I plan on disconnecting the existing battery negative ground connection, running my new ground wire from the new negative busbar (at the new battery bank location in the under bed storage in the front of the trailer) to that existing ground connection on the trailer frame. I'm just confused about what wire gauge to use. It seems like 4/0 or 3/0 are the best options. It's about a 6 foot run through my front wall, out of the bottom of my pass through storage, and then to the frame connection.