Is this your proposed setup?Ok this is a multipart question.
I am planning on running a 120v subpanel which will then connect to a Nema outlet and plug that will be used to connect the Multiplus to the grid as needed. I elected to use 10/3 wire (30 amps) due to the cost of 8/3 ( 50 amps).
From the Multiplus, I will take the AC out and place in a distribution panel which will go to numerous locations in the house.
I am aware of the need to separate the neutral and ground on the subpanel in order to avoid what has been called objectionable current.
The Multiplus requires a ground. Would I be able to attach it to the ground in the outlet which houses the Nema plug since it ties back to the subpanel and then back to the main?
Does the AC output of the Multiplus feed back in any way. In other words, if there is a short in one of the lines from the distribution box from the Multiplus, does it feed back through the unit to the AC source, the metal case ground of the Multiplus, or is a separate ground feed needed?
What wattage is the Multiplus? 3K?
I have two comments and one concern
Comments
1) The breaker in the sub panel should be 30A. (That is the max the 10AWG can handle)
2) Be sure to program the Multiplus to limit the input current to 30A or you are likely to pop the breaker in the sub-panel.
Concern:
When the NEMA plug is unplugged the Multiplus and it's output circuits are disconnected from earth ground.
Yes, you can ground through the plug, but as mentioned above, there is no ground when it is unplugged. Is there a reason you have the plug and receptacle? This appears to be a stationary install, why not hard-wire it.The Multiplus requires a ground. Would I be able to attach it to the ground in the outlet which houses the Nema plug since it ties back to the subpanel and then back to the main?
The multiplus outputs are well isolated from the inputs. However, I would feel a lot better if there was a permanent connection between the critical load panel ground and the ground of the rest of the house.Does the AC output of the Multiplus feed back in any way. In other words, if there is a short in one of the lines from the distribution box from the Multiplus, does it feed back through the unit to the AC source, the metal case ground of the Multiplus, or is a separate ground feed needed?