email is not working, I assume you mean by calling them? Anyway to get support in this Forum?Don't wait keep trying.
email is not working, I assume you mean by calling them? Anyway to get support in this Forum?Don't wait keep trying.
Well, I hear what you are saying but if you think you can buy a victron system with split phase and a capacity of 13kw for $4800, please provide the link!!!!! and I will spring for the MPPT!skipping all the drama... buy a victron, a midnight solar, a magnum, a morningstar, a Schneider, a xtant (however you spell it) etc. everybody with these chinese inverters encounters problems and its one post after another trying to figure out why you have no power. buy a top tier and be done with it. you waste more time and money trying to figure out why a 1200 USD inverter does not stack up against a 2400 USD inverter of the same rating...
HELP!!!!! SOS!!!!
prices i quoted were averages from about 5 or 6 years ago. i understand that prices have all skyrocketed, even the chinesium inverters have went up. but you would think that if its really that important you would simply go with the quality route to begin with. buyers remorse for low priced items is just as real as buyers remorse for high priced items... the difference is when you pay a lot you expect a lot and the companies in order to justify their hgiher costs do a lot.Well, I hear what you are saying but if you think you can buy a victron system with split phase and a capacity of 13kw for $4800, please provide the link!!!!! and I will spring for the MPPT!
I’ve been running two SolArk12K’s for a year and a half totally off grid- 17 MWh produced last year alone. Other than minor glitches, mostly my fault, they have left me without power about three or four times for two minutes each. Had one doa dongle. SA made it right quickly.I had a very similar experience with my 6500EX a few months back. Reached out to Signature Solar to start the RMA process and have been getting the run around ever since! My 6550EX fried overnight (didn't hear any loud boom) but SS is trying to pin this on me. Absolutely no help at all. They want me to send it back to them and charge me for repair. What kind of service is that?!
I'm moving on to Solark, whom I hear actually supports their products.
They both look correct to me, pos is on the left. Same as mine.Um… you have positive on the left on the left inverter, and positive on the right on the right inverter… at lease the red and black cables are reversed…
Yup, the angle of the picture made it appear that way.They both look correct to me, pos is on the left. Same as mine.
I see that F05 is “output short circuited”. For the inverter that you can get to turn on, can you turn off the AC Out breaker and see if you still get the error?
I see that F05 is “output short circuited”. For the inverter that you can get to turn on, can you turn off the AC Out breaker and see if you still get the error?
That's a very important new information for me!If you reapply AC input before pass-through relay has released, you will likely get a 'boom' due to inverter still connected via pass-through relay to AC input terminals and inverter is now out of AC phase with grid. It is like you applied grid to AC output of inverter, which is the error code you got.
Beside the (manual) double pole AC-in breakers (together with an AC-in main breaker) I also placed contactors to connect all AC-in's to the grid for all AIO's only in case AC-in (grid) is really required if batteries are nearly empty and no solar. I control the contactors via smart home rules depending on data getting from SolarAssistant via MQTT. It would be easy for me to implement a delay for this contactor rule to prevent the "boom" situation because of to fast AC-in switching.AC inputs for split phase should be fed via a double pole AC input breaker so both inverters get AC input simultaneously and simultaneously get disconnected from AC input when breaker is opened.
All this is also why you should not use an automatic transfer switch on AC input of inverter to switch between generator and grid. You must ensure inverter's pass-through relay is open before changing AC input source.
So let’s say your grid connection has various protection devices (reclosers or sectionalizing loop auto switches) such that gird can be lost for 1-2 seconds then be restored multiple times over the course of say 5 min? During a storm I can count the reclosings of my circuit knowing that if we hit that 4th time it’ll be lights out.If you remove AC input from grid it takes a few seconds for inverter to recognize AC input has gone open circuit.
During this period the pass-through relay remains closed with inverter AC output showing on inverter AC input terminals and the inverter starts to drift off frequency and phase from grid which is not providing phase sync mastering for inverters.
Inverter will recognize when AC input is open when it drifts too far off frequency or it lacks getting phase corrections from AC input sinewave zero crossings for some period of time.
If you reapply AC input before pass-through relay has released, you will likely get a 'boom' due to inverter still connected via pass-through relay to AC input terminals and inverter is now out of AC phase with grid. It is like you applied grid to AC output of inverter, which is the error code you got.
Normal AC input connect process is with pass-through relay open, the inverter slowly syncs to AC input phase and voltage. After achieving AC input match it closes pass-through relay putting inverter output in parallel with AC input. AC input is phase and voltage master for inverter.
Whenever pass-through relay is closed, inverter is slave to AC input. Whenever pass-through relay is open the inverter is its own master.
If you are running inverters as series stacked 240/120vac configuration, they are slave to their respective L1 or L2 AC input phase when AC input is present.
When no AC input is present, one inverter becomes 180 deg phase reference master for other unit.
AC inputs for split phase should be fed via a double pole AC input breaker so both inverters get AC input simultaneously and simultaneously get disconnected from AC input when breaker is opened.
All this is also why you should not use an automatic transfer switch on AC input of inverter to switch between generator and grid. You must ensure inverter's pass-through relay is open before changing AC input source.