Followup: I let the the system drain, in a organic way, discharging the EG4 battery low. I was curious to see what would happen.
At around 5AM, and at exactly 5% charge [Batt Type LI/01, ethernet/RS485 comms cable plugged-in and working as normal], with no incoming solar [yet], the GroWatt inverter turned off. So everything that was on AC power, turned off. Including the fridge/freezer. The GroWatt was still basically on, with Error 4 [low battery].
I realized, as the sun came up, and the GroWatt started charging the EG4....
@RichardfromEG4 WHY did you name the recently-released MPP LV6548-style inverter all-in-one, the SAME as the battery? Same logo and everything? If it's a SS exclusive product, come up with a unique name.
...that as the charge level crept, to 6%+, the Error 4 was not clearing by itself, and so the inverter remained off. There didn't appear to be any setting in the GroWatt to set the 'ON' point percentage of the battery. I reasoned, the ON-point would be some threshold determined by the EG4 BMS. [No useful documentation. See prior posts].
The sun came up, 50 watts.. 100 watts... 150 watts. I threw on the generator to speed things up and to instantly bring back AC power.... then, remembering the idiocy documented below, I immediately shut it off before the GroWatt had an opportunity to switch to Grid/Generator:
@RichardfromEG4 WHY does the BMS tell the GroWatt what the
Maximum >AC< Charging Input [Setting #11, the amount of power, in battery-charging amps, to use from Utility/Grid/Generator] should be? The EG4 BMS has
no business dictating that. Yes - it can - for the TOTAL charge input, Setting #2, which in turn, limits Setting #11. Which means, that if ONLY setting #2 is set by the EG4, the battery will never receive more amps than the BMS wants. Someone with extremely limited practical understanding [my first thought was joe the janitor, although senior janitors tend to have more common sense than everyone else], programmed the BMS to vary the maximum AC input, when this should ONLY be set by the User/System Installer who knows what their Grid/Generator connection is capable of. Very few - none, if any - mobile off-grid set-ups are going to have the suggested 10kw generator [for AC Input], in the GroWatt manual, that some air-head must have assumed was reality, and thus told the EG4 Battery BMS it should set automatically. Setting it from the BMS programatically, equates to the User being locked-out, of setting it through the front panel. And, the User can only temporarily reduce #11, through a convoluted use of the GroWatt Shinephone App and supplied WIFI Datalogger, to set it to something more reasonable [like 10 or 15 amps for a 3kw generator. 10amps @ ~52v, equating to roughly 520w output from the Generator, being a typical idle-production of a 3kw inverter-generator].
The non-solution 'solution' to that, is for the user - your customer - to use USE2 battery setting in the GroWatt. Then you lose all percentage and other useful BMS reporting.
Otherwise, with the LI/01 setting, when at any level of discharge below 90%, the EG4 will use the BMS comms cable to tell the GroWatt that setting #2 is to be 50 amps, and that setting #11 - something it should not touch! - is 40amps [2080 watts]! Somewhere above 90%, the EG4 tells the GroWatt that setting #2 should now be 12 amps, and that setting #11 should be 12 amps [or maybe #11 is reduced by the GroWatt when #2 is restricted]. I have manually set #11 through the app, to 10 amps, run the generator and observed the correct 10a@52v being put into the battery [minus around 0.68 amps, the self-consumption of the GroWatt]. Then, on a later cycle when the battery discharged below 90%, I have witnessed the EG4 BMS change #11 back to 40 amps! Nothing was restarted in that time period, and I have seen it more than once. So for sure, the EG4 BMS is presently telling the GroWatt what #11 should be, effectively locking that setting out from the front panel.
However, the above is as I understand, only from my limited perspective & observation.
I manually set #11 to 10amps, again, and started the generator. When the combined solar charging and grid charging brought the EG4 Battery
level to 15%, the Error 4 cleared, and the AC Power/Inverter turned back on.