My solar Pergola build

It is days like today that truly made me build the pergola.

Heavy clouds rolled in by 10 am. The Enphase system was down to only 1/3 of it's normal production for half the day. Only got an hour of decent sun after noon. The total from the Enphase was just 11.1 KWHs.

Meanwhile, the Pergola produced plenty and the battery was still fully topped up. Both the garage roof and pergola managed to go to float by 2 pm. And they kept the battery full until after 4 pm, just like a sunny day.

Since the Enphase was not making as much, the DC systems did stay producing longer so they made 3.6 KWHs on the garage and 9.98 KWHs on the Pergola, even though they still went to float.
 
And today, even the extra panels are just not enough.
It has been raining since last night, not really hard enough to be a good wash, but hopefully it will help get some of the ash and gunk off of the older panels on the house and garage roofs. Here is a view of the pergola from my patio.
IMG_6723.jpg
The water is just kind of beading up on them. And yes, the sky is grey with all clouds in all directions. Here is the Victron overview page.
IMG_6724.PNG
The garage roof is just over 5% of STC power and has produced 1.7 KWHs by 3:15 pm. The Pergola is getting almost 6% of STC power and produced 3.9 KWHs so far today. Yeah, that's not much, but it is a lot more than nothing. The peak power reported by Victron hit over 1,200 watts for the garage and 3,400 watts on the Pergola. But those were very short lived peaks. The rough 15 min averages were more like 800 and 2,000 watts respectively.

The Enphase system averaged just 100 watts for the last 15 minutes. It peaked to 1,700 watts for the 1:45 to 2:00 pm 15 minute time slice. The interesting part is the DC systems are doing far better than the Enphase in these horrible conditions. The Enphase system has only made 3.7 KWHs so far today. It may be 1 or 2 15 minute slices behind, but with the last 2 slices being just 200 and 100 watts total coming in from the array, it won't make a big difference. The 4,000 watt pergola array alone made a good deal more energy than the 4,800 watts of SilFab panels on the Enphase system. The 2 DC arrays together have made 5.6 KWHs in this crap weather. That is getting close to 1 sun hour (0.93 if you want to be picky) (0.85 for the garage roof and 0.97 for the pergola). The Enphase system is at just 0.77 sun hours.
 
Yesterday was certainly crap weather for solar production. I decided to let it go after just the 1 hour of grid charging at 42 amps from 3 pm to 4 pm. SC already has the data posted for the weekend. As bad as Saturday was, I still ended up net exporting 6.87 KWHs to the grid, but Sunday was very bad. That battery was full 92% at 2:30 PM on Sat. On Sunday, running the house off batteries almost the entire time, it was pulled down to 52 volts when the sun came out. That is a typical overnight discharge. That voltage at low current works out to about 55% SoC. We didn't get a lot of sun and the voltage just kind of hung there, only getting up to a high of 53.6 charging from just the DC systems. The Enphase system hardly ever made more than the house was using, so the house was also taking some from the batteries.

By 3:00 pm the battery bank was back down to 52.8 volts (about 55% SoC). It probably would have made it through to 9 pm, but my son was home gaming on his PC again, so I did the hour of grid charging at 42 amps. That made the grid consumption for Sunday 3.4 KWHs. I did it then as it is "Super Off Peak" rate 27 cents instead of "Off Peak" 30 cents overnight or the "On Peak" 43 cents from 4 pm to 9 pm.

That boost did get the battery up to 54.4 volts. That works out to 78% charged. 78 - 55 = 23% increase. That would be 8.3 KWHs. About 2.3 KWHs came from the grid. The other 6 KWHs came from the DC systems. Also, since the XW was pulling from the grid in charge mode, it was not taking any of the power from the DC systems.

Like I said, my son was gaming, and my girlfriend started another load of laundry so the washer and dryer were then both running. We sucked down all of that 8 KWHs in a bit over 90 minutes as the sun went down and no more solar was coming in. The XW was pulling ove 30 amps from the batteries for several hours. By midnight, the battery had dropped all the way to 50.5 volts, and before the sun came up this morning it had dropped all the way to 49 volts even where the XW is set to stop inverting. That is 3.5 volts per cell on my 14S NMC battery bank. The JK-BMS reported it as 3% remaining, but that is wrong. 3.5 volts at no load would be 14% remaining. The last time it got this low was on Christmas day, just over a month ago. The XW set the DC low error event.

Sunlight started hitting the panels at about 7:15 am, and the XW was no longer pulling from the batteries, so the voltage sat flat, and finally started climbing around 8:15 am. Th DC arrays were making over 1,000 watts by 9:15 am and the XW started powering the house again. The Enphase array was making 800 watts as well. The weather forecast is calling for sunny to 11 am, partly cloudy from noon to 5 pm. Will that be enough for my system to get fully charged again? The battery needs about 28 KWHs to get charged up. From 6KW of DC panels only, that would need 4.7 sun hours on both arrays. And that is with the Enphase making enough to run the house all day.

Without the pergola, I probably would have been on grid power for most of Sunday.
 
The sun is cooperating. It is after 3:30 and the sun is starting to set, but the clouds never rolled in today and I am still seeing over 2,000 watts from the DC systems. Over 500 watts from the garage roof and over 1,500 watts from the pergola. The power from the pergola peaked over 3,400 watts. The Victron app shows a max power of 3,748 watts, but that was a short peak, the 3,400 watts lasted for several minutes. The Victron app also shows the garage roof peaking to 1,749 watts, but it must have been very short, I can't find any peak that high in the trend graph. Best I found was a minute around 1,400 watts. That is still quite good at 70% of STC rating. The pergola was up closer to 85% of STC rating. That has to be some bifacial gain. The Enphase system best 15 minutes hit 3,300 watts or 69%, very close to the garage roof.

The battery is now close to 80% SoC 55.5 volts (at the XW-Pro) or 3.96 per cell, so it has charged up about 60% from just the Victrons. I could have let some of the extra Enphase power help charge, but I saw enough power coming in and wanted to see what it could do on just the DC charging. The JK-BMS SoC reading is now showing 75% SoC and it started at only 3%, so it's doing better than usual at keeping track.

So far the Garage pushed 5.89 KWHs and the Pergola did 14.62 KWHs. That is 20.5 KWHs sent to the battery with basically load on them with the XW sitting in standby. That is only about 57% of capacity. Going by voltage along is certainly not perfect, but being within 5% is not too bad. Some of my voltages are from the JK-BMS, some are from the Victron App, and some are from the XW-Pro status page. They all differ a little, and even with the slope of the NMC cells, it is enough to be off a few percent on the SoC estimate. If I use the minimum and maximum voltages from just the Victron App. it went from 48.8 volts up to 55.1 volts. 48.8 / 14 = 3.49 per cell or just 8% SoC based on a no load voltage chart. 55.1 / 14 = 3.94 volts per cell looks like 74% SoC. But the high voltage was hit with over 2,000 watts of charge current which does pull it up some and the low voltage was before the sun came up and the XW was drawing power to run the house.

I'll post the charge curve images and energy totals after the sun goes down later tonight. The XW is starting to draw a little from the battery, but the DC system is still charging as the voltage just went up another tenth.
 
The sun is truly down, no more power from any solar panels. The house is being run by the XW-Pro off of the battery bank.

Here is the Enphase power trace for the day
Enphase01-27-25.JPG
As you can see, we certainly had clouds moving across. There were quite a few power dips all day. The system had produced 17 KWH's before the bad weather moved in, and only produced 14 KWHs today. Here is the XW-Pro battery summary trace.
XW-bat_01-27-25.JPG
You can see that I did not do any real charging from the XW. But all of those little wiggles that did go to charge ended up pushing 53 watt hours to the battery. But the wiggles below also used up more, so it is a wash, or even a bit of a loss. And here are the history pages from the Victron App. You can see what happens when there is room to accept all the energy.

Garage Roof IMG_6740.PNG Pergola IMG_6741.PNG

Friday, the 4th bar in each, the system was fully charged about noon, and they spent the rest of the day in Float mode. Saturday, we had a lot of clouds, so the Enphase system did not help much and the XW had to use a lot of battery power. So the charge controllers did not end up in float very long, but they did still get the battery full. Then Sunday, bar 2, the production was so low, the system never got close to full charge with the charge controllers both staying in bulk all day. The garage roof only managed to make 1.79 KWHS and the pergola did 4.01 KWHs. The pergola was the only array that hit 1 sun hour. The Enphase system managed just 3.9 KWHs on that day.

Then today, even with all the clouds moving past, we had good sun between the clouds and it appears some extra reflections as well. The Garage roof did pretty good to pull in 6.23 KWHs. That is 3.12 sun hours. The Enphase system did only 2.92 sun hours making 14 KWHs from 4,800 watts of panels. But again, those new Hyundai panels and the new Victron charge controller on the pergola did the best. The final total hit 15.5 KWHs from just 4,000 watts of panels. That's 3.88 sun hours. Total solar production from the DC panels came out to 21.73 KWHs, over 50% more than the 14 KWHs that the Enphase system produced. We still did not top out the battery system, but we still produced a solid 40% more than the energy the house used so the battery will have no issues making it through the night. And if we get sun anything like today, the system will be topped out before 2 pm for sure.

The Extra Enphase production was also exported to the grid for credit. That export looks to be about 8.5 KWHs. It won't be posted on SCE's web site until tomorrow. Had I left the PLC commanding the XW to charge, that surely would have topped up the battery today. But then the charge controllers would have gone to float and I would have thrown some energy away. This way, I got some credit with SCE, and used all that the two Victron controllers could produce. And I will do the same tomorrow until the battery does top out again. The peak power reported by the Victron app hit 1,749 watts (87.5% of STC power) on the garage roof and 3,748 watts (93.7% of STC power) on the pergola. Those are some amazing numbers. I am sure the systems will be topping out the 35 amp and 70 amp limits of the charge controllers in spring. My 130 foot run of #10 wire sure does not seem to be hurting the production on the pergola. I measured just a 3 volt drop (just 1.6% of 190 volts) at 3,000 watts a few days ago.

Just for some giggles... Here is the So Cal Edison daily energy usage for this billing period so far.
SCE-Jan-Feb25.JPG
Even with the weak Saturday and the bad Sunday, I am still averaging over 10 KWHs of export each day so far. The predicted bill is a credit of $51 if I keep up this rate. Not too bad for the dead of winter for Santa Clarita.
 
Last edited:
As expected, the system had no issues getting fully charged up today. Both Victron charge controllers went to absorb at about 2:30 pm. I am not 100% sure if it is a voltage drop issue or a calibration issue, but the new 250/70 charge controller is always hitting absorb first. It was hitting it almost an hour earlier, and it would never do "re-bulk" like the smaller 150/35 unit. I raised the bulk voltage 0.08 volts to match the difference I was seeing at 22 and 50 amps of charge current respectively and now they hit bulk much closer, but the new one is still always first. Today it was only a couple minutes and I saw them both in absorb together.

At first I doubted it was voltage drop on the wires as I have #6 going to the older 35 amp controller and a shorter run of #4 on the new 70 amp unit. The total runs are only about 5 feet from the bus blocks. The 35 amp is going through a 50 amp breaker and the 70 amp is through a 100 amp breaker. The wiring should all be a few milliohms at most. But the #6 on the old unit is the super fine strand Windy Nation battery cable while the new controller got #4 battery cable I bought at our local auto parts store. He assured me it was pure copper cable. But I just id a measurement with my Fluke meter and the drop across the cables is showing a tiny bit more resistance on the thicker #4 wire. The currents are quite different right now as the new charge controller is targeting a slightly higher absorb voltage. So I measure the current and the voltage drop and calculated the resistance. The current on the larger controller is measuring 6 times the current of the smaller controller, but the voltage drop is almost 7 times as much. I get just 6 mv of drop at 2.1 amps on the old controller. That calculates out to 2.86 milliohms. And I am getting 47 mv of drop at 13.2 amps on the new controller. That works out to 3.56 milliohms. And this is the drop on just one cable. The total voltage drop will be double this from the bus blocks to the charge controllers. That is 33% more resistance on a wire that should be a thicker gauge. It must be copper clad aluminum. I am going to order some more Windy Nation wire to change it out. The drop is small, and it certainly is not causing a big problem now. But I am a bit concerned in spring/summer when t will be cranking the full 70 amps. That will be dropping 0.25 volts on each cable, or a half volt total between the charge controller and the bus blocks in the breaker box. That will be 17 watts of energy lost as heat in the cables, along with a 0.25 volt error in the battery voltage reading. This will obviously make it go into absorb very early.

SCE posted my Monday usage data. I exported 7.91 KWHs while the solar covered all my loads and charged the batteries back up to 80%. Today, it looks like I am exporting more like 12 KWHs and the batteries are full to 92% before 3 pm.

Only issue... The XW did the odd oscillation again last night.
 
Damn
I was just thinking about this. Our previous events happened on the same day (hours apart), but my system was fine today.
I just sent off two more emails to Schneider. This one was odd, and it did it a second time in the same day. The first time was very early this morning (I was still up at 1:44 am). I looked in the status page before stopping it, and none of the energy control icons changed from grey. But it was showing the current going positive / negative up and back, and it seemed a bit faster this time. So my "Ramp Rate" change certainly did not seem to have an impact. But then I turned on charging, set it to 20 % and it stopped swinging right away and just stayed charging. I then disabled charging and it went right back to grid sell to cover my loads in the main panel like nothing ever happened.

But now tonight was a different story.

At 5:18 pm, I got back home from the store. I went into the garage to check on my E-Bike batteries I put on charge, but then I could hear the XW-Pro making that pulsing hum noise. The display on the front stayed showing KW as if it is inverting, but the power display was going anywhere from 0.00 to over 4.20 KW of inverter power. And when it went to zero, it was actually pushing 30 amps+ of current into the batteries, even though charging is disabled in the XW.

The cycles seemed like less than 1 second this time, and what's worse. I COULDN'T STOP IT!!

My usual trick that made it stop all failed. I flipped my bypass breaker to take the load off the output side and put the subpanel back to the grid panel feed. It still didn't stop as the input side was still on the grid. I sort of panicked at this point and hit the power switch on the front panel. I heard the relay click and the display went to "OFF". At that point, the Gateway lost comm with it as well. It didn't want to power back up. I was pretty sure it was hold Power and Equalize for a few seconds, but it just sat there "OFF". How long do you need to wait? I was sure I held it for 3 to 4 seconds, and nothing. I power cycled the grid power fed and even the DC battery power. Then when I held Equalize and Power, after 4 seconds, when I let go, it switched to "STB" standby mode. Then the Gateway could see it again. I had to then go in there and switch it to operate and turn grid support and grid sell back on. But of course it had to run down the 5 minutes (300 second) timer before it stated feeding loads again. It came up in AC pass through and the relay kicked in, so I took my backup panel out of bypass. With the older firmware, it would power backup loads while waiting for the 5 minute grid qualification, but now it stayed in just pass through for the full 5 minutes.

Once the time ran out, it went back into grid sell and is once again working perfectly like nothing ever happened.

Looks like I will be reloading the firmware again and doing a full reset to factory defaults to see if it makes any difference.

This time I took a picture of the screen as I also recorded a video for Schneider.
IMG_6750.jpg
 
The few events I've seen I have stopped either by cutting grid input to the XW or by disabling grid sell. Removing the loads didn't do anything for me.

I opened a case with Schneider, they've emailed twice asking for more details. But it felt like stall tactics. They asked for my email address. Yes, they requested my email address in an email...
 
This is the "Show and Tell" area, so I am starting a new thread about my next project. The plan here is to add nearly 4,000 watts of panels to my system to get close to 10 KW of total PV panels online. I have a HUGE thread here already from when I added a Schneider XW-Pro to add self consumption time shifting and backup power to my Enphase grid tied system. That thread is out to over 1,900 posts. Here is the link if you want to skim through that.


After adding the XW-Pro and 18 KWHs of Chevy Bolt batteries, I added another 18 KWHs of battery to push it to 36 KWHs of storage and then added 2,000 watts of DC coupled solar panels to try and keep them charged. But with poor weather and more loads, it is just not keeping up anymore. I designed a very streamlined structure to support a 3x3 array of panels. I am still adjusting the exact size of the roof as I have not purchased the panels yet. I am looking in the 300-400 wat range per panel. I am waiting for a reply from Greentech Renewables, but if i don't hear back soon, I may order from San Tan Solar. The y have a few panels in the under 40 cent per watt range. For size and weight distribution with my design, I am looking at the "60 cell" form factor like my original Sil Fab 300 watt panels. The new versions about that size ae now over 350 watts at 1 meter wide and 1.7 meters long. Going 3 x 3 with that size panel, it ends up about 12 feet x 17 feet of panel. At 50 pounds per panel, it is 450 pounds of PV panels alone. Add in the racking and the wood "rafters" and it will be nearly 600 pounds. I don't have to even think about snow load here, so that is a good thing. In deck design, a single 4x4 post can support up to 600 pounds. So 4 posts has a reasonable safety factor. The 4 posts are at the corners of a rectangle just 8 foot x 10 foot. So the solar roof will overhang the 8 foot depth by a bit under 2 feet out the front and back. But in the long direction, it will be just over 3 feet out each end past the posts. Since this is in my back yard, it is north of my house. I am placing it as far west in my yard as I can, leaving room to be able to get the lawnmower behind it. That is the end of my house that is only single story. In the morning, it will get some shade from the second floor on the east end of the house. In spring to fall, there won't really be any shadow issues with this placement. But to get it up out of the shade in winter, the low end posts are 8 feet high, plus 6 inches on the concrete piers. The taller north end posts are 11 feet high on top of the piers. I drew it up at 1/2 inch - 1 foot and it looked like no big deal. But I stood up one of the 11 foot posts today. OUCH. That is higher than I pictured in my head, but it is correct. check out where the sun is hitting it in the pictures.

Here are the pre-cast concrete piers from Lowes.
View attachment 265222
That is over a cubic foot of concrete, and they are HEAVY. They are meant for a deck, but I asked and they are also acceptable for "shade structures". I measured out the area, and of course, my yard is not square, and my house is not perfectly straight in the lot. Hmmm. I did my best, and I got it within 1/4 inch of square to the back wall of the house. so it should look fine. I dug the holes. I wanted to go down a full foot, but now I know why I can't grow decent grass. The "dirt" is mostly hard clay with sand in it, and not even 8 inches down, I was hitting hard rock. I managed to get all 4 of them in place and sunk 6 to 8 inches to get them all at the same height.
View attachment 265221 View attachment 265220
If this was in an open field, I would want them deeper to deal with wind, but the structure is all going to be shaded from wind, and with my rock hard ground packed in around the pyramid shape, these are not going to move. A day after I packed the dirt in around one, I tried to pull up on it with a lever. It felt like I was just pulling against a concrete slab, and my lever was over 8:1 and I still could not make it move at all. So I am not going to try and dig them any deeper. I would need a jackhammer to go lower into the rock.

Here are the two west end posts up in position. They are being held vertical by temporary braces and stakes for now.
View attachment 265219 View attachment 265218 View attachment 265217
At 7 feet off the ground, I will have level 2x6s connecting the 4 posts. Those will have 45 degree braces to the posts as well as between each horizontal bean inside the corners. That will keep everything square and I can then remove the temp braces holding the posts straight.

I took these pics at 4 pm, my rooftop Enphase system was down to just 200 watts from 4,800 watts of panels. In the middle of those 3 pics, you can see where the sunlight is hitting the top 4 feet of the taller north post. The south end post had just gone into shade. Due to how the shade moves in, I plan to split this array. The bottom south most panels are probably going on microinverters as they will have shade issues from time to time. The next row of 3 panels will be in series, and run in parallel with the top 3 panels that are also in series. Depending on the panel voltage I get, I hope to be able to use a 150 volt Victron and not have to get a 250 volt as the price takes a fair jump. 6 x 350 watt panels would be just over 2,000 watts, and push about 40 amps into my "48 volt" battery bank. I will get a 60 or even 75 amp charge controller in case I decide to add another parallel group string of 3 panels up on the wall, or instead of the microinverters on the bottom row. Whatever panels I get, I will likely buy a few extra that I could just lay against the wall and wire in for winter. I still have my BougeRV charge controller that would be perfect for that use.

Bridging between the 8 foot and 11 foot posts, I will have a 16 foot 2x8 that end up tilted 16 degrees towards my house. Due to the angle, it will extend less than 3 feet past the posts. I may also add a few braces of 1x4 between the level 2x6 and the long tilted 2x8. There will also be 6 2x4s between the long tilted 2x8s where the 6 Iron Ridge rails will go across. I was hoping to get away with the 11 foot rails, but that depends on which panels I get. The 375 watt panels I am looking at are listed at 41.34 inches wide. Put 3 of them against each other and that is 10 foot 4 inches. So I would have 8 inches to allow for 1 inch between panels and a couple inches for end clamps. But if I go with the 430 watt panels, they grow to 44.6 inches wide, and just the panels alone is then 11 feet and nearly 2 more inches, even with no space between the panels, OOPS!! I can't find anyone who sells 12 foot rails, they jump to 14 foot. The price difference is not huge, so I may go with the longer rials so I can go with larger panels later if I decide I need more power. I really would like 400 watt panels.

I had thought about also tipping it a bit more west for evening sun, but the heading of my house is already about 25 degrees west, and I think that is plenty far as I watched the sun set today. So the other pair of posts are exactly the same as the first pair. The solar panel roof will just be leaning towards the house. The low end does go a little lower than the edge of the house roof, but it is over 10 feet away. Even on the winter solstice, the sun was on the closer 8 foot post for over 5 hours. It gets better sun than the panels on the garage roof. All the panels I am looking at are the "Half Cut" type, so on that bottom row, even if the sun blocks the lower half, the top half will still produce well. The upper end of the lowest panels will still above and north of the lower posts. The 375 watt panels are just 70 inches long, less than 6 feet. So the gap between the first and second row of panels will be 2 feet inside of the space between the 2 posts standing in the pics.
my solar awning has 7 x 400 watt bifacial panels and conveniently this string is around 240v dc. I feed this into our electric hot water service with a controller i made. The thermostat runs a contactor with 3 n/o contacts in series with a 50watt incandescent light across it, as you know switching dc is not user friendly! once heated energy can ge diverted to a grid tie inverter in summer or in winter a heater. a works in progress!
 

Attachments

  • IMG_5516.jpeg
    IMG_5516.jpeg
    598.4 KB · Views: 22
  • IMG_5515.jpeg
    IMG_5515.jpeg
    501.8 KB · Views: 23
my solar awning has 7 x 400 watt bifacial panels and conveniently this string is around 240v dc. I feed this into our electric hot water service
If I understand this correctly, you have the solar energy heating your hot water as the primary load. That is a different setup. Most people have hot water as a dump load when there is extra solar. In a colder climate, I can see that being a good use case.

Typically, my gas bills have been very low, but this has been an unusually cold winter for us in So Cal. My furnace has been running far more than normal, and the hot water heater and the clothes dryer which are both in the non heated garage also end up using a lot more gas to do their jobs. Diverting some of my extra electric to heating the water and maybe some space heating as well could be a help. On the flip side though, our summers are very hot and my garage can stay close to 100F (38C) so the water heater and clothes dryer end up using very little, and of course, the furnace does not run for 6 months straight.
 
iPhone weather shows it as "Cloudy" this morning and the sun popping out to "Partly Cloudy" around noon. They sure got the cloudy part right. The entire sky just looks white. It is hard to even tell where the sun is behind it all. It is only 10:15 am when I took these pics, but you get the idea.

IMG_6759.jpg IMG_6761.jpg

At least the rain over the weekend did a good job cleaning the panels off. The garage panels have not looked that nice in a long time.

The SilFab/Enphase system is only putting out 500 watts from the 4,800 watts of panels, that's a poor 10%, even at this early time of day. Yesterday, that array was making 2,500 watts at the same time.

The garage roof with the 2,000 watts of NewPowa and BougeRV panels with the Victron 150/35 charge controller was making 257 watts. That is doing a bit batter making almost 13%.

And the Pergola with 4,000 watts of Hyundai panels and the Victron 250/70 charge controller is producing just over 600 watts. That is a bit over 15% of the array's STC power rating. This is still poor production, but it is doing 50% better than the Enphase connected array.

My battery is down to just 50% SoC right now so I did put the XW-Pro into charge mode, but at just 5% (7 amps). This is causing a small grid draw, but this is also the cheapest time of use rate right now. The PLC is in control, so if the Enphase system does start to produce more than the house is using, it will raise the charge current to follow the power coming in. But if it then falls back to making 400 watts less than the house draw, it will stop the charging. After 4 pm, when the Enphase is making less than the house needs, it will also start to draw from the battery to cover the loads for the highest time of use block until 9 pm. I hope I get the battery charged up enough to cover it. The weather for tomorrow looks to be pretty similar.
 
I did a bit of an inspection after all this rain, and so far everything looks perfectly fine. I was a bit nervous the concrete blocks might settle into the ground under the weight, but the ground is so hard, it does not seem it has moved at all. I am sure glad I got all the wood stained and sealed before these storms. The water looks like it beads up and runs off like a waxed car.

The 1 inch gaps between the panels let a lot of water pour down in those lines. It actually cut grooves into the ground straight under the gaps. It's not just the rain in that slot, it is also all of the water from the next panel above all pouring down through each slot.

I did do one change tonight. While cleaning up I found a bit of the extra #2 Windy Nation cable I used to wire up the battery boxes and breakers. It was just enough to make the run from the New 250/70 Victron charge controller to it's breaker in the DC box. That should cure my voltage drop issue I was seeing between the two charge controllers. The #4 AWG that I had in there from the local auto parts store was basically junk. It was showing more resistance than the #8 Windy Nation cable I had on the other 150/35 Victron. True, it was running at half the current, but the voltage drop was way more than double. They claim this is pure copper wire, but I am betting it is copper clad aluminum. It also looks very thin for a #4 on the inside. The jacket is really thick, so it seems right on the outside. Lesson learned, I am not buying cable from them again. It was even more expensive than the Windy Nation stuff on Amazon. Only good thing is I was able to buy it a few blocks away. I will have to see what the voltages read tomorrow at full sun.
 
The new wire did the trick. Even at well more than double the current from the Pergola, the voltage readings on the two Victrons are now within 0.02 volts. We have some spotty clouds going by now, so the numbers keep changing, so it's hard to pin it down perfectly, but it is certainly way closer than they were with the auto store wire. I'll grab some screen shots off the Victron app after solar noon. I had the charge voltages set a little higher in the Pergola CC to compensate for the voltage rise, I should be able to get rid of that now.
 
I looked at near solar noon, and just caught peak power. As I was watching the numbers from the Victron charge controllers, the garage roof system switched to Absorb. Due to the 0.07 voltage difference in the settings, the Pergola system stayed in Bulk about 20 minutes longer. Even with that offset, it would go into Absorb first on the old cables. But now the voltage readings from both controllers stayed matched within 0.03 volts even with the Pergola at 44 amps and the Garage roof down to 17 amps. I will go back into the settings and reduce the charge voltages on the Pergola to just 0.01 higher than the garage roof. At no current (sun down) that is about the difference I am seeing in the readings. My Fluke 76 meter is showing the voltage at the charge controller battery terminals as exactly the same to that second decimal place. I have a 4.5 digit Fluke 8060A but it's at my work, I don't think I need to see millivolts for this.

Since I was home, I did go into the XW-Pro settings and manually set it to export at 16 amps from 10:30 am to 2 pm. Since the Enphase power also goes through the XW, it is smart enough to only add enough power to hit the set 16 amps. It started at about 1,800 watts at 10:30, but ramped down to just 1,300 watts when the Enphase system was at maximum power. Then it ramped back up as the sun started dropping again, maxing out at 2,550 watts at 2 pm just before the XW stopped exporting extra power. In total, it pushed about 6.5 KWHs of energy that was coming in from the DC systems on top of the extra that exported from the Enphase system. It held my utility meter right at 16 amps of export for the whole 3.5 hours. And I still had plenty of solar to top out the batteries to 93% and they didn't start to drop in voltage at all until 5:15 pm. The DC systems were in float for almost 4 hours before they went back into bulk as the sun went down. I could probably have pushed the full 16 amps for 7 hours even though it was not a perfectly clear day. The Enphase system produced 17.9 KWHs compared to the 20.2 yesterday. The two DC systems pulled in 19.1 KWHs even with nearly 4 hours of float.

Here is the battery summary from the XW-Pro today.
XW-bat_02-16-25.JPG
And the Enphase production.
Enphase02-16-25.JPG
And the production from the two DC systems. Garage then Pergola
IMG_6842.PNG IMG_6843.PNG
It's not easy to get these two to line up with how the Victron app scales the graphs. The pergola was making power more than an hour later, so the graph is squeezed to fit the whole production on the screen. And the vertical power scales are completely different. As the pergola system pulled the voltage a little above the float setting of the garage roof, the garage roof system just turned off. The offset was only 0.07 volts, but it certainly shows. The garage roof system is turned to near true south while the pergola is over 20 degrees to the west. But on this day, the power peaks are at the same time as it was effected more by the amount of clouds than the angle difference. That also shows in the power falling off early in the Enphase system as well. The clouds cleared a bit again after 3 pm, and the pergola system did go over 200 watts again to keep the voltage up out to 5 pm.
 
Today was not the best for sun, but it was pretty good. Since I was working from home again today, I was able to monitor the system and have a little fun. I still started the 16 amp export right at 10 amp, but instead of letting the PLC stop it at 2 pm, I unplugged the PLC and let it keep going. It was exporting at 16 amps all the way to 3:30 pm. Then I dropped it to 14 amps as it was starting to discharge the battery a little. Then I dropped it to 10 amps at 4:15. But then the sun was falling fast. At 4:40 I plugged the PLC back in to let it take control. Both Victron charge controllers still went into absorb and float for a while as I just couldn't push to the grid fast enough to keep up with the production rate. But it did keep them in Bulk and a lot longer than other days, and it was pushing a lot of float current as well. It is now 5 pm and we still have some sun out but the Pergola charge controller has already pushed 19 KWHs. A bit more than the 18.6 KWHs that the larger 4,800 watt on from the Enphase system managed. Even the garage roof did really well today pushing almost 8 KWHs. The sun angle is to the point where I am almost out of the palm tree shadows as well. Total production for all 3 systems today is going to end up around 45 KWHs.

The peak power on the Pergola also exceeded the 4,000 watt STC rating. Of course it was a short peak as the sun came out of the clouds, but that is still amazing. It sustained around 3,600 watts for a bit. That is still 90% of STC power. Those panels are flat out amazing.

I really need to start working on some new code to make the PLC take advantage of the extra power so I don't have to manually adjust it. I will make AC coupled charging totally manual so if I tell it to charge, the PLC won't take control. And I think I need to add a DC power meter to get the total current coming from the pair of Victron charge controllers. That way I can adjust the export power to 90% of what is coming in so the batteries stay charging and won't reverse to discharging over and over. I can start it exporting even earlier than 10 am. Have it ramp up to the 16 amp limit. Hold there until the sun is going down and the battery voltage begins to drop. The PLC is already getting the battery voltage and current that is being used by the XW-Pro. I will do a slow seek like I was with the charge current. If the DC solar current is higher than the DC current to the XW, increase the export current. If the XW DC current exceeds the DC solar current, then lower the export power. Check and adjust every 5 seconds, just a small change in export power and then check again. Bu tI will need to make sure I don't exceed the 900 KWH per month limit on my NEM 2.0 contract.
 
There is no doubt that th weather has been a bit "different" from last year to this year, so we can't make a simple comparison on just this one month. But this is pretty dramatic.

My Feb. 2024 electric usage was a net consumption 54 KWHs.
That was with the exact same 4,800 watt Enphase array and the 2,000 watt DC array on the garage roof. The only difference to this year is the addition of the 4,000 watt pergola.
My Feb. 2025 electric bill is a net credit of 243 KWHs. They still took $10.56 off of my credit for the NBCs and taxes, but then the credit for energy went up by $56

I did invest about $2,500 in the materials to build the pergola. So if I save $50 a month, it only takes 50 months to pay for it, just over 4 years. Even with it going into float early every day, it is producing about 350 KWHs a month. That means I basically "get" about 17 cents a KWH for the power it is producing. But that is only assuming I use that power within my plan year. If I end up with a huge amount of extra power banked at the end of the year, they are likely to buy off my energy credit at just 2 cents a KWH. Ideally, the pergola array can produce a lot more energy. But right now I don't have a place to send that energy. I did a little work on my PLC flow chart to help export more of it to the grid instead of just floating. But the real value is going to be charging an EV or PHEV where I will max out the production from those panels. I will also use a lot more of it once I start running the AC in the summer.
 
I have lived in Santa Clarita for over 20 years. In that time, we have had some snow fall and stick on the ground only 4 times. We have had some very strong "Santa Ana" winds that exceed 100 MPH. We have had rain with winds that made the rain go nearly sideways. But today was the first time I ever had real hail. Th odd part is that it was not even cold outside. IT went from very sunny but cool at 60F with my Enphase panels almost hitting clip at 9,800 watts. Then the clouds rolled in and the rain fell so hard, it was splashing off the ground. And then it got very loud as the rain drops turned into little ice balls of hail. The biggest hail I saw was less than 1/2 inch diameter, but the noise they made slamming onto the cars and my solar panels was shockingly loud. I don't see any damage, and the hail stopped and all melted away in just 20 minutes. Due to the band of clouds passing, we kept getting edge effects and reflections that pushed the energy up. I was getting 2,200 watts from the Enphase system after 3 pm. The day before, it was only doing 1,200 watts and last year was only at 1,600 watts. That more than a 40% increase in power after the hail had passed. Some of the increase over yesterday may have been the pressure wash that the storm produced. But I think most of it was the clouds bouncing light from other angles. Even as it was storming, the power was pretty strong as the sun was to the west while the clouds were above. Very odd weather for sure.

As for the DC systems, I didn't get a true maximum power as they were both well into float before the storm came through. The peak power from the garage roof shows as 1,585 watts (over 79% of STC) and the pergola hit 3,679 watts (92% of STC power). The Victrons stayed in float until after 5:15 pm with the battery full. It dipped a few times from the cloud cover and they did go back into bulk between a few times between 1:00 and 5:00 PM as I have it set to return to bulk after just a 0.02 volt battery drop. In reality, with the float voltage also set to the same as my absorb, it really does not make much difference. I see the float power go over 2,000 watts all the time, so it is just which LED it has lit at that point. But when I turn on a big load, I like to see it flip back to bulk so I know it is taking all it can from the solar panels again.

I was going to try and get a picture of the hail on the garage roof panels, but when I went back with my phone, just 10 minutes later, it had already all melted away to water.
 
We just had 2 more days of heavy clouds and a ton more rain. Wednesday was the worst. The clouds really never let up. I was at work, so my system was left all on its own. The Enphase system only produced 4.1 KWHs all day. That is only 0.85 sun hours from the 4,800 watts of panels. The two DC systems only did a little better with the 2,000 watts on the garage roof making 1.91 KWHs or 0.96 sun hours. And the new 4,000 watt pergola managed 4.13 KWHs or 1.03 sun hours. This was quite a bit less total energy than my house uses, so the battery ended the day down quite a bit.

Thursday was a bit better, but still way down from normal for this time of year. The Enphase system managed 8.8 KWHs or 1.83 sun hours. This was well over double the previous day. Again, the garage roof did a little better and produced 3.81 KWHs or 1.91 sun hours. And the pergola shines again pulling in 8.48 KWHs or 2.12 sun hours even with the heavy clouds.

The battery did recover quite a bit, but not enough to cover the loads. I had enough in reserve that it still has not hit the low cut off and we stayed on battery all night. But tonight will be close as it is dropping under 52 volts at 1 am. The JK-BMS is reporting that it is down to 54%. That agrees very well with the NMC voltage chart I have been using. When I get up in the morning, it will be interesting to see if it has to revert to grid power. I think it will make it without a problem. The forecast looks sunny tomorrow, so the system should get fully charged back up. Maybe I will finally see the full charge power from the pergola s it has some room to push energy for a while. Looking at past days, it could drop as low as 40%. Charging back 60% would need 21 KWHs from the two Victron charge controllers. That is 3.5 sun hours on both DC arrays. They have already done more that on clear days, so I think it will make it.
 
Okay....

I was a bit surprised. I just checked on my system and the DC panels alone have the battery up to absorb at noon. The pair of Victrons have already pushed over 15 KWHs and the battery is about 90% SoC. With the charge controllers in absorb, they are dropping in current, but still pushing 1,200 and 1,900 watts into the battery. Peak power hit was 1,600 watts from the garage and 3,700 watts from the pergola and the power was still climbing when they switched to absorb. I just commanded the XW to export as much as it can to max out my 16 amps back feed limit, but the Enphase system is also rocking at 3,900 watts with all 16 inverters at clip so the XW is only able to add 600 watts from the DC system. Check out the charge rate on the battery summary graph.

XW-bat_03-07-25a.JPG
The battery voltage climbed from 52 to 58 volts in just 3 hours. You can see where I set the XW to start exporting at 12:20 but it is only drawing off 9 amps while the charge controllers are still pushing 50 amps in. Right before it hit absorb, the charge current from the DC system hit nearly 100 amps. The pergola 250/70 was at 65 amps and the 15/35 for the garage roof was at 31 amps. I have no doubt I will see all 3 systems hitting clip in April and May.
 
We had another couple days of rainy weather. The Enphase system made just 9.1 KWHs yesterday, and 8.3 KWHs today. This is well down from the normal 23 KWHs it made a few days before. But the two DC systems did their best to make up for it. They didn't go into absorb or float so they pulled in all they could. Today the Enphase 8.3 KWHs works out to 1.73 sun hours. The garage roof managed 3.54 KWHs or 1.77 sun hours. Just a little bit better. Then there is the Pergola. It pulled in 7.86 KWHs or 1.965 sun hours for the win yet again.

How much of this extra production is just new panels vs them being "bifacial" and getting a bit more scattered light under them?

I am certainly not complaining, it is great to see them always at the top of production. Here is the battery summary graph from yesterday.XW-bat_03-11-25.JPG
From 9 am to 6 pm, the Enphase system normally makes more than the house needs, but with the rain and clouds, it fell short. The XW-Pro was pulling some battery power still trying to zero the grid. The house load exceeded production and resulting in some discharging around 10 am and 2 pm, but the energy from both DC systems still managed to "almost" get the battery full again. With the voltage offset, the XW would show the battery topping out at 58 volts. It ONLY hit 57.77 volt when the sun went down. And this was a day with well under half normal production. Today was even lower. So we fell even a little shorter. Here is Today's graph up to 7:50 pm
XW-bat_03-12-25a.JPG
We are certainly a little own today as it only got the battery back up to 56.7 volts. It will easily make it to sun up again tomorrow, but a third or 4th day of this type of weather would have me resorting to some grid power. We may be testing that theory. They are predicting more rain up to 10 am tomorrow, and then "partly cloudy" or "cloudy" all the way to 7 pm when the sun is down again. They are not listing a "sunny" day until Saturday. So it may be another 3 days of this. At least all of the solar panels are nice and clean now.
 
tha's a big storm... are you taking today off?
Nope, I had to work this morning. Started at 5 am.
The drive in to Hollywood was a bit hairy. On the up hill section of the pass, I was not able to keep going 60 MPH as the traction control kept cutting in as the wheels would spin just trying to hold speed up the hill. There was standing water up to 2 inches deep flowing down the hill My ground speed may have been 60 MPH but the water speeds was more like 90 going upstream against the current. Drove past 3 crashes on my 30 mile drive in. Going 65 was just too much, so many cars were hydroplaning.
 