BentleyJ
Solar Wizard
Before UL 1741 added the Supplemental Appendix (SA) provisions. Grid-Tie or Distributed Generation (DG) inverters would have to shut down at 60.5 Hz. The new rules require several ride-through (RT) ranges for both voltage and frequency. Frequency range was increased up to 62 Hz BUT between 60.5 and 62.0 Hz its only 299 seconds of RT before shut down. Based on the above, you will probably need to either get the Sol-Ark frequency down below 60.5 Hz or set the micoinverters to an Off-Grid profile if they are to stay on and work reliably. The attached is PDF has some good technical info about the particulars of UL 1741 SA.The micros went offline but the good news was the frequency was stable at 61 Hz. I am encouraged that I am going to get this working.