I just did a post about how my solar system performed over the last 159 days and I calculated my system efficiency which came out to a fairly abysmal 81.3%.
So how did I calculate the efficiency?
I measured my actual load using Emporia Vue inside my main panel. I have compared its readings to the utility meter before I had solar and the measurement was within 0.5-1.0% of the metered reading therefore I consider this measurement fairly accurate and precise.
My Total load side consumption was 10,700 kWh over the 159 day period.
I also got readings from my meter and I consumed 9,274 kWh of grid power during this period and exported 4,984 kWh of solar power to the grid over this same time period.
Therefore my net solar production is what I exported plus what I covered between my load and what I consumed from the grid. This comes out to 6,410 kWh of total Solar production.
However my Sol-Ark data shows that I produced 8,676 kWh and my Tigo optimizers registered 8,871 kWh. This means there is a 2.2% loss over the wires from the panels to the inverter.
If I look at strictly solar then 8,871 kWh on the roof ended up being 6,410 kWh at the load side which is 72% efficiency but I'm not sure that really covers the whole picture.
I'd say there is a 2,461 kWh loss in generating 10,700 kWh of energy for my house which comes out to to be 81.3% or 18.7% loss.
This is quite a surprising number as I would not have guessed that I'm losing this much energy within the system. Granted the battery draws 100W constant and the Sol-Ark has an idle power of 90W I'm still surprised that on average there is 644W of power just getting turned into heat somewhere along the way constantly.
Has anyone else done a similar calculation?
So how did I calculate the efficiency?
I measured my actual load using Emporia Vue inside my main panel. I have compared its readings to the utility meter before I had solar and the measurement was within 0.5-1.0% of the metered reading therefore I consider this measurement fairly accurate and precise.
My Total load side consumption was 10,700 kWh over the 159 day period.
I also got readings from my meter and I consumed 9,274 kWh of grid power during this period and exported 4,984 kWh of solar power to the grid over this same time period.
Therefore my net solar production is what I exported plus what I covered between my load and what I consumed from the grid. This comes out to 6,410 kWh of total Solar production.
However my Sol-Ark data shows that I produced 8,676 kWh and my Tigo optimizers registered 8,871 kWh. This means there is a 2.2% loss over the wires from the panels to the inverter.
If I look at strictly solar then 8,871 kWh on the roof ended up being 6,410 kWh at the load side which is 72% efficiency but I'm not sure that really covers the whole picture.
I'd say there is a 2,461 kWh loss in generating 10,700 kWh of energy for my house which comes out to to be 81.3% or 18.7% loss.
This is quite a surprising number as I would not have guessed that I'm losing this much energy within the system. Granted the battery draws 100W constant and the Sol-Ark has an idle power of 90W I'm still surprised that on average there is 644W of power just getting turned into heat somewhere along the way constantly.
Has anyone else done a similar calculation?