The SOC figures vary greatly occasionally requiring my intervention to keep from badly overcharging my battery.
The SI6048 supposedly receives data gleaned from my WhizBang Jr via one of my 2-networked Classic 250 charge controllers via my MODBUS/Canbus adaptor.
The WhizBang Jr (and subsequently both of my MidNite Classic 250's) gives a much higher SOC reading than what the SI6048 thinks.
I've double-checked my wiring inside the MidNite SMA-OG E-panel to verify that the output from the solar goes to the bus on the Inverter side of the 500A/50mv shunt (and attached WBJR). Here is where I've narrowed what I think is causing the problem down to:
The WhizBang Jr, and the SI6048's current readings (supposedly from the WBJR but looks like just from the shunt) are spot on (after calibrating the shunt) about power in or out of the batteries with no solar. With solar the WBJR shows the additional current in from the controllers, but the SI6048 still reads the value minus the current from the controllers. This makes the SOC calculations WAY OFF from each other... Often the WBJR will show I'm at 80% SOC with only like -140 net AH, but the SI6048 thinks we're at 40% and wants to run the generator.
What have I missed?
The SI6048 supposedly receives data gleaned from my WhizBang Jr via one of my 2-networked Classic 250 charge controllers via my MODBUS/Canbus adaptor.
The WhizBang Jr (and subsequently both of my MidNite Classic 250's) gives a much higher SOC reading than what the SI6048 thinks.
I've double-checked my wiring inside the MidNite SMA-OG E-panel to verify that the output from the solar goes to the bus on the Inverter side of the 500A/50mv shunt (and attached WBJR). Here is where I've narrowed what I think is causing the problem down to:
The WhizBang Jr, and the SI6048's current readings (supposedly from the WBJR but looks like just from the shunt) are spot on (after calibrating the shunt) about power in or out of the batteries with no solar. With solar the WBJR shows the additional current in from the controllers, but the SI6048 still reads the value minus the current from the controllers. This makes the SOC calculations WAY OFF from each other... Often the WBJR will show I'm at 80% SOC with only like -140 net AH, but the SI6048 thinks we're at 40% and wants to run the generator.
What have I missed?