You and I have discussed this before.Auto transformers are a no go in my book.
How do you make sure an oversized AC system is not allowed to output when grid down? OP doesn’t want to buy the battery size necessary to absorb the size of his AC.I do my AC coupling on the load side
The Radian will frequency shift lowering the output of the panels if its not needed
Is .5C essential? I think it depends on the AC coupling algorithm300 ah at 0.5c = 150 amp cell charge rate limit
What algorithm are you specifically referring to? When AC coupling with the Load Side of the battery inverter, excess PV production gets backfed into the inverter and rectified to DC to charge the batteries. Batteries being the dump load. The battery inverter cannot regulate the charging function when its going in the reverse direction.If the algorithm can be told to average .5C but allow higher bursts while waiting for AC coupling to respond, I think higher is fine, up to the battery spec.
If the algorithm CANNOT be told to do that then one should stick to .5C. Likewise if there is no positive confirmation that the algorithm is sophisticated enough to do this.
What algorithm are you specifically referring to? When AC coupling with the Load Side of the battery inverter, excess PV production gets backfed into the inverter and rectified to DC to charge the batteries. Batteries being the dump load. The battery inverter cannot regulate the charging function when its going in the reverse direction.
That said, some newer UL1741 grid-tie inverters do have the ability to step down their output in say 20% increments based on frequency steps. The XW+ ramps up frequency in 0.1Hz steps until 60.5Hz is reached. My older micoinverters do no respond to these frequency steps, they shut down at 60.5Hz otherwise its 100% output. This scenario is still different then the inverter internally regulating charge current and voltage since the frequency shift is attempting to control the input power not directly regulate the DC output to the batteries.
Are they high frequency? How well do the handle inductive loads? $$$ these are close to sol ark price correct?Outback Radian 8048
It will AC couple and battery backup
At least not this year. Really want to get a hybrid unit up and working before investing in more batteries.How do you make sure an oversized AC system is not allowed to output when grid down? OP doesn’t want to buy the battery size necessary to absorb the size of his AC.
How well do the handle inductive loads? $$$ these are close to sol ark price correct?
I just got done with a re-inspection after ESS installation as well as to qualify for a state ESS battery rebate program. Approved for both. Trophy ESS did not require UL batteries. Everything else was UL. They focused more on the Sol Ark than anything else. Big ESS rebate check is in the mail.I guess you are asking about inductive loads b/c you plan to eventually be able to operate with grid down and want to buy equipment compatible with it, even if it's not for this year.
EDIT: wanted to make sure bc for your initial grid up / time shift only requirement you can easily use an anemic storage inverter (mentioned upthread by 1-2 people), so it’s easy for readers to get confused.
I believe Outback Radian needs a separate MPPT so they ought to be priced lower to be able to compete vs the SolArk with its integrated MPPTs.
EnerSys owns Outback so it's probable that permitted installations will be pricy for a while. Due to my expectation that batteries would cost more due to the corporate structure. Since EnerSys is a battery company, so why would Outback be motivated to get a 9540 listing with non-EnerSys batteries, or implement communications / other features necessary if some 3rd party battery company wants to pay for a paired 9540 listing with Outback.
By comparison SolArk makes its money on the $$$ hybrid inverter and has a pretty large set of listed 9540 pairings with plenty of battery companies.
If you don't need permits or communications, you can hook up any battery you want, modulo theoretical implementation details like AC coupling being software locked to work worse (for no good reason) if there is no communications.
Nice. Does your POCO care about how export control and power control is done? I was reading up on the rules under some NEM jurisdictions — they’re very anal, and in a quite complicated way, since they are worried about using batteries to cheat on NEM credits.I just got done with a re-inspection after ESS installation as well as to qualify for a state ESS battery rebate program. Approved for both. Trophy ESS did not require UL batteries. Everything else was UL. They focused more on the Sol Ark than anything else. Big ESS rebate check is in the mail
Yes they were crazy about it. I had to go into my Grid Settings and alter ramp rates the voltages the reconnect time and the Q values. I’m just glad I bought the Sol Ark because all the variables they required were user adjustable and present. Im not sure they would have allowed it on the system without those setting changes. On the other hand I know one of their company engineers didn’t like it but eventually approved after I was able to intelligently respond to his questions.Nice. Does your POCO care about how export control and power control is done? I was reading up on the rules under some NEM jurisdictions — they’re very anal, and in a quite complicated way, since they are worried about using batteries to cheat on NEM credits.
Turns out there are actually standards you can get validated in the NRTL that proves an inverter will not “cheat.” XW Pro has one of those listed on its certificate and I’m sure SolArk got the right ones to maximize their addressable market.
Wow, OK. Do they do this for all projects (seems ridiculously unscalable), or is this specific to using SolArk / ESS that they're not used to?Yes they were crazy about it. I had to go into my Grid Settings and alter ramp rates the voltages the reconnect time and the Q values. I’m just glad I bought the Sol Ark because all the variables they required were user adjustable and present. Im not sure they would have allowed it on the system without those setting changes. On the other hand I know one of their company engineers didn’t like it but eventually approved after I was able to intelligently respond to his questions.
Apologies for making this confusing, probably cause it's how I feel right now! Yes I suppose I am treating this like an off grid capable inverter as well. yes having a bit more capability down the road seems like a better idea to me. I would prefer to go off grid, but I'm poor. Does it make much sense to choose an anemic inverter that can be paralleled, then buy a second one in a year or so? So with the lesser wattage inverters they would supply all they can, and if not adequate for the load than the grid would supply the rest that is required correct?I guess you are asking about inductive loads b/c you plan to eventually be able to operate with grid down and want to buy equipment compatible with it, even if it's not for this year.
EDIT: wanted to make sure bc for your initial grid up / time shift only requirement you can easily use an anemic storage inverter (mentioned upthread by 1-2 people), so it’s easy for readers to get confused.
I believe Outback Radian needs a separate MPPT so they ought to be priced lower to be able to compete vs the SolArk with its integrated MPPTs.
EnerSys owns Outback so it's probable that permitted installations will be pricy for a while. Due to my expectation that batteries would cost more due to the corporate structure. Since EnerSys is a battery company, so why would Outback be motivated to get a 9540 listing with non-EnerSys batteries, or implement communications / other features necessary if some 3rd party battery company wants to pay for a paired 9540 listing with Outback.
By comparison SolArk makes its money on the $$$ hybrid inverter and has a pretty large set of listed 9540 pairings with plenty of battery companies.
If you don't need permits or communications, you can hook up any battery you want, modulo theoretical implementation details like AC coupling being software locked to work worse (for no good reason) if there is no communications.