... but if I remember correctly, this was not sold from Watts and the unit was another brand (but basically same unit). Or am I confused with another member?So exchanging it with one from watt247 wasn't an option? That's disappointing to hear.
In a hurry to get the house's hvac wired up on loads1 and ran into a question.
The nhx does not bond ground/neutral for any output; generator, grid, load1, load2? Since I will not be running parallel with grid, the subpanel fed by load1 will now be considered the main panel, and if the nhx does not bond n/pe, then that panel will now have to be bonded.
Correct. That should still supply your bond.Hmm ... since the grid main panel is still hooked to the nhx, I guess the ground/neutral bond could remain in the grid main panel even though it really won't be the the main panel anymore. The nhx should pass the neutral and ground along without switching the bonding, but I'd rather completely disconnect everything from the grid main panel. Maybe that would make the poco happy.
Never had a solar connection to the grid. Everything was in preparation to connect to grid, but they changed requirements, i.e.; have to pay for upgraded transformer+labor and keep liability insurance. Other requirements more or less similar as before, which were not solar friendly to start with. I'd never break even with the new requirements.Less solar friendly? Are they sending the solar police after you for any amount of backfeed?
Yes, without the grid the NHX does not have a ground to neutral bond. If you have a load that needs a ground to neutral bond then you will need to make the bond at the panel fed by load 1.In a hurry to get the house's hvac wired up on loads1 and ran into a question.
The nhx does not bond ground/neutral for any output; generator, grid, load1, load2? Since I will not be running parallel with grid, the subpanel fed by load1 will now be considered the main panel, and if the nhx does not bond n/pe, then that panel will now have to be bonded.
Well…this is a diy forumSo exchanging it with one from watt247 wasn't an option? That's disappointing to hear.
What version of firmware are you running?Got up this afternoon and was checking SolarAssistant ... nothing. SA, or the Pi it's running on crashes once in a while so I went out to the shed to reset it and everything was dark. ???
Both inverters were just sitting there, on, with no solar being produced, no power output, no breakers tripped, battery 53.xv, and no alarms. No indication of why the nhx were not doing their thing.
Reset rsds and everything came back to life.
No issues for a long time. I was getting used to dependable solar and this happens.
Anyone?
View attachment 294166
Wish they were a changelog for the firmware.It's been running without issue for months. Maybe it's the firmware, maybe not but now you have a new piece of information.
Grid is not connected.Did grid power go down?
I had a hiccup with this unit. It was months ago. I think the power from the grid went out for a short amount of time, like less than a minute. Instead of kicking in to power the critical subpanel the inverter either shutdown or power cycled.
It hasn't happened again but we also don't have very many grid failures. Maybe it's similar to what you've seen here.