No, what you are saying makes not sense. My 18kpv is on 1E1E and it just works. What makes you think it is in "gridboss mode"?View attachment 274205
When the 18Kpv is wired into the gridboss and gridboss mode activated, loads will not feed from the 18Kpv grid to the loads. Hope that made sense..
Thanks for the reply.No, what you are saying makes not sense. My 18kpv is on 1E1E and it just works. What makes you think it is in "gridboss mode"?
You need to describe what you have going on in more detail (and how you have it wired) and quit guessing what is wrong. And document all of your settings. Since this is a new install, there is a very good chance that you have a wiring issue of some sort causing the behavior.
This has crossed my mind, but this is my 3rd 18Kpv and the wiring has gone through a thorough investigation.there is a very good chance that you have a wiring issue of some sort causing the behavior.
This is what grid boss made for to transfer the load through it if you want to make use of solar power you need to enable export. This inverter doesn't need grid boss since it has 200a relay it can handle the load easily.View attachment 274205
When the 18Kpv is wired into the gridboss and gridboss mode activated, loads will not feed from the 18Kpv grid to the loads. Hope that made sense..
Quattrohead am I still not explaining it well? I will try to go into more detail if it still does not make sense. ThanksDo not use the grid boss mode and keep your loads on the load terminals, or am I not getting what you're saying?
Did you restart the inverter after the update? Did you update the lcd?Quattrohead am I still not explaining it well? I will try to go into more detail if it still does not make sense. Thanks
Yeah I am sorry I am not getting what you are saying.Quattrohead am I still not explaining it well? I will try to go into more detail if it still does not make sense. Thanks
SS flashed the firmware twice. And we power cycled the unit. They did not update the lcd because my 18Kpv came with all the newest firmware already installed.Did you restart the inverter after the update? Did you update the lcd?
No grid bossDo you have a grid boss or not ?
YesDo you have grid connected to the grid port and loads connected to the load port?
replacement for the fan issue.Is this inverter a replacement or an addition ?
The 18Kpv will power the loads in Off Grid Mode, but as soon as on grid is used all the Loads go dead.What is the inverter doing or not doing?
I have ran mine successfully both in off-grid and on-grid mode. You need to describe what you are seeing and how you have it wired.Thanks for the reply.
This has crossed my mind, but this is my 3rd 18Kpv and the wiring has gone through a thorough investigation.
So are you off grid or are you grid tied also?thanks
Any faults? Others that have had off grid work but on-grid not work had multiple inverters with the legs reversed/not-consistent, but those got errors/codes. and their loads were tied together with one inverter having InverterL1= Grid L1, and InverterL2=Grid L2, but the other one was InverterL1=GridL2, and InverterL2=GridL1. And on a unit replace, unless labeled it would be trivial to reverse either the Grid or the Load and get this.No grid boss
Yes
replacement for the fan issue.
The 18Kpv will power the loads in Off Grid Mode, but as soon as on grid is used all the Loads go dead.
Your first screenshot is broken for me. What is your "Max. AC Input Power(kW)"?
9kwYour first screenshot is broken for me. What is your "Max. AC Input Power(kW)"?