Hi All,
I would appreciate some experienced opinions as to whether I have some faulty cells in this Apexium 280Ah, LiFePo4 system with JK Inverter BMS.
Having received the self-assembly kit and unpacked the five boxes, I top-balanced the cells to 3.65 VDC and left them parallel connected for 24 hours, all voltages were within a few hundredths volt and internal resistances were within a few thousandths Ohm. Assembled the battery, torqued and checked, powered on, connecting to a Victron Multiplus II 5000/70 through Lynx PowerIn and monitored through Cerbo GX with 5.4kv solar array, Samil & Solax inverters. Everything was fine and I configured the various settings with no issues (having an existing setup with just the Apexium being new).
However, the first cycle has identified some potential cell problems. The attached image (and XL file) shows a screenshot of the JK PC monitoring software with 4 hours captured (I did not include the earlier Discharge/Charge cycles as they show nothing unusual, following the initial top-balance). Cells 2, 10 and 11 are running-ahead of the other cells and causing a premature "Battery Full" message. The Victron ESS is set to 56VDC max and the JK BMS is set to 3.55 (Bat 100%), 3.6 OVP, 3.549 OVPR.
The screenshot shows one or more of those potentially faulty cells causing the charge shut-down, the cell recovers and quickly breaches the OVP again the cycle then repeating over the next 4 hours until the Sun goes down and/or discharge kicks in. The attached XL file shows the full ~4 hours, the screenshot is just an example over the first 8 minutes or so. All the battery cells, including the three identified, balance-up when left inactive or discharging for a relatively short while (minutes, not hours).
I have spoken to the supplier and they have suggested I take the three cells and "externally" charge/discharge them a few times, then match voltages (approximately) and re-install. I don't think that will help at all as they are effectively doing that within the system but will do it anyway.
I would appreciate opinions as to whether this data indicates faulty cells and whether the supplier suggestion is worthwhile.
Ooops, won't allow a spreadsheet... If requested I'll post a link.
Russ
I would appreciate some experienced opinions as to whether I have some faulty cells in this Apexium 280Ah, LiFePo4 system with JK Inverter BMS.
Having received the self-assembly kit and unpacked the five boxes, I top-balanced the cells to 3.65 VDC and left them parallel connected for 24 hours, all voltages were within a few hundredths volt and internal resistances were within a few thousandths Ohm. Assembled the battery, torqued and checked, powered on, connecting to a Victron Multiplus II 5000/70 through Lynx PowerIn and monitored through Cerbo GX with 5.4kv solar array, Samil & Solax inverters. Everything was fine and I configured the various settings with no issues (having an existing setup with just the Apexium being new).
However, the first cycle has identified some potential cell problems. The attached image (and XL file) shows a screenshot of the JK PC monitoring software with 4 hours captured (I did not include the earlier Discharge/Charge cycles as they show nothing unusual, following the initial top-balance). Cells 2, 10 and 11 are running-ahead of the other cells and causing a premature "Battery Full" message. The Victron ESS is set to 56VDC max and the JK BMS is set to 3.55 (Bat 100%), 3.6 OVP, 3.549 OVPR.
The screenshot shows one or more of those potentially faulty cells causing the charge shut-down, the cell recovers and quickly breaches the OVP again the cycle then repeating over the next 4 hours until the Sun goes down and/or discharge kicks in. The attached XL file shows the full ~4 hours, the screenshot is just an example over the first 8 minutes or so. All the battery cells, including the three identified, balance-up when left inactive or discharging for a relatively short while (minutes, not hours).
I have spoken to the supplier and they have suggested I take the three cells and "externally" charge/discharge them a few times, then match voltages (approximately) and re-install. I don't think that will help at all as they are effectively doing that within the system but will do it anyway.
I would appreciate opinions as to whether this data indicates faulty cells and whether the supplier suggestion is worthwhile.
Ooops, won't allow a spreadsheet... If requested I'll post a link.
Russ