New Combiner and I new to Lengthen/Splice my PV wire

MrM1

I'm Here, But I'm Not All There
Joined
Mar 1, 2021
Messages
2,020
Location
N. Central FL
Decided to go with these inside appropriate box types for wire transitions (solar wire to MC) and splices. Seemed simple enough, reusable and designed for the purpose.

Screenshot_2023-05-24-07-59-46-409.jpg
 

Crowz

Solar Addict
Joined
Dec 24, 2022
Messages
436
Decided to go with these inside appropriate box types for wire transitions (solar wire to MC) and splices. Seemed simple enough, reusable and designed for the purpose.

View attachment 150363
Thats what I just installed monday.

I bought that one you linked first and they sent a box of 50 yellow connectors with no rail or ends. I'm sending it back.

I ordered again and noticed this one :


71O6RMggxPL._SL1120_.jpg


It was $1 cheaper and had a ton more stuff to it. I likes it :)
 

MrM1

I'm Here, But I'm Not All There
Joined
Mar 1, 2021
Messages
2,020
Location
N. Central FL
I could not find kits for the DK6N only the DK4N. The DK6N does 8 awg, the DK4N does not. I needed up to 8 awg
 

Crowz

Solar Addict
Joined
Dec 24, 2022
Messages
436
I could not find kits for the DK6N only the DK4N. The DK6N does 8 awg, the DK4N does not. I needed up to 8 awg
I got lucky on this since I was combining the small wires from the power supply on the orange pi 3 lts thats running solar assistant and the power for the surveillance cameras and such.

I may get a larger one for the larger stuff but I crimped that stuff already and did the traditional bus bars for those.
 

Shimmy

Photon Sorcerer
Joined
Feb 22, 2022
Messages
1,241
Decided to go with these inside appropriate box types for wire transitions (solar wire to MC) and splices. Seemed simple enough, reusable and designed for the purpose.
Right approach, as long as you check on them periodically. Personally I have seen miserable safety results in the past with crimp or set-screw butt splices. The only thing we ever allowed was compression butt splices on 4/0 or larger; we replaced small wires.

Mechanical splices have a way of being forgotten and working themselves loose. This is especially true for connections that cycle from zero to a continuous >60% load daily.
 

MrM1

I'm Here, But I'm Not All There
Joined
Mar 1, 2021
Messages
2,020
Location
N. Central FL
Right approach, as long as you check on them periodically. Personally I have seen miserable safety results in the past with crimp or set-screw butt splices. The only thing we ever allowed was compression butt splices on 4/0 or larger; we replaced small wires.

Mechanical splices have a way of being forgotten and working themselves loose. This is especially true for connections that cycle from zero to a continuous >60% load daily.
I'm assuming "mechanical" also means the connection point at the breaker ?
 

Quattrohead

Photon Sorcerer
Joined
Oct 13, 2021
Messages
1,475
Location
Florida
Box and wire nuts are perfectly fine.
When I first came to the USA, wirenuts frightened me to death and made me laugh all at the same time but over the years I have come to appreciate them immensely. Done properly they are one of the safer connection methods available.
 

MrM1

I'm Here, But I'm Not All There
Joined
Mar 1, 2021
Messages
2,020
Location
N. Central FL
Box and wire nuts are perfectly fine.
When I first came to the USA, wirenuts frightened me to death and made me laugh all at the same time but over the years I have come to appreciate them immensely. Done properly they are one of the safer connection methods available.
Even for high voltage DC? (or does it AC / DC even matter)
 

Shimmy

Photon Sorcerer
Joined
Feb 22, 2022
Messages
1,241
I'm assuming "mechanical" also means the connection point at the breaker ?
The breaker connection is generally easier to inspect though. Few places inspect splices unless they have had a problem with them.
 

Shimmy

Photon Sorcerer
Joined
Feb 22, 2022
Messages
1,241
Even for high voltage DC? (or does it AC / DC even matter)
If they are made up properly it won't matter. But, if they are loose or have eccentric strain then internal arcing seems possible and higher risk with DC IMO. I don't think voltage matters much below 600V.
 