I just comissioned a new 6000xp and am seeing import (grid) power during charging of 1/4 to 1/3 what the settings specify.
Example: I have AC Charge Current set at 4A (Dc charge is 100A) but my Import Power is only 232W.
My grid side is 240v, confirmed with a multimeter. The inverter panel shows 120V on L1 and 120V on L2 when I cycle through the display.
Does anyone know of a setting I may have missed that would limit this?
Tried:
- Numerous SOC settings for min and max.
- Numerous AC and DC charge currents. Even with AC at 25A, import current still shows only 1800W. 1800W/240V=7.5A, far lower than expected.
--- The 1/3 to 1/4 I mentioned holds true at any amperage, its almost linear as I raise and lower the charge limits
- Tried Battery Eco both ways, no change
- Tried AC Input Range set to APL and UPS, no change
- Tried raising max generator input power as high as 25 (no generator anyway, just testing), no change
- System Type parallel and no parallel (system is actually single 6000XP and single 14.3Kw EG4 wall-mount)
System Info:
- Single 6000XP and single 14.3Kw EG4 wall-mount
- EPS Voltage is 240V, frequency 60Hz (have not change these, they are correct for my location)
Any ideas on why import power is so much lower than the setting?
Example: I have AC Charge Current set at 4A (Dc charge is 100A) but my Import Power is only 232W.
My grid side is 240v, confirmed with a multimeter. The inverter panel shows 120V on L1 and 120V on L2 when I cycle through the display.
Does anyone know of a setting I may have missed that would limit this?
Tried:
- Numerous SOC settings for min and max.
- Numerous AC and DC charge currents. Even with AC at 25A, import current still shows only 1800W. 1800W/240V=7.5A, far lower than expected.
--- The 1/3 to 1/4 I mentioned holds true at any amperage, its almost linear as I raise and lower the charge limits
- Tried Battery Eco both ways, no change
- Tried AC Input Range set to APL and UPS, no change
- Tried raising max generator input power as high as 25 (no generator anyway, just testing), no change
- System Type parallel and no parallel (system is actually single 6000XP and single 14.3Kw EG4 wall-mount)
System Info:
- Single 6000XP and single 14.3Kw EG4 wall-mount
- EPS Voltage is 240V, frequency 60Hz (have not change these, they are correct for my location)
Any ideas on why import power is so much lower than the setting?