New Member
I have 2 XW Pro 6848s and 2 100/600 SCCs ready to hang on the wall. My dilemma is, where to put the system. I have a workshop that has a 200amp sub panel in place but I can also put the system in my basement. 28 400W Hyperion panels(2 strings of 14) will be 100ft from the shop and 350ft from the house. The house basement is 8" thick concrete walls. My dilemma is this...do I put the equipment/48kWh diy battery bank in the shop closer to the pv panels and run heavy wire to the house through the sub panel? Not sure if I need to run a different line or how to accomplish that. Or do I put the system in the house next to main panel and run lighter gauge wire 350ft? If I entered the numbers correctly it would be less than 2% drop using 8awg(1.19%) or 10 awg(1.89%). I am also concerned about the battery bank in the house. I have been reading all I can and have seen many that say LiFePO4 is perfectly safe in the house provided it is built correctly, and have read just as many saying to never put the battery bank in the house. What would you recommend? I may be sweating the details but I don't want to endanger my family or mess up the install.