BMS is last line of defense against cell over/under charge.
If you get 12V batteries, make sure they are compatible with connecting in series for 48V; some can't take the voltage when they open.
You can get 48V pre-assembled batteries. Or individual LiFePO4 cells and assembl 16s + BMS for 48V. Or 2p16s with one BMS, or 16s2p with 2 BMS. Some BMS control an external relay for higher current.
Charge controller should charge to a voltage low enough that BMS doesn't disconnect for cell over-voltage, but high enough to allow passive balancing. Some BMS use a data bus to communicate with some inverter/charger to hold voltage in a range for balancing.
Lithium may be best utilized deeply cycling every day, so you get your use out of its cycle life before it dies of old age.
Lithium can accept about 0.5C charge rate near ambient 25 degree temperatures, but reduced to about 0.1C or 0.05C as temperature approaches freezing. For off-grid, I think 0.15C is enough to recharge during the day in most conditions.
If a battery is sized for 3 days without sun, it would only use about 15% DoD most nights. With that sort of usage, premium FLA like forklift batteries or Rolls Surette are reported to last 15 to 20 years. They do need watering and equalizing periodically. They tolerate charging below freezing.
I use SMA Sunny Island and Sunny Boy. That is one of the most expensive brands, but liquidation and old stock could be a deal for off-grid (doesn't need latest features required by code for on-grid).
Split-phase 120/240V can be up to 24kW battery inverter and 48kW PV inverters. PV panels 50% greater (e.g. 72kW) could be connected without clipping production if array has two different orientations (SE, SW).
Half that size system might meet your needs.
3-Phase 120/208Y 18kW battery inverter 36 kW PV inverters can also be done.
Some other brands like Victron, Midnight, Schneider could build similar size systems, usually DC coupled but some support AC coupled PV.
There are also SolArk, MPP, others.
The better brand low-frequency inverters will do better starting large motors. Soft-Start kits may help for smaller inverters.
If you keep utility connection, that can be a cheap reliable "backup generator", let you get by with smaller system, smaller battery especially for time without sun.
If you get 12V batteries, make sure they are compatible with connecting in series for 48V; some can't take the voltage when they open.
You can get 48V pre-assembled batteries. Or individual LiFePO4 cells and assembl 16s + BMS for 48V. Or 2p16s with one BMS, or 16s2p with 2 BMS. Some BMS control an external relay for higher current.
Charge controller should charge to a voltage low enough that BMS doesn't disconnect for cell over-voltage, but high enough to allow passive balancing. Some BMS use a data bus to communicate with some inverter/charger to hold voltage in a range for balancing.
Lithium may be best utilized deeply cycling every day, so you get your use out of its cycle life before it dies of old age.
Lithium can accept about 0.5C charge rate near ambient 25 degree temperatures, but reduced to about 0.1C or 0.05C as temperature approaches freezing. For off-grid, I think 0.15C is enough to recharge during the day in most conditions.
If a battery is sized for 3 days without sun, it would only use about 15% DoD most nights. With that sort of usage, premium FLA like forklift batteries or Rolls Surette are reported to last 15 to 20 years. They do need watering and equalizing periodically. They tolerate charging below freezing.
I use SMA Sunny Island and Sunny Boy. That is one of the most expensive brands, but liquidation and old stock could be a deal for off-grid (doesn't need latest features required by code for on-grid).
Split-phase 120/240V can be up to 24kW battery inverter and 48kW PV inverters. PV panels 50% greater (e.g. 72kW) could be connected without clipping production if array has two different orientations (SE, SW).
Half that size system might meet your needs.
3-Phase 120/208Y 18kW battery inverter 36 kW PV inverters can also be done.
Some other brands like Victron, Midnight, Schneider could build similar size systems, usually DC coupled but some support AC coupled PV.
There are also SolArk, MPP, others.
The better brand low-frequency inverters will do better starting large motors. Soft-Start kits may help for smaller inverters.
If you keep utility connection, that can be a cheap reliable "backup generator", let you get by with smaller system, smaller battery especially for time without sun.