I have 7 310w panels and looking to go with 2
Best advice so far , and yes off grid application was thinking to go 24v, I can also get another panel and increase to 8 or go with a diff/more battery set up but just seemed those batts I posted where lots of ah for the price seemed worth it. I just don’t want to get to big of a inverter ( any recommends?)and create a waste draw and mppt ratings kinda confuse me on the convertersOne more idea:
Instead of one huge SCC and an unused panel, you can setup 2 smaller systems to spread the solar harvesting across the day. If you have 3 panels (all in series) east-ish with a Victron 150/50 and 4 panels (2 series, 2 parallel) facing west-isn with a matching Victron 150/50 you would use all 7 panels and start charging earlier and finish charging later.
Obviously you could have 4 panels east and 3 panels west... not sure how i'd determine which to do. Maybe 4 east if i expected to deplete power at night and wanted/needed power earlier in the day. Conversely, having 4 west you could maximize late afternoon charging to ensure power at night.
Make sense?
You will need 8 LiFePO4 cells in series to make 24v. (3.2v x 8 = 25.6v aka 24v battery)yes off grid application 24v
The SCC does not have a draw and its not the same thing as an inverter. An inverter, converts your battery power (25.6v DC) to household current (120v AC) ... there is a standby draw on these inverters but they can always be turned off when not needed. Thats a different battery "use" discussion (we're talking charging here!).I just don’t want to get to big of a inverter and create a waste draw and mppt ratings kinda confuse me on the converters
If you got an 8th panel, you could make 2 smaller and identical systems (fewer spares!).Thank you, ok so I’ll be looking at 100/80 mppt unless I add a panel or go with the absolute genius idea of a split system correct?
So this is a completely different exercise. Do you know how much power you use in a day?Need an inverter recommendation I know I don’t have an exact number on my loads but was thinking 2000w or if I add a panel I go 3000w ballpark
Lets see what your max AC loads will be to determine how many watts your need to pull at any time.recommend still doing 24v batt bank? Can both systems go from their scc to change the same bank? Or do they need their own batt banks
Would you by chance have a diagram of this set up?If you got an 8th panel, you could make 2 smaller and identical systems (fewer spares!).
With 4 panels east-ish and 4 west-ish: with 2 in series and those in parallel (2S2P), your panel Voc 40.3 x 2 is low enough for you to get 2 very reasonably priced and top notch Victron 100/50 (takes up to 100v input and charges at a max of 50a).
Victron 100/50:
The numbers for the panels and this SCC match up nearly perfectly. I'd recommend this to my mom.
So you would have 2 arrays of 4 panels each:
4 x 310w = 1240w
1240w / 25.6v = 48.4a (theoretical max in a 100% efficient world)
This would provide some redundancy so if one piece failed you'd still have half running. And keeping a spare for 2 identical systems is feasible.
Here is 1 of the 2S2P arrays. Note there are 2 panels in series, twice. The top left panel's "+" wire is connected to the bottom left's "-" wire to make the series connection. Same with the top right and bottom right panels.Would you by chance have a diagram of this set up?
With this config 10awg should be ok for all my panel wiring correct?Here is 1 of the 2S2P arrays. Note there are 2 panels in series, twice. The top left panel's "+" wire is connected to the bottom left's "-" wire to make the series connection. Same with the top right and bottom right panels.
Those 2 strings are combined in parallel by connecting the "+" wires from each string together and also connecting the "-" wires together to make the parallel connection. Thus 2 in series, then 2 in parallel (2S2P).
The series connections add the volts for the panels: 40.3v + 40.3v = 80.6v, the amps remain the same.
The parallel connections add the amps for the series strings: 9.3a + 9.3a = 18a.
Total array: 1240w 80.6v 18a
Create 2 arrays like this with one pointing east-ish and one pointing west-ish.
Not shown are each SCC connecting to the battery bank.
View attachment 32806
Yes, up to 60ft distance, one way.With this config 10awg should be ok for all my panel wiring correct?
I am unfamiliar with this unit but there are many threads about it (use search tool).The growatt 3000TL 24P