Bonding externally is always best practice. If you look at almost all major brands like SolArk, Schneider, Victron, Outback, there will not be a bond present in the unit. Allowing the end user to ground outside the unit will allow for safely stringing multiple inverters. I'm very confused by the statement that they are now unsafe without the bond. This makes the units safer and gives the possibility of more usage cases. The only time I would personally want a bond present in the unit is if I were running a single unit in an entirely offgrid set up, an RV application, or marine usage.
I do understand the frustration of having older units that had the bond present but now do not. Changing this made the most sense for the users since there are numerous usage cases and not being bonded was most practical for the majority of these. NG Bonding is a topic that can be confusing and frustrating.
Are you saying it is acceptable to tie the output neutral back to the input neutral of the inverters? That is what schnider and solark *require*. I would need to look up outback, but my bet is they at least allow it and may require it as well. Victron does not require it, but my bet is that they allow it. Furthermore, I can get clear documentation on how these products handle bonding and what is supported.
In the past I have been told by Signature Solar and others that a common neutral configuration is not a permitted configuration. Without the common neutral configuration and no bonding screw, there is no reasonable way to install these safely if the AC input is hooked up to the grid.
Let's look at this simple setup of one of these inverters without the bonding screw in place:

With this
simple setup, there is no NG bond on the output when the inverter is in battery/invert mode. Furthermore, if the installer puts an NG bond in the critical load box, there will be two NG bonds when the inverter is in pass-through mode. Either way, the system is unsafe.
There are only two ways I can think of to make this very simple configuration safe.
- Replace the NG bond screw...But the user does not have the screw and even if they can get the screw it is not clear NG4 supports it.
- Run a neutral connection from the main breaker box neutral bar to the critical load box neutral bar.... But NG4 has not said this is supported and others have said it is not supported.
The same problems exist with the more complex stacked configurations. Without the bonding screws or a common neutral, you can't set them up safely.
BTW: You may want to review this thread as well:
As many of you know, The value-priced inverter manufacturers provide horrible documentation so I have been on a mission to understand the grounding and bonding of the popular value-priced inverters. Edit: Corrected Ground to Neutral. As part of this, the question of 'common Neutral' has come up...
diysolarforum.com
In that thread, I do a deep dive into this set of issues.
I do understand the frustration of having older units that had the bond present but now do not. Changing this made the most sense for the users since there are numerous usage cases and not being bonded was most practical for the majority of these. NG Bonding is a topic that can be confusing and frustrating.
There are *many* aspects of this that are frustrating. Having no way to tell externally if a particular unit shipped with or without the screw is just one of them.
* Changing a fundamental safety characteristic of a product without a broad and detailed communication of the implications.
* No clear documentation of how the inverter handles neutral bonding.
* No clear documentation of what configurations are supported around neutral bonding
* Inconsistent answers to questions about bonding and what is supported.
* Dismissive responses from signature solar that do not answer the questions about bonding and what is supported.
This set of issues was a known problem before EG 4 release their clone. Furthermore, I raised the issues with EG4 as soon as the first inverter was released. The person at EG4 I was working with originally (and is still on this forum) ghosted me after a while. I have also had very unproductive exchanges with signature solar about this.
So yes I am frustrated. The problem is getting worse, not better and because there is no clearly supported way to set them up safely,
my recommendation will remain "Do not use".
There are three simple things EG4 can do to change my mind.
1) Support common neutral wiring.
2) Ship *with* the bonding screw and allow the user to remove it without special permission
3) Clearly document #1 and #2 in the manual.
(This is exactly the same as what I asked EG4 to do when the inverter was first released)
You are welcome to PM me if you would like to discuss this privately.