Newer models of EG4 6500ex are built without the bonding screw

I just tested the continuity between ground and neutral for each inverter, there was none. I also finished setting them up today and ran a small load, worked well.

I agree, in some cases this could be dangerous to operate without the NG bond in the inverters. I haven't checked the manual to see if they added the fact that both screws are out. Will do tomorrow.

Where can I find the build date?
The build date was on the sticker that is over the top screw on the right side of the case.

I wonder if this was a previously returned unit.
Where the previous customer had removed the screw.
I doubt it because it has an in tact sticker over the screws and it's super clean inside. I would expect some dust around the fans if it was used for any amount of time. There's also two of them.

@vladkgb When you opened that case, did you take it apart far enough to look at the back of the board where the screw is? Are there traces that could still contact the metal that the screw screws into?
If this was the case, I would get continuity on ground and neutral right?
 
If this was the case, I would get continuity on ground and neutral right?
Maybe, maybe not. On the 5000ES, we know the screw holds the trace on the back of the board down against the metal. When the screw is removed, the board can flex away from the metal and break the contact.... or it could also stay touching if the board flexes down. I am trying to find out if the 6500 has this possibility.
 
Maybe, maybe not. On the 5000ES, we know the screw holds the trace on the back of the board down against the metal. When the screw is removed, the board can flex away from the metal and break the contact.... or it could also stay touching if the board flexes down. I am trying to find out if the 6500 has this possibility.
Sorry I closed the case up. If I get in there again for whatever reason I can mess with that. But as it is, there's no bond in each of the inverters with those screws gone, so I'm not worried about what you're describing. This is a stationary setup, so there shouldn't be any flex anyway.
 
Maybe, maybe not. On the 5000ES, we know the screw holds the trace on the back of the board down against the metal. When the screw is removed, the board can flex away from the metal and break the contact.... or it could also stay touching if the board flexes down. I am trying to find out if the 6500 has this possibility.
There is no trace on the back of the 5000ES board.
 
There is no trace on the back of the 5000ES board.
Forgive me. I was not precise enough with my statement.

Some of the earlier Growatt 5000ES inverters sold in Europe had traces on the back and that made pulling the screw out an unreliable way to turn off the dynamic bonding. Signature solar had them build a version for the US that did not have this issue. (I do not know if that version is now being sold in Europe or not), Growatt, EG4, and MPP inverters are all designed and built by the same company, so I wanted to see if there is a similar issue with the EG4 6500.
 
Forgive me. I was not precise enough with my statement.

Some of the earlier Growatt 5000ES inverters sold in Europe had traces on the back and that made pulling the screw out an unreliable way to turn off the dynamic bonding. Signature solar had them build a version for the US that did not have this issue. (I do not know if that version is now being sold in Europe or not), Growatt, EG4, and MPP inverters are all designed and built by the same company, so I wanted to see if there is a similar issue with the EG4 6500.
Still incorrect. None of them had it. It was a false statement made by Signature Solar.
 
WOW!!! I had an exchange with EG4 support and they confirmed that they are no longer installing the bonding screw.

This is the message I sent them:
Many people use EG4 inverters with a Reliance multi-circuit transfer switch. This line of transfer switches doesn't switch neutral but is popular for retrofits because it combines the transfer switch and critical load box.

1673985318733.png

If you trace the output neutral, you will see that it ends up connecting back to the input neutral. In order to avoid multiple NG bonds, this requires the bonding screw be removed in the inverter.

Many people have set the inverter up this way and by all reports, it works fine. However, it is very unclear whether this is supported by EG4.

1) Does EG4 support the removal of the bonding screw? If not, then this configuration and *any* multi-inverter stacking will violate the NEC code around Neutral-ground bonding.

2) Assuming the bonding screw is removed, does EG4 support common neutral layouts such as this.


I have tried to get clear answers to these questions from your distributors but have been unable to. Consequently, I am advising people not to use the EG4 inverter in this configuration or any multi-inverter stacked configuration. If I could get a clear statement from EG4 on these questions I would appreciate it.

Note: As with the situation with the input current, the support (or lack thereof) of these two items needs to be clearly documented in the EG4 documentation. There are significant safety implications and the designers/users need clarification on what is allowable.

This was their response:

Because every installation differs, we want to be able to provide the best possible answer for your question/concern. While the bonding screw is now being removed from all units, we do support the removal of ones that currently have it present as long as documentation is provided by the customer to their distributor that an assessment was made by an installer recommending to do so.

We are currently discussing with our engineering department as to the best way to address this concern from yourself and many other customers, so as soon as we have a more concrete answer, we will be sure to reach out and inform you of any updates we receive.

Thank you for your continued support and patience.

EG4 Electronics Support

Edit: Clarified the recommendation.
Since they are no longer shipping with the bonding screw and have not said they support a common neutral. I do not recommend using these inverters in *ANY* configuration that uses the AC inputs tied to the grid. Even the simplest single inverter set-up can not be done safely.
 
WOW!!! I had an exchange with EG4 support and they confirmed that they are no longer installing the bonding screw.

This is the message I sent them:


This was their response:



Since they are no longer shipping with the bonding screw and have not said they support a common neutral. I do not recommend using these inverters in *ANY* configuration. Even the simplest single inverter set-up can not be done safely.
WOW indeed!
 
"we do support the removal of ones that currently have it present as long as documentation is provided by the customer to their distributor that an assessment was made by an installer recommending to do so."

I am having a hard time trying to understand what that means.
I would think it will be the manufacturer/seller is the one that provides the documentation to the installer and the customer.
 
"we do support the removal of ones that currently have it present as long as documentation is provided by the customer to their distributor that an assessment was made by an installer recommending to do so."

I am having a hard time trying to understand what that means.
I would think it will be the manufacturer/seller is the one that provides the documentation to the installer and the customer.
In my opinion, they are making the whole problem worse by making changes to this critical part of the product but not addressing how to set the product up safely in all supported configurations.
 
Last edited:
Bonding externally is always best practice. If you look at almost all major brands like SolArk, Schneider, Victron, Outback, there will not be a bond present in the unit. Allowing the end user to ground outside the unit will allow for safely stringing multiple inverters. I'm very confused by the statement that they are now unsafe without the bond. This makes the units safer and gives the possibility of more usage cases. The only time I would personally want a bond present in the unit is if I were running a single unit in an entirely offgrid set up, an RV application, or marine usage.

I do understand the frustration of having older units that had the bond present but now do not. Changing this made the most sense for the users since there are numerous usage cases and not being bonded was most practical for the majority of these. NG Bonding is a topic that can be confusing and frustrating.
 
Bonding externally is always best practice. If you look at almost all major brands like SolArk, Schneider, Victron, Outback, there will not be a bond present in the unit. Allowing the end user to ground outside the unit will allow for safely stringing multiple inverters. I'm very confused by the statement that they are now unsafe without the bond. This makes the units safer and gives the possibility of more usage cases. The only time I would personally want a bond present in the unit is if I were running a single unit in an entirely offgrid set up, an RV application, or marine usage.

I do understand the frustration of having older units that had the bond present but now do not. Changing this made the most sense for the users since there are numerous usage cases and not being bonded was most practical for the majority of these. NG Bonding is a topic that can be confusing and frustrating.
So the ground screw for the PCB (part of the EMI filter circuit, and Etc.) is removed AFTER compliance certificated is issued, if that is the case then it is no longer complied to test that was done to get compliance.
Did EG4 resubmit the change to the TuV about the change?
 
Bonding externally is always best practice. If you look at almost all major brands like SolArk, Schneider, Victron, Outback, there will not be a bond present in the unit. Allowing the end user to ground outside the unit will allow for safely stringing multiple inverters. I'm very confused by the statement that they are now unsafe without the bond. This makes the units safer and gives the possibility of more usage cases. The only time I would personally want a bond present in the unit is if I were running a single unit in an entirely offgrid set up, an RV application, or marine usage.

I do understand the frustration of having older units that had the bond present but now do not. Changing this made the most sense for the users since there are numerous usage cases and not being bonded was most practical for the majority of these. NG Bonding is a topic that can be confusing and frustrating.
Are you saying it is acceptable to tie the output neutral back to the input neutral of the inverters? That is what schnider and solark *require*. I would need to look up outback, but my bet is they at least allow it and may require it as well. Victron does not require it, but my bet is that they allow it. Furthermore, I can get clear documentation on how these products handle bonding and what is supported.

In the past I have been told by Signature Solar and others that a common neutral configuration is not a permitted configuration. Without the common neutral configuration and no bonding screw, there is no reasonable way to install these safely if the AC input is hooked up to the grid.

Let's look at this simple setup of one of these inverters without the bonding screw in place:

1673990728978.png
With this simple setup, there is no NG bond on the output when the inverter is in battery/invert mode. Furthermore, if the installer puts an NG bond in the critical load box, there will be two NG bonds when the inverter is in pass-through mode. Either way, the system is unsafe.

There are only two ways I can think of to make this very simple configuration safe.
  1. Replace the NG bond screw...But the user does not have the screw and even if they can get the screw it is not clear NG4 supports it.
  2. Run a neutral connection from the main breaker box neutral bar to the critical load box neutral bar.... But NG4 has not said this is supported and others have said it is not supported.

The same problems exist with the more complex stacked configurations. Without the bonding screws or a common neutral, you can't set them up safely.


BTW: You may want to review this thread as well:


In that thread, I do a deep dive into this set of issues.

I do understand the frustration of having older units that had the bond present but now do not. Changing this made the most sense for the users since there are numerous usage cases and not being bonded was most practical for the majority of these. NG Bonding is a topic that can be confusing and frustrating.
There are *many* aspects of this that are frustrating. Having no way to tell externally if a particular unit shipped with or without the screw is just one of them.

* Changing a fundamental safety characteristic of a product without a broad and detailed communication of the implications.
* No clear documentation of how the inverter handles neutral bonding.
* No clear documentation of what configurations are supported around neutral bonding
* Inconsistent answers to questions about bonding and what is supported.
* Dismissive responses from signature solar that do not answer the questions about bonding and what is supported.

This set of issues was a known problem before EG 4 release their clone. Furthermore, I raised the issues with EG4 as soon as the first inverter was released. The person at EG4 I was working with originally (and is still on this forum) ghosted me after a while. I have also had very unproductive exchanges with signature solar about this.

So yes I am frustrated. The problem is getting worse, not better and because there is no clearly supported way to set them up safely, my recommendation will remain "Do not use".

There are three simple things EG4 can do to change my mind.

1) Support common neutral wiring.
2) Ship *with* the bonding screw and allow the user to remove it without special permission
3) Clearly document #1 and #2 in the manual.

(This is exactly the same as what I asked EG4 to do when the inverter was first released)

You are welcome to PM me if you would like to discuss this privately.
 

Attachments

  • 1673987767443.png
    1673987767443.png
    101.5 KB · Views: 6
Last edited:
I've always wondered if it would be possible to make this a configuration option in the 6500s. The inverter already programmatically enables/disables the bond depending on whether or not your in grid-bypass or not, so why not expose that configuration ability in the inverter settings? That way depending on each persons unique needs, they can set the bond appropriately. Default it to "on" for each inverter and allow people to turn the bond off no matter which mode the inverter is in.
 
I've always wondered if it would be possible to make this a configuration option in the 6500s. The inverter already programmatically enables/disables the bond depending on whether or not your in grid-bypass or not, so why not expose that configuration ability in the inverter settings? That way depending on each persons unique needs, they can set the bond appropriately. Default it to "on" for each inverter and allow people to turn the bond off no matter which mode the inverter is in.
I can not say definitely, but I am pretty sure the hardware uses the same signal for the bonding relay as it uses for the transfer switch. If that is the case, the firmware is unable to disable the bonding relay without also disabling the transfer switch.

What you describe, is exactly what Victron does with their systems. If EG4 has any common sense, they would do this on future products. The other thing they should consider is creating a product that does common neutral and no bonding. This product would be the best for the home market but would be difficult to use in the mobile market.
 
I can not say definitely, but I am pretty sure the hardware uses the same signal for the bonding relay as it uses for the transfer switch. If that is the case, the firmware is unable to disable the bonding relay without also disabling the transfer switch.

What you describe, is exactly what Victron does with their systems. If EG4 has any common sense, they would do this on future products. The other thing they should consider is creating a product that does common neutral and no bonding. This product would be the best for the home market but would be difficult to use in the mobile market.
Yeah, it’s hard to say for sure. It’s almost seems like common sense though.

I’m supposed to have a call with one of their techs this week and exposing the option in the configuration is one of my many questions I want to get answered.
 
@BenFromSignatureSolar

In the past, I have tried to fill the information void left by EG4 by documenting how to properly do the grounding and bonding of the 6500 and posting it on the resource section of this forum. I have updated the document and my recommendations based on this latest revelation.

 
I looked up an outback inverter and found this in the manual.

1673999123050.png

Since only one of the neutral terminals are required to be hooked up, the two neutral posts are clearly tied together internally. This inverter ALWAYS opperates as a common neutral system.
 
Bonding externally is always best practice. If you look at almost all major brands like SolArk, Schneider, Victron, Outback, there will not be a bond present in the unit. Allowing the end user to ground outside the unit will allow for safely stringing multiple inverters. I'm very confused by the statement that they are now unsafe without the bond. This makes the units safer and gives the possibility of more usage cases. The only time I would personally want a bond present in the unit is if I were running a single unit in an entirely offgrid set up, an RV application, or marine usage.

I do understand the frustration of having older units that had the bond present but now do not. Changing this made the most sense for the users since there are numerous usage cases and not being bonded was most practical for the majority of these. NG Bonding is a topic that can be confusing and frustrating.
When did the change take place?
 
WOW!!! I had an exchange with EG4 support and they confirmed that they are no longer installing the bonding screw.

This is the message I sent them:


This was their response:



Edit: Clarified the recommendation.
Since they are no longer shipping with the bonding screw and have not said they support a common neutral. I do not recommend using these inverters in *ANY* configuration that uses the AC inputs tied to the grid. Even the simplest single inverter set-up can not be done safely.
Nice, I haven't put mine in operation yet but they are installed and wired.

F-ing mess.
 
Bonding externally is always best practice. If you look at almost all major brands like SolArk, Schneider, Victron, Outback, there will not be a bond present in the unit. Allowing the end user to ground outside the unit will allow for safely stringing multiple inverters. I'm very confused by the statement that they are now unsafe without the bond. This makes the units safer and gives the possibility of more usage cases. The only time I would personally want a bond present in the unit is if I were running a single unit in an entirely offgrid set up, an RV application, or marine usage.

I do understand the frustration of having older units that had the bond present but now do not. Changing this made the most sense for the users since there are numerous usage cases and not being bonded was most practical for the majority of these. NG Bonding is a topic that can be confusing and frustrating.
What IS unsafe and totally against any certifications is changing this mid production run without apparent knowledge.
This is crazy.
 
My recommendation is always remove the screw and use a common neutral. So, this just saves the respondent a step.
Or maybe not, if they don't know which version they have.
Is there any documentation that comes with the units that no longer have the bonding screw?
Or a big sticker on the front that states, "no internal bonding included".
 
EG4 has confirmed that they are removing bonding screws on all of their inverter models.

Unfortunately, they refuse to answer whether or not they support a common neutral configuration.

My questions to them:
1) Does EG4 support configurations on the 6500 EX where the output neutral ends up being tied back to the input neutral? (I have asked this question multiple times without a clear yes or no answer)

2) Does the decision to not ship with the bonding screw apply to all of the EG4 inverters?

Their response
To answer you questions:
  1. Due to our liability policies, we cannot give advice on the AC wiring configurations of a system since, as I have mentioned, every install differs and should be assessed on an install to install basis by the qualified person on that site. Be on the lookout for a video that clarifies the NGB issue coming soon to our Youtube channel that will explain the way it functions in our systems.

  2. Yes this applies to all of our units.
Regards,

EG4 Electronics Support

They are removing the bonding screws from all of their inverters, but they refuse to say they support the only way to make the system safe without bonding screws for most configurations.
 
I just received my replacement units a few days ago and I can confirm both units had the bonding screws removed. I had earlier units with the manufactured sticker showing 07/22 and those had the bonding screws. The newer units I have show 10/22 and those have them removed.
 
I had earlier units with the manufactured sticker showing 07/22 and those had the bonding screws. The newer units I have show 10/22 and those have them removed.
That is good data to have. It narrows down the manufacture date of the change. Is this for the 6500EX?
 