Not really following what you are saying.
But with two sources, you have to make sure that every conductor or bussing can handle what the two sources could put on them.
On a load side tap, the two sources can combine. On a line side tap, they can't.
This is the reason why a load side tap, must be at the opposite end of the panel bussing. To lesson the two sources from fully combining in a single place. But since it still can, there's a limit on the total of the two sources.
By "load side tap" I don't mean branch breaker installed in breaker panel busbar.
I mean Polaris or insulation piercing connector installed on cable between main breaker (e.g. 100A) and a sub panel with its own main breaker (e.g. 100A).
Let's say the tap goes to a 100A fused disconnect.
And the "Y" shape of wire is 2 awg, so fine for 100A but certainly not 200A.
Not an "E" shape bunch of wires like the busbar in a breaker panel. If it was, backbone of "E" is a busbar, needs to carry sum of current. Body of Polaris serves that purpose in my case.
Thevenin says 100A from grid + 100A from PV = 200A available at intersection of "Y" to go out third leg.
But sub panel has 100A breaker, so that is the most current that can flow.
A 2 awg wire after intersection of "Y" has 200A available to it, but protected by 100A breaker at far end.
That is a "Feeder Tap".
In image below, the extra breakers at near end of run because length 25' > 10'
If they had been 10'and in metal conduit, then "Feeder Tap" and rely on OCP at far end.
For our case, consider "GEN" to be "Inverter", and instead of a transfer switch just wired in parallel.
Do I need to put Breakers for 2 Separate Panel board feeders supplied from load side of Automatic transfer switch with Utility and Stand by generator sources the 2 Panel boards are within 25 Ft from Service entrance ATS (with Stand by generator source) and has their own main breakers as well...