Found a bunch of NTC current limiter resistors from an old power supply. Turns out these are perfect size for reducing inrush current from 2 HP air compressor. They are 2 ohm 23A 260Vac SG-420 limiters.

Lets see if they help reduce air compressor peak startup current. Here is a measurement without the limiters. Peak current 50.4A (35.5A rms). Compressor takes 0.25 sec. to start.

Next I connect 2 limiters in series with the air compressor. Peak current reduced to 36.8A (25.9A rms) or 27% reduction in surge current. Compressor takes 0.75 seconds to start.

I tried 3 limiters in series but it did not reduce surge current, it only made it take longer to start.

The results with the chop saw did not come out as good. While it does reduce peak surge from 170A to <50A, on subsequent starts the effect goes away because NTC resistors don't get enough time to cool down which keeps their resistance low.
First start 49.6A peak current.

Second start 59.2A peak current.

Third start 76A peak current.

So it looks like these NTC limiters would work OK for inductive load motor starting once in 5 - 10 minutes (hvac compressor also fits this duty cycle profile). For universal motors that start often these don't work so well and thyristor chopper limiter should work better.

Lets see if they help reduce air compressor peak startup current. Here is a measurement without the limiters. Peak current 50.4A (35.5A rms). Compressor takes 0.25 sec. to start.

Next I connect 2 limiters in series with the air compressor. Peak current reduced to 36.8A (25.9A rms) or 27% reduction in surge current. Compressor takes 0.75 seconds to start.

I tried 3 limiters in series but it did not reduce surge current, it only made it take longer to start.

The results with the chop saw did not come out as good. While it does reduce peak surge from 170A to <50A, on subsequent starts the effect goes away because NTC resistors don't get enough time to cool down which keeps their resistance low.
First start 49.6A peak current.

Second start 59.2A peak current.

Third start 76A peak current.

So it looks like these NTC limiters would work OK for inductive load motor starting once in 5 - 10 minutes (hvac compressor also fits this duty cycle profile). For universal motors that start often these don't work so well and thyristor chopper limiter should work better.