First posting to this forum. While I have 35+ years of professional PV and battery system design experience, I'm retired now so a bit rusty on my NEC, especially the recent Code cycles.
I'm designing the battery side of my 2x EG4 18kpv system, which is currently operating well in grid tied mode fed by 9s x 8p Znshine 450's. My county is still on the 2014 Code cycle, so it looks like I have some options for my battery system design that might not be available to folks on more recent Code revisions. I'd like to build up my own LiFePo4 battery system using 304ah prismatic cells and JK BMS's.
Here's my question. Neither polarity of the battery lugs on the EG4 inverters are grounded. This is just fine per NEC 250 VIII because it operates under 60Vdc. So far so good.
However, article 240 requires OCPDs for all ungrounded current carrying conductors. So my conclusion is that to be Code compliant I either need to use a listed two pole breaker, two single pole breakers, or two battery fuses for each battery. Not one only for the positive conductor, as is shown in the EG4 18Kpv manual and is commonly being done by members of this forum.
Am I missing something here? If so, can someone point to the Code section allowing only a single OCPD in the positive leg when both positive and negative conductors are ungrounded?
I'm designing the battery side of my 2x EG4 18kpv system, which is currently operating well in grid tied mode fed by 9s x 8p Znshine 450's. My county is still on the 2014 Code cycle, so it looks like I have some options for my battery system design that might not be available to folks on more recent Code revisions. I'd like to build up my own LiFePo4 battery system using 304ah prismatic cells and JK BMS's.
Here's my question. Neither polarity of the battery lugs on the EG4 inverters are grounded. This is just fine per NEC 250 VIII because it operates under 60Vdc. So far so good.
However, article 240 requires OCPDs for all ungrounded current carrying conductors. So my conclusion is that to be Code compliant I either need to use a listed two pole breaker, two single pole breakers, or two battery fuses for each battery. Not one only for the positive conductor, as is shown in the EG4 18Kpv manual and is commonly being done by members of this forum.
Am I missing something here? If so, can someone point to the Code section allowing only a single OCPD in the positive leg when both positive and negative conductors are ungrounded?