CharlieInSoCal
New Member
- Joined
- Apr 2, 2021
- Messages
- 5
I think this is the correct place to post ...
We are putting in a barn that if I brought grid power to it I'm looking at about 450 ft away from the closest sub panel in the garage. To run a single 15 amp circuit calls for 3 AWG wire to keep voltage to below recommended 3%, and this is about $2300 in THHN/THWN wire alone. Add in conduit, trenching, and other costs, not happening.
So, looking at solar just for lighting, and use a 4000 watt generator I already own for any non lighting needs.
I already have solar for my house (3000 excess kWh last year, will go to zero or near zero with out addition of PHEV vehicles), so I've got real world monthly numbers of solar generation at my specific location.
I'm planning to use twelve (12) four foot LED tube fixtures that are 24 watts each and produce 3100 lumens at 6500K. I will use six fixtures in the center aisle and three fixtures on each side of the barn (one fixture in the center of each stall). We would use the lighting maybe an two hours max per day in winter, half of that spring/fall, and likely very little summer. As to summer, depending on how temps play out, we may have some ceiling fans for air movement -- though we have excellent prevailing winds from the cooler coastal air (we are 12 miles as the crow flies to the Pacific), and the barn is a raised center aisle with one foot of open space top of barn wall to roof eave overhang along the entire length of both sides, and the same one foot gap along the sides of the raised center aisle roof -- i.e. should get good ventilation.
So, with maybe two hours max use per day use of 300 watts (rounded up), this should be roughly 25 to 50 amp hours max, and typically much less as the lights will be on three separate switches (center and each of the two sides of the barn) and my wife says she would probably most of the time use just the center aisle switches.
PVwatts and real history say the planned single 72 cell 370 watt panel will give me 30 kWh in the worst month and about 58 kWh in the best months (about 535 kWh for the year), I'm leaning to a single 12 volt battery with 100 AH to 150 AH (can always add another battery if needed).
I like the All in Ones (such as MPP Solar LV1212) but it looks like I can't set up the inverter to be switched on/off via an external switch. So, maybe separate charge controller (40 amp MPPT) and 1000 watt pure sign wave inverter with remote on/off (equipment is likely going to be away from the entry light switches (I'll rewire remote on/off to a light paddle switch), and then the appropriate fuses.
Permit application submitted this week. Permit process could be months (sad), then grading. Barn will be installed in two days (pre engineered barn). Then sprinkler system installed and final inspection. All solar (or electric if I did run power) after barn is signed off and approved.
So, questions are:
- Any feedback on approach?
- All in One or separate charge controller and inverter?
- Best battery technology with least fire risk (AGM, LifePO4, or Bolt Ultra Silicate-Salt)? FYI, building codes require barn to have fire sprinkler system.
Thanks in advance for comments and feedback.
We are putting in a barn that if I brought grid power to it I'm looking at about 450 ft away from the closest sub panel in the garage. To run a single 15 amp circuit calls for 3 AWG wire to keep voltage to below recommended 3%, and this is about $2300 in THHN/THWN wire alone. Add in conduit, trenching, and other costs, not happening.
So, looking at solar just for lighting, and use a 4000 watt generator I already own for any non lighting needs.
I already have solar for my house (3000 excess kWh last year, will go to zero or near zero with out addition of PHEV vehicles), so I've got real world monthly numbers of solar generation at my specific location.
I'm planning to use twelve (12) four foot LED tube fixtures that are 24 watts each and produce 3100 lumens at 6500K. I will use six fixtures in the center aisle and three fixtures on each side of the barn (one fixture in the center of each stall). We would use the lighting maybe an two hours max per day in winter, half of that spring/fall, and likely very little summer. As to summer, depending on how temps play out, we may have some ceiling fans for air movement -- though we have excellent prevailing winds from the cooler coastal air (we are 12 miles as the crow flies to the Pacific), and the barn is a raised center aisle with one foot of open space top of barn wall to roof eave overhang along the entire length of both sides, and the same one foot gap along the sides of the raised center aisle roof -- i.e. should get good ventilation.
So, with maybe two hours max use per day use of 300 watts (rounded up), this should be roughly 25 to 50 amp hours max, and typically much less as the lights will be on three separate switches (center and each of the two sides of the barn) and my wife says she would probably most of the time use just the center aisle switches.
PVwatts and real history say the planned single 72 cell 370 watt panel will give me 30 kWh in the worst month and about 58 kWh in the best months (about 535 kWh for the year), I'm leaning to a single 12 volt battery with 100 AH to 150 AH (can always add another battery if needed).
I like the All in Ones (such as MPP Solar LV1212) but it looks like I can't set up the inverter to be switched on/off via an external switch. So, maybe separate charge controller (40 amp MPPT) and 1000 watt pure sign wave inverter with remote on/off (equipment is likely going to be away from the entry light switches (I'll rewire remote on/off to a light paddle switch), and then the appropriate fuses.
Permit application submitted this week. Permit process could be months (sad), then grading. Barn will be installed in two days (pre engineered barn). Then sprinkler system installed and final inspection. All solar (or electric if I did run power) after barn is signed off and approved.
So, questions are:
- Any feedback on approach?
- All in One or separate charge controller and inverter?
- Best battery technology with least fire risk (AGM, LifePO4, or Bolt Ultra Silicate-Salt)? FYI, building codes require barn to have fire sprinkler system.
Thanks in advance for comments and feedback.