Hi,
I'm constructing 3x 18foot diameter geodesic domes on my property and aiming to go fully off grid.
Each dome will have a heat pump, small microwave (700watts), small coffee maker (550watts) and bar fridge (800watts) , sink, shower and compost toilet. Water pump will be a separate submersible unit in a rain water tank system powered by it's own means and hot water supplied by propane on demand system.
24v vs 48v Battery System
If I go 48v, that would present the option of going with a 48v heat pump and not have the inverter take the hit on that allowing me to go with a lower wattage inverter. Downfall being an extra 1000$+ per heat pump for the dc model and having to order a 12000btu (https://ecosolaris.com/en/produit/off-grid-solar-ac-dc4812/) vs 9000btu (https://senville.ca/9000-btu-mini-split-air-conditioner-senl-09cd/) and being 12000btu vs 9000btu would also use more power than needed to heat/cool the space. Having written this, I think I just talked myself out of going 48v...
If I go with the 9000btu which is 782watts, rated current of 6.8amps, minimum 16amp breaker requirement then a 5kw should be more than enough to handle the above mentioned items with their inrush currents? (5000w/110v = ~45amp)
We don't plan on running the domes year round but only during the summer/fall season, I don't suspect the heat pump will need to be running 24/7, if I stay away from the 48v system and run 24v, then would a 24v 100Ah LiFe04 battery suffice or larger? If it wasn't enough I could always add another 100Ah in parallel but would like to have my order done as to avoid shipping charges and delays from China.
If running the 100Ah battery, one 375 watt panel should suffice to charge it during summer and 2x 375watt panels if going with the 200Ah battery?
Thank you to anyone who decided to have a read on this
I'm constructing 3x 18foot diameter geodesic domes on my property and aiming to go fully off grid.
Each dome will have a heat pump, small microwave (700watts), small coffee maker (550watts) and bar fridge (800watts) , sink, shower and compost toilet. Water pump will be a separate submersible unit in a rain water tank system powered by it's own means and hot water supplied by propane on demand system.
24v vs 48v Battery System
If I go 48v, that would present the option of going with a 48v heat pump and not have the inverter take the hit on that allowing me to go with a lower wattage inverter. Downfall being an extra 1000$+ per heat pump for the dc model and having to order a 12000btu (https://ecosolaris.com/en/produit/off-grid-solar-ac-dc4812/) vs 9000btu (https://senville.ca/9000-btu-mini-split-air-conditioner-senl-09cd/) and being 12000btu vs 9000btu would also use more power than needed to heat/cool the space. Having written this, I think I just talked myself out of going 48v...
If I go with the 9000btu which is 782watts, rated current of 6.8amps, minimum 16amp breaker requirement then a 5kw should be more than enough to handle the above mentioned items with their inrush currents? (5000w/110v = ~45amp)
We don't plan on running the domes year round but only during the summer/fall season, I don't suspect the heat pump will need to be running 24/7, if I stay away from the 48v system and run 24v, then would a 24v 100Ah LiFe04 battery suffice or larger? If it wasn't enough I could always add another 100Ah in parallel but would like to have my order done as to avoid shipping charges and delays from China.
If running the 100Ah battery, one 375 watt panel should suffice to charge it during summer and 2x 375watt panels if going with the 200Ah battery?
Thank you to anyone who decided to have a read on this