Ok, so this thread is an extension to my original 12V 3300W off-grid build here.

I started a new thread for focus.

What I've basically done is add additional RCD protection to the system by adding RCBO breakers to both AC outputs of the inverter.

Things you should know for context:
- Inverter has no N-G bond
- Inverter has no RCD protection
- Inverter 2 AC outputs / receptacles
- each AC output is running into separate RCBOs via the consumer/sub panel (see images & schema)
- N-G bond made in the consumer panel

My assumption
- If a get a ground fault on one of the AC outputs, then only the RCBO for that output should trip

Here's what is actually happening:
- If I simulate a ground fault on AC output 1 (I do this using the Low Impedance (LoZ) feature on my Digital Multimeter (DMM) by touching the DMM prongs on the RCBO), then both RCBOs trips
- Same behaviour goes for AC Output 2, i.e. if I simulate a ground fault then both RCBOs trip

Here's my questions:
- Can someone please explain what is going on here? I don't understand why a ground fault on one of the AC outputs is causing both RCBOs to trip. It's as if both AC outputs are on the same circuit?
- Are both RCBOs tripping because of the way the inverter is internally wired OR because I added a N-G bond? Can I do additional tests to confirm which?
- Am I causing any safety issues with my wiring?


Kinds Regards
GeeGee


Basic Schema

1732615950798.png


1732622183667.jpeg

1732622195642.jpeg
 
Last edited:
Your N/G bond is on the wrong side of the RCBOs.
It should be on the line side (input).
 
ok, tx and tx for the quick reply......its appreciated

I will re-wire tomorrow and test again and post back my results....fingers crossed.

GeeGee
 
I didn't think australia had N-G bond because it had no Neutral - all 230vac or 3-phase?
 