Having said all of that. I do not know of a device that will automaticly switch panels in and out of the array..... It would typically not be needed on an MPPT controller.
Found a schematic :So it is separate from the Midnite? Is it between the panels and and the midnight? Or is it between the battery and the Midnight?
If it is between the panels and the midnight..... it should never pop.
If it is betwwn the midnite and the battery it should be larger. It should be at least a 94A x 1.25 = 117. Round that up to a 120A.
You should never run a fuse or a breaker right at it's trip value.
Because the MPPT controller clamps voltage. , yes?Having said all of that. I do not know of a device that will automaticly switch panels in and out of the array..... It would typically not be needed on an MPPT controller.
Is it #16 or number #17 on the diagram that is popping? What are the trip ratings on each?Found a schematic :
No. Because MPPT controllers typically limit the current. The controller can not limit the voltage and If you let the voltage get too high it will damage the MPPT controller.Because the MPPT controller clamps voltage. , yes?
Because the MPPT controller clamps voltage. , yes?
I’m talking about #16 fuseSorry, yes your right of course. But if the array is 24V and this fuse is tripping, although rarely. Would it just be heat?
And could I add 2P (400W ea) and increase the fuse to 130A . Would the MidNite at 96A tolerate that safety or is it too much?
Again, thank youI’m talking about #16 fuse
Sorry, yes your right of course. But if the array is 24V and this fuse is tripping, although rarely. Would it just be heat?
And could I add 2P (400W ea) and increase the fuse to 130A . Would the MidNite at 96A tolerate that safety or is it too much?
OK..... thank you for the information. If that is a 100A breaker between the combiner box and the midnite, something seems really wrong. Could you tell me the Voc and Isc of the panels? (Or the make/model of the panels) Also, what size breakers are in the combiner box?I’m talking about #16 fuse
I hear ya! That midnite classic is not a cheap item.But because I want to add more panels, I’m trying to understand so I don’t reck the MidNite .
Thank you , you are so kind! I did a lot of reading on the MidNite last night and I found the bit about 174VocI just sent Midnite a message asking about over-paneling. Once I get an answer and we have the Voc and Vsc of the panels we can look at what can work. We can also look at how to minimize the impact of the shading.
I’m interested to hear how big your wires are back from your combiner box?!? Any design room to bump up the voltage Instead of throwing away photons?
Also I go down to -40C in winter averaging -22C so how does that affect the 174Voc @ -10C?The from the Pv to the combiner box are #6 AWG
The other 2 panels are 385W, Isc: 10.1A, Voc: 48.21, Imp: 9.61, Vmp : 40.05The from the Pv to the combiner box are #6 AWG