So correct me if wrong in this scenario
@smoothJoey .
- An appliance is rated at 50 amps max.
- You ridiculously oversize the wire to 2/0 gauge.
- Before the wire you have a 50 amp fuse.
- You push 80 amps through the fuse, which would blow that fuse.
- The wire can more than handle 80 amps.
- Would that fuse then be considered to protect the appliance instead of the wire?
If by appliance one refers to either a load or a charge source and not a battery or other in-line components of the circuit.
Those appliances regulate current.
If there is a short upstream then the appliance is out of harms way.
If there is a short downstream then the appliance regulates the current.
If the appliance has an internal short then the fuse will protect the wire.
Its too late for the appliance.
The scenario I can see where a fuse may protect an "appliance" is if there are inline "appliances" that don't regulate current.
Like a BMS, battery protect or shunt etc...
I'm thinking that those should be treated as part of the wire and the fuse should be sized to protect the wire(including these "appliances").
I guess it also depends on one's definition of "appliance".
Thanks for making me think.