Outback Skybox LFP settings and netmetering with backup using battery challenges
goldserve
I finally set up the Outback skybox and it is great. I got 2 x EG4 batteries so I wanted to post my settings to have people check if I could optimize the system even more.
One of the challenges was to get the skybox to use battery whenever the LCOE (levelized cost of energy) is lower than the grid TOU rates. Right now, I'm using self consumption and it is using the battery but not exactly the way I want the skybox to.
Here are my settings from OpticsRE:
SUBSECTION : STATUS
ATTRIBUTES :
Current Status : FAULT
Power Factor : -0.99
AC Voltage : 246.1 V
Solar Input : OK
Grid Input : OK
Load Input : OK
Battery Input : OK
Generator Input : OK
Solar Output : OK
Grid Output : OK
Load Output : OK
Battery Output : OK
Generator Output : OK
Solar Other : 128
Grid Other : OK
Load Other : OK
Battery Other : OK
Generator Other : OK
Units Detected : 1
Model Number : SBX5048_120_240
SUBSECTION : CONFIG
ATTRIBUTES :
Nominal AC Output Voltage : 120/240 (US Models)
Nominal Frequency : 60 Hz
RSD Rapid Shutdown Response : PV
CT Type : Custom
Rated Current : 300 A
Phase Shift : 0
Turns Ratio : 3,000
Units Installed : 1
Role : Master
Endpoint Termination : Enable
12V AUX port : Off
Relay AUX port : Off
TAB : PV
SUBSECTION : STATUS
ATTRIBUTES :
PV Voltage : 12 V
PV Current : 0 A
PV Wattage : 0 KW
Peak Power : 5,525.16 W
Date and Time of Peak Power : 04/23/2021 12:09
Highest Voc : 561.9 V
Date and Time of Voc Occurrence : 05/13/2015 21:44
SUBSECTION : CONFIG
ATTRIBUTES :
Vmp : 30.9 V
Voc : 38.1 V
Imp : 8.58 A
Isc : 9.08 A
Pmp : 265 W
Module Type : Polycrystalline
Number of Parallel Strings : 2
Number of Modules in Series per String : 8
Array Size (STC Watts) : 0 KW
TAB : Grid
SUBSECTION : STATUS
ATTRIBUTES :
Frequency : 59.99 Hz
Power Factor : 1
Grid Sell Timer Status : 00:00 MIN:SEC
AC Voltage : 246 VAC
SUBSECTION : CONFIG
ATTRIBUTES :
Grid desired mode : Self-consumption
GridZero Max Threshold : 4 KW
Charge Limit : 6 KW
Demand Cap Enable : Yes
Maximum grid demand limit : 12 KW
Enable time of use rates : Yes
Cost of Energy per kWh (flat rate) : 0
Grid Interconnection Profile : IEEE 1547 2003
Sell Limit : 5 KW
HV1 (%VACnom) : 110 %VACnom
LV1 (%VACnom) : 88 %VACnom
HV2 (%VACnom) : 120 %VACnom
LV2 (%VACnom) : 50 %VACnom
HVTRP1 : 1 SECS
LVTRP1 : 2 SECS
HVTRP2 : 0.16 SECS
LVTRP2 : 0.16 SECS
RCDL : 60 SECS
HVRC : 108 %VACnom
LVRC : 90 %VACnom
HFRC : 0.4 Hz
LFRC : 0.6 Hz
HF1 : 0.5 Hz
LF1 : 0.7 Hz
HFTRP1 : 0.16 SECS
LFTRP1 : 0.16 SECS
TAB : Load
SUBSECTION : STATUS
ATTRIBUTES :
Percent of Skybox Capacity : 11 %
L1 Total Load : 0.18 KW
L1 Self Supply : 0 KW
L2 Total Load : 0.41 KW
L2 Self Supply : 0 KW
Lifetime Self Supply : 1.19 MWh
SUBSECTION : CONFIG
ATTRIBUTES :
Enable Off-Grid AC Load Management : Off
Load Management Threshold : 35 %
Drop 240v on Grid Disconnect : No
Drop 240v on Low SOC : No
Drop L2 on Low SOC : No
TAB : Battery
SUBSECTION : STATUS
ATTRIBUTES :
State of Charge : 60 %
Charge Status : Charger Off
Battery Voltage : 53 V
Battery Temperature : N/A
Remaining Run Time : 00:08:54 dd:hh:mm
Temperature Compensation Offset : 0 V
Cumulative Discharge : 0.05 kWh
Battery Discharging Lifetime : 0 MWh
Days Since Charged Parameters Met : 0
Lowest Battery SOC : 99 %
Lowest Battery Voltage : 52.87 V
SUBSECTION : CONFIG
ATTRIBUTES :
Battery Series : Custom
Battery Model Number : CUSTOM LITHIUM
Battery Description : EG4_LIFEPO4
Battery amp-hours per string : 200 Ah
Battery Installation Date : 07/2022
Battery Manufacture Date : 01/2022
Charge Efficiency Factor : 98 %
Battery Installation Cost : 0
Absorb end amps per string : 10 A
Charge amps per string : 60 A
Discharge amps per string : 100 A
Number of strings : 1
Battery Levelized Cost of Energy : 0.07
Lifetime Cycles : 1,500
Minimum SOC : 35 %
Maximum SOC : 100 %
Absorb Charge : Timed
Absorb Voltage : 57.4 V
Rebulk Voltage : 51.2 V
Max Absorb Time : 02:00 HRS:MIN
Low Battery Cut-Out Voltage LBCO : 48 V
High Battery Cut-Out Voltage HBCO : 58.4 V
LBCO Time Delay : 00:10 MIN:SEC
HBCO Time Delay : 00:10 MIN:SEC
Low Battery Restart : 49 V
High Battery Restart : 58.4 V
battery_charge_amps_per_string : 30 A
TAB : Generator
SUBSECTION : STATUS
ATTRIBUTES :
Generator Status : Off
Frequency : 0 Hz
Power Factor : 1
Total runtime : 00:00 HRS:MIN
Last Start Reason : None
Output Voltage : 20.3 V
SUBSECTION : CONFIG
ATTRIBUTES :
Generator Max Input Current Limit : 60 A
Support Threshold : 6 kVA
High Voltage Limit L-N : 130 V
Low Voltage Limit L-N : 105 V
High Frequency Limit : 63 Hz
Low Frequency Limit : 57 Hz
Generator Type : AC
Output Rating : 5 kVA
Connect Delay : 30 SECS
Disconnect Delay : 1 SECS
Warm Up Time : 00:00 MIN:SEC
Cool Down Time : 05:00 MIN:SEC
Enable AGS on low battery : No
SOC Level to Start : 50 %
SOC Level to Stop : 80 %
24 Hour Voltage Start Level : 48.8 V
2 Hour Voltage Start Level : 47.2 V
2 Min Voltage Start Level : 44 V
Enable AGS Start on Load : No
Load Start : 5 KW
Load Start Delay : 5 MIN
Load Stop : 5 KW
Load Stop Delay : 1 MIN
Enable AGS Quiet : No
Weekday Quiet Time Begin : 00:00 HRS:MIN
Weekday Quiet Time End : 00:00 HRS:MIN
Weekend Quiet Time Begin : 00:00 HRS:MIN
Weekend Quiet Time End : 00:00 HRS:MIN
Enable AGS Exercise : No
Generator Exercise Start : 12:00 HRS:MIN
Exercise Duration : 15 minutes
Exercise Interval : Monthly
Excersise day of month : 1
TAB : Firmware
SUBSECTION : STATUS
ATTRIBUTES :
Running Version : 1.5.30
Last Check for Update :
Latest Version Found : N/A
Downloaded Version : N/A
Local Drive Detected : N/A
Optimized battery while monitoring boms.
TAB : Battery
SUBSECTION : STATUS
ATTRIBUTES :
State of Charge : 98 %
Remaining Run Time : 00:12:11 dd:hh:mm
Cumulative Discharge : 7.87 kWh
Battery Discharging Lifetime : 0.01 MWh
Lowest Battery SOC : 57 %
Lowest Battery Voltage : 51.92 V
SUBSECTION : CONFIG
ATTRIBUTES :
Charge amps per string : 80 A
Minimum SOC : 35 %
Maximum SOC : 100 %
Absorb Voltage : 55 V
Rebulk Voltage : 51 V
Max Absorb Time : 00:10 HRS:MIN
Low Battery Cut-Out Voltage LBCO : 49 V
High Battery Cut-Out Voltage HBCO : 58 V
Low Battery Restart : 50 V
High Battery Restart : 57 V