RCinFLA
Solar Wizard
- Jun 21, 2020
- 3,561
With disconnect PV power and grid connection, try a near 5 kW load on inverter (like water heater + clothes drier) to see how much battery voltage drops.
5 kW should pull about 120 amps from battery so a 280 AH LFP string should hand it with no problem.
Each 280 AH cell should not drop more than 0.1 vdc so 1.6v max for string, plus any other cable, breaker, or connections loss. Net should be less then 2v drop at inverter DC input between light load and 5 kW load, so not less than 48-49 vdc at inverter terminals.
That would check inverter and battery for excessive battery voltage drop. Should be ready to check voltage at inverter input, before and after BMS near batteries if it does have excessive net voltage drop to find where it is dropping.
Having a cheap IR temp gun to point at connections is a quick way to check for heating due to poor connections.
I would guess bad connection, bad bms, or bad cell. Beyond that it might be a intermittant issue in inverter.
Double check you don't have selling to grid enabled on inverter from batteries during the night.