kcbuild
New Member
Thanks Sunshine-eggoIf DC negative is already grounded, that means your AC and DC grounds are the same, so it technically shouldn't matter.
The preference is to run a ground wire from the chassis screw to the AC ground that is connected to an earth rod.
Everything above the ground (dirt) bonded.
Everything below the ground (dirt) bonded.
ONE connection from above ground to below.
Worth watching link #7 in my signature from the timestamp linked.
No ground rods at array. Run a ground conductor from the panel frame along with the PV wires back to the system ground.
With a 2P array, you don't need any fusing or breakers to protect the wire. PV wire should be sized for 1.25X array Isc and fused for 1.25X that value if your array is 3P or more. In a single string or 2P, the panels themselves will act as fuses before the panel wires will burn up. In 3P or greater arrays, a short circuit of two strings through a 3rd string (or more) could exceed the panel wire rating and cause the panel wire to catch fire.
I relax the fine strand requirement on the PV input of the MPPT because it's lower current than the output, but it is very important to properly secure the wire in the terminals.
100A fine strand wire from MPPT to battery with 125A fuse/breaker.
Probably not all cells within the battery, but probably the battery temperature in 2 locations.
From the Lynx Smart BMS manual:
Low temperature or high cell voltage cut off
If a cell voltage becomes too high and has reached the high cell voltage threshold (3.75V hard coded in battery), or if the low temperature threshold (adjustable in battery) has been reached, the ATC contact opens and will turn off all chargers. If the Lynx Smart BMS is connected to a GX device, DVCC compatible chargers that are connected to the same GX device will be turned off as well.
It should be pretty straightforward provided you configure it properly and have both the Lynx and the MPPT connected to the Cerbo with DVCC enabled.
Unfortunately the ground/rods situation is a bit of a mess, and as noted, I will need to do some clean up to get to your link#7 ideal (which I have read several times-very helpful). The original Outback install included separate ground buses, wires AND rods on the AC side AND the DC side (ie separate grounding rods placed for AC and DC at the inverter shed location). These in addition to the main AC panel ground system/rods at the cabin itself. I think this was common at the time and within Outback specs. This will need to be simplified eventually tying everything together at a single ground rod site (likely with the main panel at the cabin). I am double checking everything and drawing out a wiring diagram to make sure I have everything accounted for. I don't want to leave something ungrounded or with undersized ground wiring. The one place the original installer (2007) did not place extraneous ground rods was at the solar panel frames, instead taking the frames' ground wire along with the PV out lines 150 ft and tying it into the DC neg ground at the outback DC panel at the inverter/battery shed. To make matters more complicated now the installer of the new solar panels this summer (2024) insisted on adding yet an additional ground rod at the solar panels 'cus that's how he does it. I even tried to invoke Mike Holt, but it was easier to just let the installer proceed with the new ground rod than argue, and disconnecting that rod at least will be straightforward. It just goes to show how confused this whole issue is even in 2024 and even for professional installers.