Overkill Solar - Wrong BMS Size for my system?

monoxyde

New Member
Joined
Jun 2, 2021
Messages
26
The overkill 8s bms is only rated for 100 amps continuous.
You can't expect to run 150 amps continuous through it.
I understand that, however I've built my system for 150 amp capacity.

With my usage, I don't think I'm going to hit 150 AMP, but I may touch 100 amp, so may have some issues. It's understood.

Now, new question.

I'm looking at DALY 200/250 A systems on Amazon. I see they come with 2 AWG cable.... is it easy enough to upgrade that to 1/0 AWG?

Is there another BMS that is recommended besides Daly?
 
Joined
Nov 30, 2019
Messages
12,462
I understand that, however I've built my system for 150 amp capacity.
You have built your system for <=100 amps continuous.
I would estimate that the bms over-current protection will trip PDQ at ~125 amps.
The bms is the bottleneck.
With my usage, I don't think I'm going to hit 150 AMP, but I may touch 100 amp, so may have some issues. It's understood.

Now, new question.

I'm looking at DALY 200/250 A systems on Amazon. I see they come with 2 AWG cable.... is it easy enough to upgrade that to 1/0 AWG?

Is there another BMS that is recommended besides Daly?
Not easy.
You would have to source or make those connectors.
The 2 awg cable on the bms likely has silicone insulation, probably rated for 200C so its ampacity rating would be considerably higher than for 2 awg welding cable with 105C insulation.
 

acdoctor

Solar Addict
Joined
Oct 5, 2020
Messages
660
Location
Central Arkansas
I am running 4S2p with two overkill 120 bms so far working great. I monitor every cell and have 4 temp sensors. 24 volt 240 amps that is 2800 watts down at LVD.
 

monoxyde

New Member
Joined
Jun 2, 2021
Messages
26
Still a build in process.

200/250 AMP BMS should arrive on Friday.


Waiting on BMS to arrive Friday.

Battery <-> BMS <-> Negative Bus Bar <-> Growatt

Hopefully this will give you some idea of what I'm doing. I'm not claiming I know what to do, but it's been a slow process, just doing one thing at a time.
 
Joined
Nov 30, 2019
Messages
12,462
@smoothJoey I guess I forgot to describe the positive side of things.

Battery Positive <-> 250 Amp Breaker <-> Battery Disconnect with @FilterGuy 's pre-charge design( https://diysolarforum.com/resources/inverter-disconnect-switch-with-precharge.60/ ) <-> Growatt
That breaker looks like a knockoff.
If you want a breaker for the Armageddon position I suggest this one.
 

monoxyde

New Member
Joined
Jun 2, 2021
Messages
26
That breaker looks like a knockoff.
If you want a breaker for the Armageddon position I suggest this one.
I just read the reviews, good catch!


I may just do an ANL fuse in the mean time, and add a breaker at a later date. I'd prefer a breaker over fuse, because if I'm out in the middle of nowhere and don't have extra ones I can just flip it back on... I don't know, I'm not the electrician here.

Fuse or breaker? I know it's mostly for Armageddon purposes like you stated.
 
Joined
Nov 30, 2019
Messages
12,462
I just read the reviews, good catch!


I may just do an ANL fuse in the mean time, and add a breaker at a later date. I'd prefer a breaker over fuse, because if I'm out in the middle of nowhere and don't have extra ones I can just flip it back on... I don't know, I'm not the electrician here.

Fuse or breaker? I know it's mostly for Armageddon purposes like you stated.
An ANL fuse has an arc interrupting capacity rating of <10,000 amps.
For the fuse/breaker closest to a 24volt or greater LFP battery prevailing wisdom suggests a fuse with minimum 20,000 amps AIC.
Also I've heard reports that when those ANL fuses blow under high current the tend to create shrapnel.
 