B BartonB New Member Joined Oct 5, 2023 Messages 108 Location Jorden Sep 14, 2024 #1 2 server rack batteries 200A 24V connected in parallel The app shows that the designed capacity is 200ah The sticker on the battery says 5120Wh (each one) Am I missing something?
2 server rack batteries 200A 24V connected in parallel The app shows that the designed capacity is 200ah The sticker on the battery says 5120Wh (each one) Am I missing something?
sunshine_eggo Victron's little biatch Joined Oct 26, 2021 Messages 23,347 Location Honey Badger Ranch (HBR), USA (6500' in ENE AZ) Sep 14, 2024 #2 200Ah * 25.6V = 5120Wh
B BartonB New Member Joined Oct 5, 2023 Messages 108 Location Jorden Sep 14, 2024 #3 sunshine_eggo said: 200Ah * 25.6V = 5120Wh Click to expand... Yes that's correct I connected two batteries, each one 5120wh So the designed capacity should show 400ah, no?
sunshine_eggo said: 200Ah * 25.6V = 5120Wh Click to expand... Yes that's correct I connected two batteries, each one 5120wh So the designed capacity should show 400ah, no?
4 400bird Solar Wizard Joined May 23, 2020 Messages 4,378 Location California Sep 14, 2024 #4 But each BMS still only sees/is connected to 200Ah.
B BartonB New Member Joined Oct 5, 2023 Messages 108 Location Jorden Sep 14, 2024 #5 400bird said: But each BMS still only sees/is connected to 200Ah. Click to expand... When you connect them in parallel with com, only the master BMS works... So I assumed it will show the total capacity?
400bird said: But each BMS still only sees/is connected to 200Ah. Click to expand... When you connect them in parallel with com, only the master BMS works... So I assumed it will show the total capacity?