Hi!

I am a newbie here and have 8 260amp LifePo4 cells (WB-LYP260AH) Series connected them to make a 24v battery and have been using with my All-in-one MPP Solar 2424LV-MSD. Works great.

Recently I purchased 4 280amp EVE cells and intend to buy 4 more. My question is:

Once bought 4 more 280amp EVE cells, can I series connect them to make a 24v and then parallel connect them with my 260amp 24v battery to use with my PIP?

What would you do if you were in my shoes?
Thanks
 

Attachments

  • 1BF05A46-D8F2-4580-9B66-761478B1B38F.jpeg
    1BF05A46-D8F2-4580-9B66-761478B1B38F.jpeg
    92.5 KB · Views: 7
  • 94D00603-98AC-4D0B-BB85-B62CA3B74D7C.jpeg
    94D00603-98AC-4D0B-BB85-B62CA3B74D7C.jpeg
    74 KB · Views: 6
  • EFD02DC3-64A8-47A2-8A85-B231CF66E0EB.jpeg
    EFD02DC3-64A8-47A2-8A85-B231CF66E0EB.jpeg
    72.7 KB · Views: 6
  • B915A380-7BEA-4C00-850E-EE0ACF07E638.png
    B915A380-7BEA-4C00-850E-EE0ACF07E638.png
    362.2 KB · Views: 7
  • 5D6F5EC5-AB7D-4CFE-8B3D-80359232EEA4.jpeg
    5D6F5EC5-AB7D-4CFE-8B3D-80359232EEA4.jpeg
    47.7 KB · Views: 7
Thank you for your prompt response.
Yes, I have a 80 amp BMS that I am planning to use once I purchased the next four cells.
Which brings me to the next question. Prior to parallel connect the two battery packs Do I have to parallel connect all 16 cells to balance or parallel connecting 8 similar cells with the same amperage separately?
 
I'm not following?
Why would you parallel the 16 cells? Are you top balancing prior to building the battery?
 
Yes I was thinking to top balance the cells but I am not sure how to do this whether I should connect ALL 16 cells in parallel or put together the same 8 EVE cells top balance them and similarly put together the other 8 group of cells and top balance them.
 
Top Balance your 260AH cells and build them into a pack with BMS & Fused and do the same for the EVE-280's. Make sure that when you wire them in parallel you use the same lengths of Battery Cables to the busbar from each battery pack. The AH difference between the 260 & 280 won't present any problems when charging or discharging.

BMS Note:
Each battery pack should have it's own 8S BMS and be fused as well.
Each pack should be able to handle the full Discharge & Charge potential of your system, so the BMS' should be sized accordingly for Amperage Handling.
When choosing a BMS, it is highly recommended to ensure it has the capacity + room to spare. For FET Based BMS, generally 25% above your max load is suggested. So if you are going to pull 100A go for 125 or better 150A. Also typically FET based BMS only take 50% for Charge Input handling. BMS' which use Relays/Contactors rely on those for the rating capacity handling most often in systems that use 250A and higher.

Hope it helps, Good Luck.
Steve
 