Greendream
Off-grid Beginner
Yeah I figured they were out of balance, is there any other way to balance them? I actually haven't tried doing the LVCO, I think its set on my inverter to 42, maybe I'll try to increase that?
Set your charger to 50.8V bulk, absorb and float and set LVCO for 44.8V. Make sure you're not charging with more than 50A per battery. That is what was recommended to me by BB. You can try floating lower. If the cells are out of balance the BMS balancing is very slow and floating at 48.7 wont be in range for BMS to balance.
From the specs online -
Charging Voltage Range: | 48.7 - 50.75 |
48V LLAMA - LiFePO4-115Ah-5.3kWh - BigBattery.com
The 48V LAMA from BigBattery is a slim and powerful battery requiring zero maintenance and can power your home or solar system with no problem. Get yours today! LiFePO4-115Ah-5.3kWh Battery
bigbattery.com