Mind clearing something up for me? Wouldn't the voltage need to be over a certain point, AND the current to drop for the 100% to be synced?
Yes. That's how it works. Voltage over the charged value. Current under the tail current % for the set time period (3 min by default).
Wouldn't this avoid the false sync to 100% when the current drops due to low solar only?
Default config is 0.2-0.3V below FLOAT.
For solar charging, you use ABSORPTION. When variable solar drops below tail current when the battery is not nearly fully charged, voltage will typically drop below the "charged" voltage and avoid false sync.
10. Troubleshooting
www.victronenergy.com
See 10.3.11.
It is also possible that the battery monitor synchronises too early. This can happen in solar systems or in systems that have fluctuating charge currents. If this is the case change the following settings:
- Increase the “charged voltage" to slightly below the absorption charge voltage. For example: 14.2V in case of 14.4V absorption voltage (for a 12V battery).
- Increase the “charged detection time” and/or decrease the "tail current" to prevent an early reset due to passing clouds.