I am looking to connect a off grid solar system to the house electrical system. I have a 24V 1200VA Victron inverter i would like to feed a manual transfer switch via 50 amp plug via breaker / disconnect box. The transfer switch passes the inverter / generator neutral to the neutral on the load center where the ground is bonded to the neutral. I have done a bunch of research and it looks like this will work but I have some wierd voltages from the inverter. With the inverter NOT connected to the house electrical system and with or without the chassis ground on the inverter to a ground rod (Earth ground). The inverter Hot to ground and neutral to ground off the inverter A/C outlet has 60 Volts A/C. Hot to neutral has 120 volts. I checked the inverter and the neutral is NOT bonded to the A/C Ground but the A/C Ground IS bonded to the chassis ground.
Question 1 - Will this inverter 24V 1200VA Victron work in this design?
Question 2 - The Inverter having 60 volts from Hot to ground and Neutral to Ground normal and will this change when the inverter neutral and ground is bonded in the load center?
Question 1 - Will this inverter 24V 1200VA Victron work in this design?
Question 2 - The Inverter having 60 volts from Hot to ground and Neutral to Ground normal and will this change when the inverter neutral and ground is bonded in the load center?