I posted this question elsewhere but trying here since I've gotten no response yet. Attached is a drawing of my overall proposed layout.
The other two panels each have their own main breakers (one is 200A ITE, the other is a 150A breaker feeding another 200a ITE panel). Each panel will be backfed from the inverters via a new output panel into a backfeed breaker (with interlock kit) or a manual transfer switch (MTS).
My inverters (EG4 12000XP’s) maintain a continuous neutral between AC input and output but do not create a neutral-ground bond, so they must be set to floating mode since my main panel already has a neutral-ground bond. All subpanels have isolated neutrals.
The question is about whether I must run a dedicated neutral from the inverter output panel to each panel’s backfeed breaker and manual transfer switch—especially given that all panels share the same house neutral bus anyway. If I do run new neutrals, will this possibly create parallel neutral paths?
Additionally, a video discussing this same issue (YouTube link) explains why running two neutrals is unnecessary and can lead to grounding and troubleshooting issues. The person in the video emphasizes that the backfed panel already has a neutral from the main service, so running another neutral from the inverter output panel is redundant and potentially problematic.
Thanks.
Summary of My Setup and Question
I have a home with two separate 200A services that are spliced in a wire trough to feed three main panels. I’m repurposing one Siemens 200A panel as a sort of “splitter”, removing its branch breakers and installing only three breakers (100A, 100A, 125A) in their place to feed two inverters and a new subpanel. The new subpanel will hold the original branch circuits.The other two panels each have their own main breakers (one is 200A ITE, the other is a 150A breaker feeding another 200a ITE panel). Each panel will be backfed from the inverters via a new output panel into a backfeed breaker (with interlock kit) or a manual transfer switch (MTS).
My inverters (EG4 12000XP’s) maintain a continuous neutral between AC input and output but do not create a neutral-ground bond, so they must be set to floating mode since my main panel already has a neutral-ground bond. All subpanels have isolated neutrals.
The question is about whether I must run a dedicated neutral from the inverter output panel to each panel’s backfeed breaker and manual transfer switch—especially given that all panels share the same house neutral bus anyway. If I do run new neutrals, will this possibly create parallel neutral paths?
Avoiding the Parallel Neutral Issue
I found a discussion here (link here) where someone warns against running two neutrals—one from the main panel to the inverter input and another from the inverter output panel to the backfed panel. The concern is that this would create parallel neutral paths, which violates NEC 310.10(H) and can cause unexpected current flow, but I have separately red that 300.3(B) & 310.10(H) require all conductors of a circuit be in the same cable/conduit to avoid inductive heating.Additionally, a video discussing this same issue (YouTube link) explains why running two neutrals is unnecessary and can lead to grounding and troubleshooting issues. The person in the video emphasizes that the backfed panel already has a neutral from the main service, so running another neutral from the inverter output panel is redundant and potentially problematic.
Final Questions
Given this setup, do I need to run a neutral from the inverter output panel to each backfeed breaker and the manual transfer switch, or is the existing shared neutral sufficient? If I do run new neutrals, would this cause parallel neutral paths, and is there any scenario where running an extra neutral is actually needed? When I am moving the branch breakers to the subpanel, can I tie the original and new panels' neutral bus bars together with a single thicker gauge wire and only move the hot L1 and L2 lines?Thanks.