ANL fuses run to hot - they are from car audio - anything from car audio should be kept there. They also have a very low AIC compared to the class T or MRBF even.
The ANL has an AIC around 5000amps the MRBF is good to 10,000 amps. The class T is good to 20,000amps. Because of the extremely low internal impedance of the LFP batteries they can put out 7000amps in the event of a BMS failure in a dead short.
If your fuse AIC doesn't exceed the possible arc size when the fuse blows it will just arc across it and continue to pass current until the casing burns away and the cable ends come apart.
So you do need MRBF on each battery post and you do need a
ANL fuses run to hot - they are from car audio - anything from car audio should be kept there. They also have a very low AIC compared to the class T or MRBF even.
The ANL has an AIC around 5000amps the MRBF is good to 10,000 amps. The class T is good to 20,000amps. Because of the extremely low internal impedance of the LFP batteries they can put out 7000amps in the event of a BMS failure in a dead short.
If your fuse AIC doesn't exceed the possible arc size when the fuse blows it will just arc across it and continue to pass current until the casing burns away and the cable ends come apart.
So you do need MRBF on each battery post and you do need a class T on the main line between the bus bar and the inverter.
The size of the MRBF on the battery post would depend on the max current output of the BMS. If it is a 100amp BMS you would put 125amp fuses. If it is 200 amps 250amp fuses... i.e. max BMS current * 1.25 = fuse size.
The line from your charger to the bus bar should be a 50 amp fuse - Fuses protect wires they don't protect equipment.
Here is why you fuse all the batteries - If one cell in a battery fails and shorts that battery will have lower voltage and the other batteries will dump max current into the shorted battery. That current is enough to blow the BMS into a short and get even more current. The time involved for all of this to happen is under a second. If you have fuses that means the one on the shorted battery will fail and current will cut off from it and the other two will keep working.
If your cable runs between battery and bus bar are more than 7 inches long I would think about fusing the bus bar end as well.... I say think because you need to make certain that where the cables are install nothing can ever drop on them or rub or have a chance to short them out.
I've done the math in the past, you can dig it up if you want. It was 4 parallel 12v batteries with 100amp BMS. But the deal is that if you have a 2ft cable run and something shorts from the middle of that cable to the negative it can flash from 24c to 200c in under a second. 300amps coming down the cable to the short point and 100 amps coming up the cable to the short point. Assuming the shorting item/wrench/etc survives the inital flash and is welded into place it takes under a minute for a box end wrench to melt and be molten steel flying all over.
Have a look at this thread (I know it is long, will summarize
So, after 4 to 5 years of working flawless, the 100 kwh lifepo4 battery caught fire at night and burned our house down. Luckily our family just made in out on time.
Inspection of the fire expert revealed that a melt fuse melted, and created an arc between the 2 points wich ultimatly started the fire.
So i learned to not use melt fuse anymore, plus once the house is rebuild, i will put the new system in a seperate shed outdoor.
The summary is the guy had 1 cell short in one of 7 parallel battery banks. All of the banks had fuses to a bus bar and there was a shunt trip on the other side of the bus bar. The chain of events was a shorted cell vented, this filled the room with hydrogen gas and some other nasties, the Mega fuse he had protecting that battery exploded into a shower of sparks (there are youtube videos showing that), and the hydrogen ignited. That would have caused other cells to vent and add fuel... Bad chain of events and several things were uncovered looking at his build thread and pictures... He did everything right at the time he built the system.. the things uncovered are things that changed after the fact and he didn't update.
Part of it was to do with DIY batteries and part was to do with the design.
on the main line between the bus bar and the inverter.
The size of the MRBF on the battery post would depend on the max current output of the BMS. If it is a 100amp BMS you would put 125amp fuses. If it is 200 amps 250amp fuses... i.e. max BMS current * 1.25 = fuse size.
The line from your charger to the bus bar should be a 50 amp fuse - Fuses protect wires they don't protect equipment.
Here is why you fuse all the batteries - If one cell in a battery fails and shorts that battery will have lower voltage and the other batteries will dump max current into the shorted battery. That current is enough to blow the BMS into a short and get even more current. The time involved for all of this to happen is under a second. If you have fuses that means the one on the shorted battery will fail and current will cut off from it and the other two will keep working.
If your cable runs between battery and bus bar are more than 7 inches long I would think about fusing the bus bar end as well.... I say think because you need to make certain that where the cables are install nothing can ever drop on them or rub or have a chance to short them out.
I've done the math in the past, you can dig it up if you want. It was 4 parallel 12v batteries with 100amp BMS. But the deal is that if you have a 2ft cable run and something shorts from the middle of that cable to the negative it can flash from 24c to 200c in under a second. 300amps coming down the cable to the short point and 100 amps coming up the cable to the short point. Assuming the shorting item/wrench/etc survives the inital flash and is welded into place it takes under a minute for a box end wrench to melt and be molten steel flying all over.
Have a look at this thread (I know it is long, will summarize
So, after 4 to 5 years of working flawless, the 100 kwh lifepo4 battery caught fire at night and burned our house down. Luckily our family just made in out on time.
Inspection of the fire expert revealed that a melt fuse melted, and created an arc between the 2 points wich ultimatly started the fire.
So i learned to not use melt fuse anymore, plus once the house is rebuild, i will put the new system in a seperate shed outdoor.
The summary is the guy had 1 cell short in one of 7 parallel battery banks. All of the banks had fuses to a bus bar and there was a shunt trip on the other side of the bus bar. The chain of events was a shorted cell vented, this filled the room with hydrogen gas and some other nasties, the Mega fuse he had protecting that battery exploded into a shower of sparks (there are youtube videos showing that), and the hydrogen ignited. That would have caused other cells to vent and add fuel... Bad chain of events and several things were uncovered looking at his build thread and pictures... He did everything right at the time he built the system.. the things uncovered are things that changed after the fact and he didn't update.
Part of it was to do with DIY batteries and part was to do with the design.