Please check my design.

Brewman

Solar Enthusiast
Joined
May 16, 2020
Messages
511
I have labeled all the wire sizes. Please look it over and see if I have it all correct.

24V system schematic V2.jpg
 
I will be adding it soon, right now I just want to make sure the wire gauge is correct.
The symbol abstraction is a pain for me.
I have to look at the wire and then refer to the legend.
Just saying.
 
I would use the 125 amp battery fuse as the disconnect unless you have a reason to disconnect frequently. Can add the switch later if removing the fuse becomes a PITN. I prefer to not add additional connections and resistance in the inverter power loop.

The 50 amp breaker to the controller is a bit redundant since the wire is the same as the main battery cable fused at 125. Or could use smaller wire assuming the distance is short from controller to bus.

I don't think the circuit breaker is needed between the solar and controller. Usually not needed unless 3 strings or higher voltage. Does make a convenient switch. 60 volts is getting up high enough you may not want to just remove a wire for service.

I am not sure what that battery connection is off the transfer switch.

Wire seems light to the 12v fuse block. How many amps does the 24-12 converter supply?
 
I have labeled all the wire sizes. Please look it over and see if I have it all correct.
Insufficient information... for example if the panels are 1V @ 250 amps a 40 amp breaker won't cut it ;-)

But let's assume 30V and 8.2 amps with a local minimum temperature of -25°C and an Isc Temperature Coefficient of 0.04 %/°C. Then with 2P that's 16.4 amps at +25°C, and 16.8 amps at -25°C ( peer approved example math, don't trust any calculations I do ;-). If the code says you have to upsize by 25% that's an ampacity of 21 amps.

Not all copper wire is equal in terms of ampacity. If it's a ground mount and you're using 60°C copper wire (e.g., UF-B) then you'd want gauge 10. But, if you're using 90°C Copper (e.g., THWN-2) then 14 gauge might do. Is it on a hot roof? In a conduit? Hot wires have more resistance and you might have to compensate with a lower gauge.

That's why we have the write-up: What wire gauge should I use? (video). The video is really really good, I definitely recommend it.

The symbol abstraction is a pain for me.
Amen! ;-)
 
Last edited:
The inverter is 2000W @ 24V, so a normal draw of up to 84 amps. But if it surges to 3000W for 5s that would be 125 amps and 5 seconds might put some serious heat on the wire. I'd look up the manufacturer's recommendations. Also, wire quality makes a big difference, in looking at 3 categories of wire AWG 4 might handle 70 amps, 85 amps, or 95 amps.
 
My chart says 160 amps for #4 105c insulation unbundled and not enclosed in conduit. I agree #2 would be better unless the length is fairly short.
 
Panel info
  • Rated Power: 250W
  • Open circuit voltage (VOC): 37.6 V
  • Max power voltage (VMP): 30.3 V
  • Short circuit current (ISC): 8.85 A
  • Max power current: 8.27 A
  • Power Tolerance 0/+3%
  • Maximum system voltage: 600V (UL)
  • Fuse Rating: 15 A
Converter is 40AIMG_20210717_205040894.jpg
IMG_20210717_210740575.jpg
 
Last edited:
Two comments. I am doing a similar build but went with a Victron 3000va. It includes the charger and ATS function. What I am wondering about, I think in my case the shore power goes to the inverter and then to the AC distribution. On your diagram, I don't see a path from the inverter to AC distribution.

Someone asked about the DC>DC converter wire gauge. I planned for the wire to be 8ga, but the wire coming from the converter is only 12ga and it is rated at 40a. How can the converter rated for 40A out use 12ga wires?
 
I think you’re good to go brewman as long as the fuse block connected to that converter pulls less than 50 amps at 12v which is roughly 25amps @ 24v that fuse of yours shouldn't pop. Oh, also as long as your converter can handle an output of up to 12v at 50 amps and just in case you do pull 50 amps at 12vdc I hope it does pop because 12 wag will not handle 50 amps at 12vdc (I checked on that ampacity link posted above by svetz :)
 
Two comments. I am doing a similar build but went with a Victron 3000va. It includes the charger and ATS function. What I am wondering about, I think in my case the shore power goes to the inverter and then to the AC distribution. On your diagram, I don't see a path from the inverter to AC distribution.

Someone asked about the DC>DC converter wire gauge. I planned for the wire to be 8ga, but the wire coming from the converter is only 12ga and it is rated at 40a. How can the converter rated for 40A out use 12ga wires?
Yeah 40a and 12ga doesn’t sound like a good idea. I’d go 30a max and that’s with a good thhn wire.
 
Since you are using thhn...
I suggest you get 4 awg, 6 awg and 12 awg.
4 awg is easy to work with and big enough for the critical path.
6 awg is even easier work with.
12 awg is trivial.

The nice thing about thhn is its relatively cheap.
I prefer to get white, then use red, black and green electrical tape to identify the wires.
 