Crashcourse
- Nov 1, 2020
- 31
Good day folks! I think my math is correct and I’m hoping this will work.
I have 12 x 12V 100W Panels:
Maximum Power (Pmax): 100W
Maximum System Voltage: 700 DC
Maximum Power Voltage (Vmp): 18V
Open Circuit Voltage: 21.6V
Maximum Power Current (Imp): 5.55A
Short Circuit Current: 6.06A
And a 60A MPPT Charge Controller:
MPPT P60:
12V:open circuit voltage ≤48V(Voc) maximum. PV input power:780W
24V:Open circuit voltage ≤100V(Voc) maximum.PV input power:1560W
Automatic identification of 12V/24V system voltage
Rated charging/discharging current:60A
Maximum open circuit voltage solar panel (Voc):18V-48V(12V)/36V-96V(24V)
Power terminal:10 AWG
And a 4 string PV combiner.
What I would like to do is wire 4 sets of 3 panels in series (those 4 sets would be paralleled in the combiner, obviously) which I believe would give the Charge Controller ~54 volts at ~22 amps. The Charge Controller should then give my 24 volt battery bank (6 x 105Ah 12 Volt deep cycle LAs wired 2s3p) ~28 volts at ~44 amps, right?
Am I right about this and will it work without issues?
Thank you.
MPPT P60:
Thank you.