200A fuse for 2ga wire less than 5 ft works well.what are your thoughts on my post above
200A fuse for 2ga wire less than 5 ft works well.what are your thoughts on my post above
btw , how did you determine how much your battery can discharge? i have a 12v 280ah DIY , i believe the discharge rate is .5c , my bms is 120a200A fuse for 2ga wire less than 5 ft works well.
i only use my microwave when my generator is on and have no need to connect it to the inverter , i hardly use itThe BMS determines the discharge rate. So yours is 120A. So you really don't need wire and fuses for 200A. I would still use 2ga wire and a 200A fuse, though. My SOK BMS says it is 100A / battery and I have pulled 115A for 10 minutes from it when I had the microwave and residential refrigerator running at the same time.
120A @ 12V is 1,440W. That should be plenty to operate your 1000W inverter and some other basic DC loads. Are you planning to run the microwave off the inverter?
I used these https://www.amazon.com/gp/product/B07DN8KMTC/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1
I would not rely on the BMS shuntfor accuracy, but that's just me. I prefer just looking at the shunt display at any time mounted on the wall.@smoothJoey
why does everyone buy a shunt? i have an app i can use on my phone to monitor the overkill solar bms , is that not sufficient?
im looking at the link now , but i was asking bc i dont understand where the main positive will lead off , all 4 posts look the same , so it doesnt matter which one i lead to the class t fuse ?I used these https://www.amazon.com/gp/product/B07DN8KMTC/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1
Go heavy, all connections can generate resistance and heat. These are heavy.
All the posts are the same, so attach main battery line anywhere. And then attach all the loads anywhere. Try not to stack a lot of wire lugs on a single post.im looking at the link now , but i was asking bc i dont understand where the main positive will lead off , all 4 posts look the same , so it doesnt matter which one i lead to the class t fuse ?
i use the busbar to attach all positive lines , but then what about the line from busbar to the class t or battery? thanks
ok i just added the victron bmv 712I would not rely on the BMS shuntfor accuracy, but that's just me. I prefer just looking at the shunt display at any time mounted on the wall.
If your BMS does current accounting then the shunt is functionally redundant.@smoothJoey
why does everyone buy a shunt? i have an app i can use on my phone to monitor the overkill solar bms , is that not sufficient?
2021-09-28 06:58:03 Low=3.390V Average=3.410V High=3.428V Delta=0.038V Balance=01010001 Cell=26.5C Ambient=24.9C SOC=166.2AH Rate=12.0A boost 05:57:57
2021-09-28 06:58:09 Low=3.381V Average=3.399V High=3.417V Delta=0.036V Balance=00000000 Cell=26.5C Ambient=24.9C SOC=166.2AH Rate=0.0A float 00:00:06
--
2021-09-29 06:59:30 Low=3.389V Average=3.410V High=3.427V Delta=0.038V Balance=10100000 Cell=25.8C Ambient=24.3C SOC=164.3AH Rate=11.8A boost 05:59:23
2021-09-29 06:59:36 Low=3.381V Average=3.398V High=3.415V Delta=0.034V Balance=00000000 Cell=25.8C Ambient=24.3C SOC=164.4AH Rate=0.0A float 00:00:06
--
2021-09-30 06:35:03 Low=3.390V Average=3.410V High=3.427V Delta=0.037V Balance=10100000 Cell=26.0C Ambient=24.2C SOC=162.7AH Rate=12.0A boost 05:34:56
2021-09-30 06:35:09 Low=3.381V Average=3.399V High=3.416V Delta=0.035V Balance=00000000 Cell=26.0C Ambient=24.2C SOC=162.7AH Rate=0.0A float 00:00:06
--
2021-10-01 06:44:30 Low=3.390V Average=3.409V High=3.426V Delta=0.036V Balance=10100000 Cell=25.8C Ambient=24.2C SOC=161.1AH Rate=12.0A boost 05:44:24
2021-10-01 06:44:36 Low=3.381V Average=3.399V High=3.416V Delta=0.035V Balance=00000000 Cell=25.8C Ambient=24.2C SOC=161.1AH Rate=0.0A float 00:00:06
--
2021-10-02 06:51:26 Low=3.389V Average=3.410V High=3.427V Delta=0.038V Balance=01010001 Cell=26.2C Ambient=25.1C SOC=159.8AH Rate=12.0A boost 05:51:20
2021-10-02 06:51:32 Low=3.381V Average=3.398V High=3.416V Delta=0.035V Balance=00000000 Cell=26.3C Ambient=25.1C SOC=159.8AH Rate=0.0A float 00:00:06
--
2021-10-03 06:42:33 Low=3.390V Average=3.411V High=3.429V Delta=0.039V Balance=01010001 Cell=27.2C Ambient=25.7C SOC=158.8AH Rate=12.0A boost 05:42:27
2021-10-03 06:42:39 Low=3.382V Average=3.400V High=3.417V Delta=0.035V Balance=00000000 Cell=27.2C Ambient=25.7C SOC=158.8AH Rate=0.0A float 00:00:06
--
2021-10-04 06:32:39 Low=3.389V Average=3.410V High=3.429V Delta=0.040V Balance=10100000 Cell=27.3C Ambient=26.0C SOC=157.0AH Rate=12.0A boost 05:32:33
2021-10-04 06:32:45 Low=3.382V Average=3.399V High=3.418V Delta=0.036V Balance=00000000 Cell=27.3C Ambient=26.0C SOC=157.0AH Rate=0.0A float 00:00:06
--
2021-10-05 06:34:36 Low=3.389V Average=3.410V High=3.428V Delta=0.039V Balance=01010001 Cell=26.7C Ambient=25.3C SOC=155.2AH Rate=12.0A boost 05:34:30
2021-10-05 06:34:42 Low=3.382V Average=3.399V High=3.417V Delta=0.035V Balance=00000000 Cell=26.7C Ambient=25.3C SOC=155.2AH Rate=0.0A float 00:00:06
Based on the calculations in post #5 you only need a 125A Class T fuse given that you have a 1000W inverter. 200A is the max fuse size for 2AWG but that doesn't mean you need to use the max size fuse. And if you later decided to get a bigger inverter (say 2000W) then neither the 2AWG nor the 200A fuse will be big enough so going with the larger wire and larger fuse gains you nothing. It's fine to use the 2AWG wire if that's what you have but it doesn't really provide any useful upgrade path.if i use 2 awg wire from positive bus bar to class t fuse , max amps for 2 guage wire is 205a ,
so ill use a 200amp class t fuse
Battery cable from ANL fuse can go to any terminal, it just depends on what other circuits you need to run and how you will have to route them.im looking at the link now , but i was asking bc i dont understand where the main positive will lead off , all 4 posts look the same , so it doesnt matter which one i lead to the class t fuse ?
i use the busbar to attach all positive lines , but then what about the line from busbar to the class t or battery? thanks
Based on my previously stated strategy....
got it , ok i got a 62a breaker that is good for 400 volts , the 16a breaker from the panels to the SCC is also good for 400 voltsAs I stated in post #22, the wire and breaker between the SCC and the bus bar needs to account for the SCC outputting up to 50A to the battery. So that means 6AWG wire and a 65A or 70A breaker.
copy will add to diagramThe shunt for the BMV-712 goes between the battery negative terminal and the negative bus bar.
this is what came with the device so i just checked the manual to see what it was and added itYour inverter fuse should be 125A, not 110A. 110A would work but if you ever actually put a 1000W load on the inverter you might pop the fuse since it is really close to the max load.