Hey all,

With the recent increase in regulatory control of solar, why is there not more people talking about and covering “just plug it in” 110V solar? This is quite common in Germany. But the amount of FUD around back-feeding / permits / regulation is simply astounding, especially when the inverter in question is UL 1741 / CA Rule 21.


Probably going to set up a solar pergola with these transparent panels

And this inverter. I think it will be “over paneled” by quite a bit if I just use one inverter, but there is no real issues with that, right? I like the light pass through properties of the 460W panels.
 
With the recent increase in regulatory control of solar, why is there not more people talking about and covering “just plug it in” 110V solar? This is quite common in Germany. But the amount of FUD around back-feeding / permits / regulation is simply astounding, especially when the inverter in question is UL 1741 / CA Rule 21.
Huh? It’s very well explained on numerous threads

NEC requires you to use a dedicated circuit for the inverter. Most cases of plugging in to a receptacle don’t meet that, and indeed a circuit will be allowed to have sections of the wiring in excess of that allowed by breaker.

You are required to get an interconnection agreement with all POCOs in California.

UL1741/Rule21 does not address spurious exports. In fact the CPUC recently allowed POCOs to increase the datapoint time resolution on smart meters, which makes it easier to detect unapproved backfeed.

And EG4 has posted language warning against using zero export to escape interconnection agreement

I personally think the U.S. should support this, it’s not like physics are super different over here other than double the current from being on 120V for the same power size.
 
There’s even replies on that video explaining the reasoning in detail. Take a look at the one from this user

1731261709284.png

I guess making this more complicated is that people play fast and loose with what they mean by backfeed/export

UL1741 interactive basically just means it won’t energize the output when the grid is down or you unplug things. While you also need the right zero export behavior to avoid being detected by a high resolution smart meter

Also if this type of device was going to become legal in the US, they probably need to adjust the parameters to avoid energizing the plug. Since you are not using an inlet receptacle the plug will have exposed 120V in the latency the interactive inverter is allowed to leave the output on

Rule21 compliance is kind of laughable to claim bc the illegal interconnection is no longer compliant with the sections saying this type of inverter has to be approved in that way, for your specific site
 
All right I’ll give constructive way to improve the project. You should change to using a dedicated 240V circuit with inlet receptacle. That will likely increase your safety (by virtue of hiding the energized prongs) and allow you to use much better tested / broadly adopted inverters.

(Another issue is that there is likely no GFCI on this path. Certainly not from the panel breaker side since American GFCI breakers cannot be used for backfeed).
 
Because utility does not want you to have solar. So they create a ton of red tape to make it expensive to grid tie. In Germany they decided that the risk is too low to prohibit this.
 
Please don’t be like the other FUD-sters and assume I didn’t read the comments and also do research.

The 110V is on a dedicated circuit (de commissioned sprinkler circuit) and also house is approved for back feed / has bi directional meter.

Here in the real world, people do sketchy things with 110V generators, most home work is unpermitted, and heck in my area many homes have illegal unpermitted septic tanks. I think it’s cute how everyone is so worried about UL rated devices dealing with pretty low power outputs like it’s some sort of devil magic.
 
Because utility does not want you to have solar. So they create a ton of red tape to make it expensive to grid tie. In Germany they decided that the risk is too low to prohibit this.
Technically speaking they have lower current and probably back-feed able RCDs. And the equipment is lab tested because it is allowed

I don’t want to encourage people to do this in the US mainly because the prohibition means nobody writes standards, codes to it; and no equipment can be properly tested. Unlisted off grid inverters will likely have superior installation conditions on average to plug in porch solar, so I want the plug in porch solar to have superior design and lab vetting in advance to compensate even if I think unlisted off grid AIO are fine
 
Please don’t be like the other FUD-sters and assume I didn’t read the comments and also do research.

The 110V is on a dedicated circuit (de commissioned sprinkler circuit) and also house is approved for back feed / has bi directional meter.

Then you should have led with the research and due diligence that you put in. Your OP was stated broadly and without these important qualifications. And it definitely suggests to people to just “plug it in” without what the salient risks to think through and accept should be

You will be fine

If it is dedicated why not switch it to 240 and widen the equipment options.
 
Last edited:
Hey all,

With the recent increase in regulatory control of solar, why is there not more people talking about and covering “just plug it in” 110V solar? This is quite common in Germany. But the amount of FUD around back-feeding / permits / regulation is simply astounding, especially when the inverter in question is UL 1741 / CA Rule 21.


Probably going to set up a solar pergola with these transparent panels

And this inverter. I think it will be “over paneled” by quite a bit if I just use one inverter, but there is no real issues with that, right? I like the light pass through properties of the 460W panels.
Don't be shocked when your utility company shows up and tells you to disconnect it. You can argue until you are blue in the face about its UL listing.
 
Don't be shocked when your utility company shows up and tells you to disconnect it. You can argue until you are blue in the face about its UL listing.
OP is fine ; as I understand it they appear to have an interconnection agreement for their other solar, and this will be a blip compared to the main system

If they don’t… well then. Maybe it’s too small fry to trip the anomaly detection. But people on this forum have been detected for low amounts

I am not against agitating for this, if someone sends a petition to sign to ask for regulation change, sure.

(I’ll add that another technical difference to EU is that there is less utility transformer loading to backfeed 230V than to backfeed one phase)
 
Last edited:
You will be fine

If it is dedicated why not switch it to 240 and widen the equipment options.

Thank you, yeah I figured it would be fine (because this seems like an extraordinarily simple project, electrically speaking). Its 110V because that's what the wiring of the already de-commissioned breaker supports.

But I am more wondering: Why aren't more people talking about it?

There are definitely "zero export devices" that exist that will prevent utility levels of net metering, I believe the most new customers in the state of Hawaii relies on them now. Is there actually any law against having self consumption, Rule 21 / UL 1741 / IEE1754 inverters in a house that do not contribute to the grid?

If so, I'd love to see it. By the way, in my area, there are much more "black and white" laws about off-grid. You're not allowed to do it, so why is everyone talking about it?
 
Its 110V because that's what the wiring of the already de-commissioned breaker supports.
You can electrically swap to 220 if it is no used by any outlets / devices you haven’t found. Provided there is space for a double breaker.

Code wise it depends on the wiring method. For cables you can swap back and forth. For conductors in conduit there are labeling rules that will generally prohibit it in most cases

There are definitely "zero export devices" that exist that will prevent utility levels of net metering, I believe the most new customers in the state of Hawaii relies on them now.
I don’t know what you mean by this. I think the missing nuance is as follows.

The application zero export settings are meant for is approved interconnections where the grid will not accept any power (even at zero $0/W). It is very well tested in multiple countries and with a regulatory and approval framework it slots into

This DOES NOT mean that it is intended to hide an unapproved interconnection of an inverter outputting in parallel to grid. It is also a harder technical problem. To hide you have to zero at very fast response time to combat EG kHz rate detection sensors. While zero export approved interconnections are allowed to average over seconds timescales

In some countries like South Africa there were at least a few years of large scale cat and mouse between users of such systems and the utilities. I don’t know many of the details but I’ve seen threads on some forums about it.

Is there actually any law against having self consumption
Dunno. No lawyers have ever weighed in on a forum that I’ve been in. So the rando DIYers and engineers just have guessed that it is civil / can result in just utility company sanctions
 
This DOES NOT mean that it is intended to hide an unapproved interconnection of an inverter outputting in parallel to grid. It is also a harder technical problem. To hide you have to zero at very fast response time to combat EG kHz rate detection sensors. While zero export approved interconnections are allowed to average over seconds timescales

Thank you for the response, yes I am not implying the zero export devices hide the solars presence, but rather address the economic argument a utility would have against not having interconnect agreement, since the safety argument is already addressed by UL 1741 / Rule21. And if there are no external impacts and no law against it, I believe the risk of this is quite low.

Unless the utility just is concerned about revenue avoidance and then goes to the permitting authorities (somehow) and tries to enforce. But that's akin to the sewer company going around with a thermal camera trying to look for warm spots in the ground for unpermitted septic that leads to loss of revenue. They don't really got time for that, and even if they did, the backlash would be huge.
 
...

But I am more wondering: Why aren't more people talking about it?

...
Because it takes utility company and in some jurisdictions local/State permit approval. Even if you already have an interconnect agreement it does not mean that using this device is authorized. Heck there is many grid tie folks that are not allowed to alter their setup with out going through a lot of hoops.

It is not worth talking about.
 
Because it takes utility company and in some jurisdictions local/State permit approval. Even if you already have an interconnect agreement it does not mean that using this device is authorized. Heck there is many grid tie folks that are not allowed to alter their setup with out going through a lot of hoops.

It is not worth talking about.

As I mentioned, off grid is not allowed in many jurisdictions (including much of CA), so we shouldn't talk about it, right?
 
Thank you for the response, yes I am not implying the zero export devices hide the solars presence, but rather address the economic argument a utility would have against not having interconnect agreement, since the safety argument is already addressed by UL 1741 / Rule21. And if there are no external impacts and no law against it, I believe the risk of this is quite low.

I don't think there's a fundamental reason against it. But it will require someone to agitate for it. It took a pretty long time to get utilities on-board with grid tie solar and to build the consensus for rate payers subsidizing net metered residential systems (often installed by wealthy people, and arguably also by predatory PPA / loans). Quirks of the US compared to elsewhere - more safety risk aversion, much fewer export limits for residential except in Hawaii; export limits / infrastructure upgrades are as necessary here for utility scale as elsewhere.

I'm sure the utility will complain about leg imbalance but they can certainly math out some limits or whatever.

There's also I think a question about the ROI of this agitation. If you agitate for balcony zero export as opposed to Europe which is I believe balcony with net metering bank (but I haven't looked at it closely), the installer of those systems might only be offsetting utilization on a single circuit or a single leg. Single circuit happens if you put the zero export CT clamps at the most convenient place for plugging in, namely the plug. Then you can only zero out stuff, EG, plugged into a receptacle on the inverter or the plug (imagine a plug that has goes: Plug -> CT -> Bus of Solar output and Receptacle. Then the Zero export can cancel usage on that receptacle, but it will not know about utilization elsewhere. This might work well for an AC).

It would be better to put the CT in as upstream of a main panel or subpanel as possible. However, this substantially increases the amount of electrical work needed. Albeit mostly low voltage, and potentially you can use a wireless transmitter (but this will affect the zero export quality, so it comes with its own eng tradeoff)

If you export into a utility side bank, then none of this is necessary. But then you pull in concerns from the utility about loading the system.

I guess another reason this will be hard to do in the US, is that a lot of the grid tie stuff has been spearheaded by solar installer industry. They likely do not have a way to exploit small scale systems, so someone else will have to lobby and agitate. Not sure how to put together the coalition etc. It definitely won't be DIY solar hobbiests -- the intersection of people with expertise that are really passionate about microsolar, is not going to be that big probably. Hobbiests with expertise tend to have built their own macho, huge off-grid systems. The Sierra Club / NRDC probably aren't going to put their lobbiests on this vs other issues
Unless the utility just is concerned about revenue avoidance and then goes to the permitting authorities (somehow) and tries to enforce. But that's akin to the sewer company going around with a thermal camera trying to look for warm spots in the ground for unpermitted septic that leads to loss of revenue. They don't really got time for that, and even if they did, the backlash would be huge.
It depends on the ROI for the investigation and social dynamics. For solar, you can detect it with camera drones, those are super-super cheap to fly and then plug the pixels into some image recognition model. And social dynamics can be manipulated.

I don't think it's yet affordable to go around looking for unpermitted septics with LIDAR and IR sensing. LOL.

As I mentioned, off grid is not allowed in many jurisdictions (including much of CA), so we shouldn't talk about it, right?
Can you provide a reference for this? 1741 covers off-grid.
 
Leg imbalance is a non issue. The service is rated at full capacity for each Leg.
And the utility transformer balances anything going to the grid.
The only two issues are utility agreement and code compliance.
Code compliance is the biggest. And this type of connection doesn't meet NEC.
And I doubt that it ever will.
 
Leg imbalance is a non issue. The service is rated at full capacity for each Leg.
And the utility transformer balances anything going to the grid.
The only two issues are utility agreement and code compliance.
Code compliance is the biggest. And this type of connection doesn't meet NEC.
And I doubt that it ever will.

People love to say this, but then present zero evidence.

I spent 3 minutes researching this, and found this. So do you have any examples to cite, or just FUD?

Screenshot 2024-11-10 at 11.43.29 AM.png
 
I spent 3 minutes researching this, and found this. So do you have any examples to cite, or just FUD?
I’m not sure this says what you think it does. I read it as primary supply, not backfeed

And it is the equivalent solar clause to an old clause about feeding both legs of a panel from 120V

If you’re going to dive in the code book at least be fair and balanced and also look for stuff like the dedicated inverter circuit clause, which precludes the low hanging ways to backfeed 120V
 
Here is one such legal investigation. Any real grid defection at scale would probably need to be litigated in the courts around here.


Oof this source is a little too aggressively “seizing the means of production” for me to engage with without exerting a lot of emotional labor to power through. (EDIT: to be clear, I do like a lite version of that, but this one was a bit much)

This is certificate of occupancy. Not off grid on a property that already has a cert. I meant — example of not allowed to pull off grid permits for an existing property.

It’s probably not feasible to install enough batteries to go off grid without backup without being super uneconomical or running into Residential Code limits on max kWh

And, there is a forum member in either San Diego metro or county that is working on off grid towards a habitation cert. They just have to install enough fossil fuel standby generators to satisfy load calc. Not cheap. Probably not legal within city limits to use standby power in the Bay Area when grid is up, I know my city on the peninsula has standby power rules
 