Despite the reputation that Sol-Ark has on this forum, I feel the need to report a none to happy experience of our Sol-Ark installation.
In September 2023, we installed 3 x 15Kw, hybrid inverters, in parallel, as a 3 phase system.
We have seen varying issues, including ramping issues, to which Sol-Ark have applied a firmware increase the speed of the MPPT operation, which appears to have helped reduce the ramping.
However, we have also experienced an ongoing problem with the MPPT input voltage fluctuating, going between open circuit voltage, and less than 100V. This problem has been present since nearly day 1.
This problem only exhibits itself, when the units are in Parallel, with batteries in the system. If the system is put into grid tie mode, and the units taken out of parallel operation, with no batteries in the system, then the issue does not exhibit itself. It also does not exhibit itself, when not in parallel, and the batteries only connected to a single inverter.
It does not appear to be continuously present, and may or may not appear on restart, but does eventually, normally within 2 hours, reappear.
Sol-Ark technical support have spent considerable time with us trying to troubleshoot the problem.
We have proved that it is not related to the TIGO RSD’s, having taken them out of the MPPT 3 string, and still seeing the problem.
It also does not matter which string is connected to MPPT3 input, it is only that input that is affected. It is not, therefore string related.
Sol-Ark, having ruled out external factors, sent us a replacement inverter under warranty which they bench tested before sending out. The new inverter exhibited identical behaviour to the old one.
Sol-Ark have now advised us that they have no resolution to the problem, which they say is unique to our installation.
Our only resolution appears to be to purchase an additional inverter, and remove the 2 off MPPT3 inputs from our existing installation, and run them through the new inverter as a stand alone grid tie unit.
Quite apart from the additional cost incurred to purchase and install the additional inverter, this also removes the ability to use this PV power to gain the advantage of the hybrid functionality of the existing installation, and therefore increases the time to recover the Capital expenditure.
Despite having pointed out to Sol-Ark that the entire system was purchased and installed, based on the functionality they claim, together with their reputation, and the inverters not operating correctly, Sol-Ark are refusing to allow us to keep the good inverter we removed, to use as the 4th grid tie only inverter for the 2 off MPPT strings we need to remove from the existing 3 inverter installation.
I am not happy that they appear to be washing their hands of any responsibility for a product that does not work as claimed. We have invested nearly $200k in a system that does not work as specified, and are now expected to invest more money to put in place a work-around to cover their problem.
I am open to any feedback from forum members as to anyone who has, or are, experiencing the same issue, and any suggestions as to what might be causing this, apart from a firmware issue within the inverters themselves.
Attached is an example MPPT3 voltage graph from Solar Assistant monitoring.
In September 2023, we installed 3 x 15Kw, hybrid inverters, in parallel, as a 3 phase system.
We have seen varying issues, including ramping issues, to which Sol-Ark have applied a firmware increase the speed of the MPPT operation, which appears to have helped reduce the ramping.
However, we have also experienced an ongoing problem with the MPPT input voltage fluctuating, going between open circuit voltage, and less than 100V. This problem has been present since nearly day 1.
This problem only exhibits itself, when the units are in Parallel, with batteries in the system. If the system is put into grid tie mode, and the units taken out of parallel operation, with no batteries in the system, then the issue does not exhibit itself. It also does not exhibit itself, when not in parallel, and the batteries only connected to a single inverter.
It does not appear to be continuously present, and may or may not appear on restart, but does eventually, normally within 2 hours, reappear.
Sol-Ark technical support have spent considerable time with us trying to troubleshoot the problem.
We have proved that it is not related to the TIGO RSD’s, having taken them out of the MPPT 3 string, and still seeing the problem.
It also does not matter which string is connected to MPPT3 input, it is only that input that is affected. It is not, therefore string related.
Sol-Ark, having ruled out external factors, sent us a replacement inverter under warranty which they bench tested before sending out. The new inverter exhibited identical behaviour to the old one.
Sol-Ark have now advised us that they have no resolution to the problem, which they say is unique to our installation.
Our only resolution appears to be to purchase an additional inverter, and remove the 2 off MPPT3 inputs from our existing installation, and run them through the new inverter as a stand alone grid tie unit.
Quite apart from the additional cost incurred to purchase and install the additional inverter, this also removes the ability to use this PV power to gain the advantage of the hybrid functionality of the existing installation, and therefore increases the time to recover the Capital expenditure.
Despite having pointed out to Sol-Ark that the entire system was purchased and installed, based on the functionality they claim, together with their reputation, and the inverters not operating correctly, Sol-Ark are refusing to allow us to keep the good inverter we removed, to use as the 4th grid tie only inverter for the 2 off MPPT strings we need to remove from the existing 3 inverter installation.
I am not happy that they appear to be washing their hands of any responsibility for a product that does not work as claimed. We have invested nearly $200k in a system that does not work as specified, and are now expected to invest more money to put in place a work-around to cover their problem.
I am open to any feedback from forum members as to anyone who has, or are, experiencing the same issue, and any suggestions as to what might be causing this, apart from a firmware issue within the inverters themselves.
Attached is an example MPPT3 voltage graph from Solar Assistant monitoring.