Anyone else realize this potential problem?
Polarized DC breakers such as the ones used in Midnight Solar MNPV combiner box have polarity. The + side must be connected to the highest potential, which would be the PV string. This is required for the arc suppression to function.

However if one of the PV strings becomes shorted, the other PV strings will feed into it, and the high potential for the shorted PV string may reverse. The shorted string breaker trips, the arc protection is defeated, and the breaker may burst into flame with an arc raging on.

Thoughts?
Anyone from Midnight Solar around to chime in?