So I'm planning to power up my system for the first time today and would appreciate any pointers or corrections to my plan.
Main Components:
Main Components:
- EG4 6000xp
- EG4 Indoor 280Ah battery
- Reliance Protran-2 transfer switch
- Grid AC Input disconnect switch
- IMO DC Disconnect
- Midnite SPDs
- Watts 247 4-2 Combiner Box
- 20 Aptos 400W panels in two 10-panel circuits (~350W per circuit)
- EG4 battery- turn ON with side switch and check front panel for correct activation (green light)
- Question: Do I need to have the BMS in "closed loop" or do I need to load up the BMS Tools software?
- 6000xp -
- Check for ~48V DC on battery input terminals
- Turn ON battery power breaker on front panel
- Turn ON inverter side power switch
- Verify inverter powers up
- AC Disconnect - Turn on Grid AC disconnect switch
- 6000xp - Turn ON AC input breaker
- Combiner Box -
- Turn on circuit #1 breaker
- Turn on circuit #2 breaker
- Check for no voltage at 6000xp PV inputs
- Midnite SPDs - Check that blue lights are on for both circuits
- IMO Disconnect Switch - Switch ON
- 6000xp -
- Check for ~350V DC at both PV inputs
- Turn ON PV on/off switch on inverter side
- Turn ON AC output breaker
- Check for 240V AC at output of Load breaker
- Protran-2 Transfer Switch-
- Turn ON circuit breaker for first switch
- Flip first switch from Line to Gen (this is attached to Inverter AC output)
- Verify that circuit is operational
- Repeat steps 1-3 for all 9 circuits
- 6000xp settings -
- Check all inverter settings per installation manual