K-fab
JAFO
I've two PowMr 5000W inverters set up to run 240VAC (120VAC from each unit) to power an HVAC compressor.
Everything is wired correctly - I figure this to be a true statement as a very good friend (the guy who got me down this Solar rabbit hole and knows his stuff) gave it a look over and the "OkeeDokee". Plus I've not let any smoke out of anything when I've powered the system up. I'm decently sharp with this stuff and REALLY respect electricity. Being shocked is my #1 most despised 'input'.
All lugs/connections are tight, as Will says that most of the systems he troubleshoots have loose connections. See? I pay attention and I'm trainable!
I'm in contact with PowMr's tech service right now but I figured I'd toss this out on the forum and see if anyone can find (what I imagine will be a really simple fix) the issue. Below is what I shared with PowMr's tech after they asked for more info.
Pictures are of:
Entire system
Inverters, BMC, breakers/cut offs
Unit 1 wiring
Unit 2 wiring
Unit 2 fault
Unit 2 VAC in from breaker. This is the same voltage as Unit 1 but from the other leg of the breaker.
I cannot get any VAC out of either inverter.
No. 1 is set to AC1st because I’m trying to pass 120VAC through. This will get set to PV1ST when issue is solved.
Many of the voltages listed are what came up on screen as I scrolled through the settings. I’m guessing this is set by the inverter because of battery selection? LiFePO4 is what I have. Bank of 16 EVE LF304Ah Grade A batteries.
No. 30 - I have one unit set to address 1 and the other to address 2
Code - Unit 2 is reporting Fault Code 39 - ParaAcSrcDiff Inconsistent AC input source in parallel. I’m taking the input 120VAC from the same double pole circuit breaker. One leg leads to Unit 1 and the other leads to Unit 2 (the problematic one).
All grounds and neutrals feed to the ground and neutral bus bars in the breaker box on the other side of the wall from the inverters.
All of the wires are about a meter long from breaker panel to inverter.
Both inverters have these settings:
No Setting
1 AC1ST
2 60hz (default)
3 UPS (default)
4 42.8V
5 50.0V
6 PV1ST
7 100A
8 LFP14 <---- THIS IS WRONG. It should be LFP16 since I'm running a 16S/48V battery. It also changes the default voltages accordingly.
9 CU49.2
10 120min Default
11 49.2V
12 42.0V
13 5s (default)
14 44V (default)
15 40.8V
22 DIS (default)
23 ENA (default)
24 ENA (default)
25 ENA (default)
26 ENA (default)
27 ENA (default)
28 40A (default)
30 id1 & id2 (two units Unit 2 is throwing the fault) <----- You need both of the communication cables installed between the units.
31 2P1 <---- Nope! It's PAL This and dual communication cables let the units shake hands and swing sine waves in synchronicity.
Line 31 is INCORRECT - my orange note was editing after getting things working temporarily. See my last entry (#6 in this thread) for the correct settings. One unit needs to be 2P0 and the other 2P2.
32 SLA (default)
33 WOW
34 DIS (default)
35 46.0V
36 100A
37 48.8V
38 120Vac (default)
I did not include any of the timer settings as I'm not using them nor have I changed any from default.
Edits to this original post are in color.
Everything is wired correctly - I figure this to be a true statement as a very good friend (the guy who got me down this Solar rabbit hole and knows his stuff) gave it a look over and the "OkeeDokee". Plus I've not let any smoke out of anything when I've powered the system up. I'm decently sharp with this stuff and REALLY respect electricity. Being shocked is my #1 most despised 'input'.
All lugs/connections are tight, as Will says that most of the systems he troubleshoots have loose connections. See? I pay attention and I'm trainable!
I'm in contact with PowMr's tech service right now but I figured I'd toss this out on the forum and see if anyone can find (what I imagine will be a really simple fix) the issue. Below is what I shared with PowMr's tech after they asked for more info.
Pictures are of:
Entire system
Inverters, BMC, breakers/cut offs
Unit 1 wiring
Unit 2 wiring
Unit 2 fault
Unit 2 VAC in from breaker. This is the same voltage as Unit 1 but from the other leg of the breaker.
I cannot get any VAC out of either inverter.
No. 1 is set to AC1st because I’m trying to pass 120VAC through. This will get set to PV1ST when issue is solved.
Many of the voltages listed are what came up on screen as I scrolled through the settings. I’m guessing this is set by the inverter because of battery selection? LiFePO4 is what I have. Bank of 16 EVE LF304Ah Grade A batteries.
No. 30 - I have one unit set to address 1 and the other to address 2
Code - Unit 2 is reporting Fault Code 39 - ParaAcSrcDiff Inconsistent AC input source in parallel. I’m taking the input 120VAC from the same double pole circuit breaker. One leg leads to Unit 1 and the other leads to Unit 2 (the problematic one).
All grounds and neutrals feed to the ground and neutral bus bars in the breaker box on the other side of the wall from the inverters.
All of the wires are about a meter long from breaker panel to inverter.
Both inverters have these settings:
No Setting
1 AC1ST
2 60hz (default)
3 UPS (default)
4 42.8V
5 50.0V
6 PV1ST
7 100A
8 LFP14 <---- THIS IS WRONG. It should be LFP16 since I'm running a 16S/48V battery. It also changes the default voltages accordingly.
9 CU49.2
10 120min Default
11 49.2V
12 42.0V
13 5s (default)
14 44V (default)
15 40.8V
22 DIS (default)
23 ENA (default)
24 ENA (default)
25 ENA (default)
26 ENA (default)
27 ENA (default)
28 40A (default)
30 id1 & id2 (two units Unit 2 is throwing the fault) <----- You need both of the communication cables installed between the units.
31 2P1 <---- Nope! It's PAL This and dual communication cables let the units shake hands and swing sine waves in synchronicity.
Line 31 is INCORRECT - my orange note was editing after getting things working temporarily. See my last entry (#6 in this thread) for the correct settings. One unit needs to be 2P0 and the other 2P2.
32 SLA (default)
33 WOW
34 DIS (default)
35 46.0V
36 100A
37 48.8V
38 120Vac (default)
I did not include any of the timer settings as I'm not using them nor have I changed any from default.
Edits to this original post are in color.
Attachments