If you do a Sol-ark 12kW set up as grid-tied, the ATS function is built into it with a 4ms switching time, pretty much a UPS like performance. You can set the inverter mode as you need and your grid tie can provide what power demands are beyond the capacity. If you want it to prioritize serving load during daylight PV production hours, it can do that. Their documentation and support are very good IMO. Also, get someone qualified to draw up your electrical design with a complete list of components and details on bonding and grounding. More local, more better.
You can use the loads calculator on the Sol-Ark site to figure out how much you really need. The “12kW” is, I believe, meaning that you can serve continuous load of 9,000 W ac (16,000 surge) and 3,000 W dc battery charging if you have enough DC input from your panels. They can be paralleled to cover 18 kW continuous, but that’s $12K for inverter/charger/gen control/ATS functions built into those boxes - a decent value but absolute dollars rule.
Finally, look into how much additional you really get from seasonal adjustment = I’m at 41N, not 30 like you and its like 4.4% annualized - I don’t know if I’d bother creating mechanical complexity in my mounting for 2-3% - you have summer AC load - bias it for that and/or add more panels up to VDC input limits.
Hope it helps!
You can use the loads calculator on the Sol-Ark site to figure out how much you really need. The “12kW” is, I believe, meaning that you can serve continuous load of 9,000 W ac (16,000 surge) and 3,000 W dc battery charging if you have enough DC input from your panels. They can be paralleled to cover 18 kW continuous, but that’s $12K for inverter/charger/gen control/ATS functions built into those boxes - a decent value but absolute dollars rule.
Finally, look into how much additional you really get from seasonal adjustment = I’m at 41N, not 30 like you and its like 4.4% annualized - I don’t know if I’d bother creating mechanical complexity in my mounting for 2-3% - you have summer AC load - bias it for that and/or add more panels up to VDC input limits.
Hope it helps!