Problem changing size of main grid fuse in SMA Sunny Island 6.0H-13 settings

riksnel

New Member
Joined
May 29, 2024
Messages
1
Location
The Netherlands
Hi all,

I've recently built some batteries with JK Inverter BMS's and to my delight my SMA SI6.0H-13 actually accepts the CAN output of the BMS (setting Pylontech, as I read on this forum). Further more I'm able to control charging and discharging (active power setpoint at grid connection point) using Modbus (about which I read on this forum), which was my goal and is great.

The SI monitors the energy flow at the grid connection point using an SMA Energy Meter on 'Speedwire' (ethernet). The SI has a setting:

"AC Side / Public electricity mains / Maximum current of the ext. network interface"

which is set to 26.5A for some reason (which corresponds to about 6kVA of apparent power).

When I try to change this value to 35A, the interface says: 10122 "Setting of parameter "Maximum current from utility grid" failed. Installation assistant must be started"

Now, when I start the installation assistant, it resets all the settings (also the grid country standard). So I begged SMA to give my a GGC and eventually I got it.

I expected this setting to appear to appear in the "Installation assistant", but instead I get this:

screenshot-installation-assistant-6-active.png
screenshot-installation-assistant-6-reactive.png
So it seems to be able to limit active power (W) and reactive power (VAr), but I want to limit apparent power (VA). Furthermore, if I set a limit for active power, the 'reactive power screen' (second screenshot) won't let me click 'next'. Also, whatever I put in here, the value of 'Maximum current of the ext. network interface' stays at 26.5A.

Does anyone know what I need to do to put in the correct value for 'Maximum current of the ext. network interface'? Is it perhaps a problem with the browser (I tried firefox and chrome, chrome wouldn't even display the time settings (second screen of installation assistant)). Is there a recommended browser to talk to firmware 3.30.37.R

Thanks for reading this far!

Greetings,

Rik.
 
13 series users on this forum are scarce, forum members with SI's mainly have SI5048 and SI6048. So there is no experience of how the 13 works.

As a SI5048 user, which has only 2 Grid connection country options, then my suggestion is that your selectable options are being limited by the Country Grid Code selected. Try selecting another countries Grid code and then seeing if the option you want appears.

When you have it sorted then on the JK you can select Canbus FSS, this is the SMA Canbus protocol they named after an obscure footer code on the bottom of the SMA Canbus specification PDF. It gives more info to the SI including an extra decimal point on V and SOC. It works with my SI5048. Pylontech copied it and call it Pylontech Plus.