what is the purpose of the 'grid' breaker?Yes, it's only purpose is to feed the loads (house).
what is the purpose of the 'grid' breaker?Yes, it's only purpose is to feed the loads (house).
Functionally it's incorrect. Because you have the inverter input and output connected together.i hope you know what i mean, i'm not trying to neglect safety, just meant from a functional/theoretical point of view, lol
To protect against overload or a short, in, or after the inverter.what is the purpose of the 'grid' breaker?
how does one separate them? wouldnt separating them functionally make the inverter be in 'intercept' mode of the grid connection?Functionally it's incorrect. Because you have the inverter input and output connected together.
Input and output of the inverter.where?
but they dont act as strictly input/output. from what i'm seeing/experiencing, both act as input AND outputInput and output of the inverter.
Yes, that's how it should be.how does one separate them? wouldnt separating them functionally make the inverter be in 'intercept' mode of the grid connection?
Correct, when operating without the grid. (Transfer switch in generator position)in which case, i'm entirely dependent on what my inverter can output = 12kw, right?
When operating on grid. (Transfer switch in grid position)i was originally going to set it up in 'intercept' mode, vs 'TEE', but if i have demands of over 12kw, i'm screwed. and i do have an EV to charge, so that alone can put me over what the 'load' breaker on the inverter can support
The grid port is bidirectional.but they dont act as strictly input/output. from what i'm seeing/experiencing, both act as input AND output
HMMMMMMMMMMMMMMMMMMMMMMMMMMMMMMMMMMM, your last point i think is starting to make a lot of sense...Yes, that's how it should be.
Correct, when operating without the grid. (Transfer switch in generator position)
When operating on grid. (Transfer switch in grid position)
The inverter will assist the grid and do whatever it can. The grid will take care of what it can't. (This all happens through the grid port)
That's correct, for the way you are setup.HMMMMMMMMMMMMMMMMMMMMMMMMMMMMMMMMMMM, your last point i think is starting to make a lot of sense...
so in theory, if i were to go turn off the 'load' breaker right now, functionally i'd be connected the way you're describing?
so the load side of the inverter should only ever be used when the grid is down, emergency situation, and dont expect to be able to run all my shit at full blast at once in that scenario?
hey i'm a complete retard when it comes to electricity, lol. ask me to machine or design or weld something, i'm your man! hahaWe now know why the Readings are not making sense.
YupView attachment 292748
This is starting to make a lot more sense now. So if I'm thinking about this correctly, because I was feeding both sides of the inverter, it was essentially going into a feedback loop?
We all only know what we know.hey i'm a complete retard when it comes to electricity, lol. ask me to machine or design or weld something, i'm your man! haha
thank you for helping me work through this.
Lmao, yeah, nobody can be an expert at everything.We all only know what we know.
This just happens to be my chosen career.
Do not ask me to weld anything. lol
CorrectSo to get this corrected, would it be ok for me to take my wires from the line taps and just put them in the lugs on the bottom where the small red and black wires currently are? (They go to a plug the old owners used to plug the generator into)
They looked small, in the video.Also, you were concerned about the size of the wires going to and from the inverter?
It's very possible.I wonder if the way I had it wired was causing the over current alarms I was getting before
i paid an electrician to wire up the inverter, i THINK he sized it properly... lolCorrect
They looked small, in the video.
Just make sure that they are sized correctly.
It's very possible.
It was definitely screwing with the inverter readings.
I trust Noone.i paid an electrician to wire up the inverter, i THINK he sized it properly... lol
nope, he knows nothing about solar/hybrid inverters, i told him where to connected, that blame is on me, hahaI trust Noone.
Especially if he decided where to connect the load wires.
Depends on how fast you can throw that switch. lolView attachment 292770
Wired up the ups/ load side to the bottom of transfer switch.
What happens if I transfer it now, would there be a momentary drop in power?
point taken, will do. although if someone comes close to my house uninvited... probably wont work out well for themDepends on how fast you can throw that switch. lol
But, you should have removed the generator wires. If someone connects a generator to the load side of your inverter, you'll be shopping for a replacement.
Yeah, if someone shows up on my property uninvited. I assume that they are there to recycle my lead.point taken, will do. although if someone comes close to my house uninvited... probably wont work out well for them