PV Trenching & Conduit

Gold Country Russ

Solar Enthusiast
Joined
Jun 28, 2023
Messages
163
Location
Sierra Mountains, Ca.
I have been agonizing about trenching for a single 9-panel string of west facing vertical bifacial panels. My problem is very thin soil and lots of shale and rock. I finally realized that using IMC (threaded steel conduit) allows shallow 6" depth trenches instead of the required 18" for PVC plus the metal conduit also functions in place of a ground wire. This would allow up to 6ea #10 THHN wires in a single 1/2" conduit. In my first case it would be a single 3.6KW PV 348VDC #10-2 wire circuit and a 20A 120VAC #10-2 wire circuit for a utility receptacle circuit & yard flood light. So much simpler!
 
Some comments about OK to mix AC and DC of same system. But not separate system like flood lights.


Multiple conduits would fix that.

1/2"? Go larger, 3/4" or 1".
Don't believe conduit fill tables. Go larger.

I don't want rusty steel threaded connections as safety ground, I want copper wire.
Although may be code compliant.
 
@Hedges IMO, 100+feet of galvanized & threaded steel conduit is itself a very significant ground, especially when connected to 10ea. 3'-imbedded 50+Lb. steel posts. I found a better place for the utility power and flood light so no AC. Will use 1/2" IMC, 2-#10 THHN, and leave a pull cord for another potential PV circuit.
 
You couldnt have 6 #10's in a 1/2 conduit, as that violates the conduit fill amount. (Its dang near 100% full. ) You'd have to go with 1" for 6 #10's.
 
I would hate to have anything buried that shallow tbh. 6" is well below my "check before you dig" threshold for casually banging in spades and posts.

But yeah, I'm in a similar situation with shallow topsoil over gravel and rock. Hand-trenching is a bloody pain, but iirc 18" was the minimum for what I was running, so it had to be done.
 
As a person who's dug a few ditches and learned a few slivers of wisdom, put pipe in 50-100% larger diameter than what you need. Put in 2-3 of those pipes in any trench you dig, because 5 years from now technology changes, expansions/upgrades happen and you'll wish you weren't now digging the same ditch again.
 